Electric heater (shop, 220). 10,000 watt, 42 amp draw. 50 amp breakers OK? From what found, seems right. What I have now welder..thanks.
 
To avoid these ads, REGISTER NOW!
OP
R

Robby321

Well-known member
Joined
Jan 22, 2015
Messages
607
Location
Olympia, WA
OK, I'll have to look into this a bit more. What about a 7500 watt? But what found, wants 40 amp breakers. Run with 50's?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,029
Location
Modesto, CA
10Kw heater will need 50a breaker with either #8 THWN in pipe or 6/2 NM-b

7.5K heater will need 40a breaker with either #8 THWN in pipe or 8/2 NM-b

BTW elec heat is expensive to operate.

EDIT: i incorrectly estimated in my head the continous load sizing.

Will need 60a breaker with #6 wire (either 6/2 NM-b or #6 THWN)
 
Last edited:
To avoid these ads, REGISTER NOW!

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN
OP is in Washington state, between the BPA and the Grand Coulee Dam, its the cheapest electric in the country.
 
OP
R

Robby321

Well-known member
Joined
Jan 22, 2015
Messages
607
Location
Olympia, WA
OP is in Washington state, between the BPA and the Grand Coulee Dam, its the cheapest electric in the country.

Yep..but getting old and still use wood stove shop (dry heat shop toys and tools, rust PNW rainy season) but the hassle getting wood says maybe new. No Nat Gas here, just propane and a tank, heater installed be 2 grand easy. Just thinking ahead..attached shop to house off a enclosed porch. And I just about LIVE out here! My sanity and sanctuary "Dudgeon". :beer:
 