Ah, I see the clamp on ammeter suggestion now. That would have been the first thing I checked. Thanks!
Many "20 amp rated" loads such as welders get away with 15 amp plugs because thy are intermittent duty. Your welds may draw just a little more than 15 amps, and depending on duty cycle may or may not trip the breaker. For example 17-18 amp bursts for 20 seconds with a cooling period between bursts might not trip the breaker, but a sustained burst of 30 seconds repeated rapidly might. It's all about the cb time curve."You cannot plug a 20amp male into a 15 amp female."
Thanks Paul for responding, but that's not it. 20a compressors, and 20a mig welders have the standard 3 prong 110v plug.
20 amp receptacles will accept the 15 amp plug, but the 15 amp receptacle will NOT accept the 20 amp plug.I am surprised to hear that since a 20 amp female has a a different shaped (sideways T ) prong
![]()
As you can see it will accept a 15 amp male.

That's because this person is a spammer. These people like to find high Google searched threads and put their link in there. They usually always add a link to a website. This thread with 12,000 views and this thread with 11,500 views. I almost wager that the poster is from Nigeria. I see this and I'm not even a moderator. You might not like how I wire things. But I got your six.Wow lot of wrong info on this thread brought back from the dead.
Im still trying to figure out how a 20a plug can fit in a 15a receptacle.![]()
A 140 can easily pull well over 20, I forget what it's rated output is. The manual calls for a 20 circuit I believe. Yes the code allows for smaller wire for welders, in fact 12 on 50.Many "20 amp rated" loads such as welders get away with 15 amp plugs because thy are intermittent duty. Your welds may draw just a little more than 15 amps, and depending on duty cycle may or may not trip the breaker. For example 17-18 amp bursts for 20 seconds with a cooling period between bursts might not trip the breaker, but a sustained burst of 30 seconds repeated rapidly might. It's all about the cb time curve.
NEC in special cases allows a #10 wire with a 50 amp breaker for welder applications. This can be done because of duty cycle ratings.
20 amp receptacles will accept the 15 amp plug, but the 15 amp receptacle will NOT accept the 20 amp plug.
That's because this person is a spammer. These people like to find high Google searched threads and put their link in there. They usually always add a link to a website. This thread with 12,000 views and this thread with 11,500 views. I almost wager that the poster is from Nigeria. I see this and I'm not even a moderator. You might not like how I wire things. But I got your six.