Breaker question

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I bought a 90 amp breaker for my subpanel feed. It's an Eaton CH breaker. I'm having a difficult time stabbing it onto the bus bar. I noticed the breaker has these spring clip things around the contacts. Am I supposed to remove these clips before installing the breaker? I think it will install easily if I remove them but I don't know if they must stay on or not.
 

Attachments

  • 20170418_212208.jpg
    20170418_212208.jpg
    156 KB · Views: 96
  • 20170418_212153.jpg
    20170418_212153.jpg
    146.6 KB · Views: 89
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
They need to stay, a little more pressure to get the breaker to seat will be required.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
Those clips stay. It is normal for a large breaker to require some force to clip it to the bus. The tight connection is required to keep the connection from getting hot with a possible 90A current.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I installed that identical 90A breaker in my CH panel and it does take a bit of force to get it snapped into place.
 
OP
E

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
What brand and model of panel do u have?

It's a Cutler Hammer panel. I don't know the model number but I can check when I get home this evening. It uses CH breakers though. Panel is from when the house was built in 1979.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
Your just going to have apply a bit more pressure, only time had any real issue installing CH frame breakers was in a meter/main that was manufactured in Costa Rica.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
Before you force it into place, please be sure to read the labels on the panel and the breaker and make sure this breaker is listed for use the panel you have. Only then push hard.

Walta
 

Zzaring

New member
Joined
Dec 16, 2019
Messages
1
Location
Ky
I’m looking for a panel cover part number for the panel box with part number of ch40km200. Thanks !
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
You should turn off the main breaker before you install the breaker (and wear gloves) in case your hand accidentally slips somewhere you don't want it to be :shocking:
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
You should turn off the main breaker before you install the breaker (and wear gloves) in case your hand accidentally slips somewhere you don't want it to be :shocking:

100% - was thinking same thing. Good advice. The 70A in my far end and the 100A in the near end took considerable oomph to seat. MAke sure everything is lined up and push. Gloves and power off if possible to avoid issues with a slip when it sits down.
 
OP
E

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
This is an old thread that was revived. I installed the breaker a few years ago, and it's been working fine.:thumbup:
 