Breaker didn't trip when wire was cut. Trouble shooting tips...

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,898
Location
Essex Co., NJ
Replacing the doors in my house. While cutting out the old one, I cut clean through the wire feeding the lights in the room. (Someone routed the feed through the headers on top notching the top corner of the rough opening. Lousy work for sure).

Anyway, curious why the breaker didn't trip as the blade cut through the wire.

Thoughts?
 
To avoid these ads, REGISTER NOW!
OP
B

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,898
Location
Essex Co., NJ
It had power going to it for the lights were on at the time. It sparked, smoked, and arc on the blade of the sawsall.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
What you cut through was no doubt just a switch leg. You just turned the light off the hard way! How old was the wiring? Sounds like there was no ground wire.

I am assuming you were using a double insulated saw, one that had only a two prong plug. At the time you cut through the wire the blade and metal casing of that saw were at line potential. If your body was grounded you would have gotten a good jolt, perhaps knocking you off the ladder. If it were a three prong saw, plugged into a grounded outlet, it would have tripped the breaker, and minimized shock danger.
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
If its is a switch leg, there is no neutral and thus no way to have a dead short to trip the breaker (esp if no ground wire is present). The saw blade became the switch momentarily as it went thru the wires.

Charles
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,238
Location
Modesto, CA
Unless the OP has a Sh*tsco(Zinsco) or an FPE stab-u-in-the-back(stab-lok) panel, then Im also gonna say its a switch leg!!

The arcing and smoke could just be from cutting the wire under load and not a short at all! Have ever disconnected a neutral wire with a load connected through it?
 
Last edited:

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Agreed, it could have been a switchleg with no ground wire in the romex. But I have also seen on numerous occasions where a breaker didn't trip after a circuit was shorted and not just the crappy FPE's or Zinsco's. If the short is "short" in duration a breaker will sometimes not trip. I'm betting this is the case, since the OP mentioned it sparked and smoked. The only question in my mind being is this indicitive of a faulty breaker? As cheap as breakers are, it might not be a bad idea to just swap out the one that should have tripped.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
I've done this a few times: cut live wires. Sometimes the breaker trips, sometimes not. Couple of factors, but how quickly the blade (circular power saw) moved through the wire and where in the cycle the AC is can affect it.

I suppose if you are worried, you can replace the breaker, but I suspect it's OK.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I think you are correct in wondering if you seen smoke and sparks. There may be an issue, with an arc something should have happened?
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
My Experience is similar to nehog's, you can monetarily short a wire and not trip a breaker. But not for long... A moving saw blade may make and break the connection enough that the breaker never trips. More so if the blade is coated.

When I was epoxying my garage floor I stepped on the lead to the vacuum cleaner with my spiked shoes. Nice noise, a quick flash and that was it. The wire melted back from the arc before the breaker tripped. Seems likes it takes a bit to make a good connection when jabbing live wires.

I think the wires arced back faster than the spike could penetrate. The saw blade may have done the same thing.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
A concern here is the possibility of a missing bond to a 3 wire fed panel. I have had them flash when making an arc and so small you could barely see a spark and knock off a 30A breaker This may be worth a little investigation.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,758
Location
Long Island
No breaker can trip in under around 1.5 cycles. That's about 1/40th is a second. If the short is broken in less time than that the breaker will. It trip.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,927
Location
oregon
Time current curve

All circuit protection devises have a time/current curve (as linked above). Like rlitman said you probably did not create a short of enough time and magnitude to trigger the breaker. You may not have created a dead short at all and may have only broke the current carrying line to the load and only the current of the load created the spark, smoke, and burn on the blade.

lg
no neat sig line
 
OP
B

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,898
Location
Essex Co., NJ
The OP has never confirmed if there was a ground or neutral conductor in the Romex. There may have been no "short" at all.

Sorry guys. I was away for a few days. It was the older Romex that has what appears to be that coated cloth-type covering. It did have a ground wire which was very thin compared to new Romex.

Thanks for all the replies.
 

kamesama980

Well-known member
Joined
Mar 28, 2013
Messages
471
Location
columbus, IN
I have encountered, in the past, situations that especially with only a brief arc, the resistance of the air gap and tool grounding is enough to limit current and keep from tripping a breaker or fuse.

I've seen many times in autos a break in the wire that's shorting through corrosion or otherwise doesn't make a good connection. Sure clean wire to a bare ground would blow the fuse but corroded wire to painted body makes it just enough current to be a pain in the ****. Cars don't run so well when the 5v reference voltage drops to 4v.
 

offroadsteve

Well-known member
Joined
Apr 28, 2011
Messages
173
Location
Hampton, VA
Still not enough information to really know, but I have what sounds like the same wire in my house (cloth-covered romex), and the "with ground" is used randomly in the house along with "without ground".

I'd suspect a switch leg as others have said and you didn't create a dead-short to trip the breaker (load was still limited by the light fixture). I know all the bedrooms in my house are wired with the feed from the panel coming into the celing box and then branching from there for the light switch and all outlets in the room (think spider web).
 