So installing a new compressor, 5 hp 3 phase, the motor shows amps 15.4-14.7 would a 20 amp enough or should I bump it up to a 30 amp breaker? Is there a normal % of head room you should have?

Maybe we should have some stickies be created for general rules, see the other thread on how many outlets per breaker is a good rule of thumb.
 
To avoid these ads, REGISTER NOW!

mayday0017

Well-known member
Joined
Oct 20, 2010
Messages
1,715
Location
Houston Texas
Doesn't sound like a real 5hp motor to me... Not sure what braker to run either as I know little to nothing about 3 phase

5hp is typically 20-25ish amp (roughly)
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I'd start with a 20 amp breaker. I always go 125% of the NEC motor HP tables, and then pick the next size up breaker.

The tables say 15.2 amps for a 240 3 phase motor x 125%=19 amps
 
OP
P

pmason0

Well-known member
Joined
Nov 12, 2011
Messages
251
Location
East Tennessee
Aceman, thanks, that was what I as thinking, rounding up, going up the 20 thinking it was 15.2.
mayday, as I understand 3 phase motors are less amperage as they are to be more efficient.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,145
Location
Minneapolis
Doesn't sound like a real 5hp motor to me... Not sure what braker to run either as I know little to nothing about 3 phase.

A 230vac three phase 5hp motor has a full load amp rating of about 15.2 amps.

Personally, I'd go with a 30 amp breaker, 20 amp is cutting it a little close. [I have a page out of an old Square D circuit breaker catalog with recommended trip ratings that I use as a cheat sheet.]
 
Last edited:
To avoid these ads, REGISTER NOW!

'04 Cummins

Well-known member
Joined
Jul 14, 2012
Messages
137
Location
MD
With an inverse time circuit breaker (standard breaker), max overcurrent protection is 250% of full load current, then increase to next standard size (NEC Table 430.52). 15.2 x 2.5 = 38, so actually max breaker would be 40 amp, though I would go with a 30.
 