Breaker ?
jaker10
Bartonvillle Illinois
How many amps can I safely pull from a 20 amp breaker? I have a 220 volt air compressor that is tagged 13 amp. I also have a 220 volt grinder that is tagged 3.3 amp. Can both run on a 20 amp breaker. Wire is rated at 20 amp. I think the wire is 12 2 but would have to look to make sure. So is 16.3 safe on 20 amp breaker?
How many horse is the compressor?
A continuos load is sized at 125% and therefore the continous load on a circuit should never be more than 80% of circuit capacity. This means 16a.
The compressor should really be on its own circuit due to in rush currents...
J
jaker10
Compressor says 13 amp and owners manual says 15 amp minimum branch circuit requirement. Manual says 3.2 HP. I'm running it off a 20 amp breaker. Grinder is 1/2 HP and 3.3 amp :dunno:
Speedy Petey
NY State
You are FINE with these two on a 20A circuit. Neither is even close to a continuous load, and even if the compressor starts while running the grinder the breaker should be ok handling the temporary startup current.
sberry
Brethren, Michigan
I agree. I am sure the grinder is designed to be able to run from a 20. If it came with a factory cord and is a 14 may be able to run on 30A in a certain environment.
Speedy Petey
NY State
In that case it'd need a 30A attachment plug or be hard wired, which is highly unlikely for a 1/2hp grinder.
sberry
Brethren, Michigan
I was wondering if it came with a factory plug? Most of that small stuff is 120 even though it can be wired either voltage. I was just generalizing anyway, you do see this in woodworking shops which often have multiple machines on a circuit.
Units that have no additional overcurrent are limited to the size breaker they may be connected to. If its got a 16 wire needs to be limited to a 15 or 20A. Obviously this is simplification and very general.
J
jaker10
This is an old grinder made in 1957, don't know if it came with a plug . But it's got one on it now. The air compressor say to hard wire it.
Norcal
Those old Rockwell grinders are nice machines, have a couple of early 1970's era ones, myself. Unless your circuit breakers are made by Federal Pacific Electric, I would not worry about the grinder & compressor being on the same circuit.