breakers too large for appliance

ericm

Well-known member
Joined
Apr 17, 2016
Messages
1,963
Location
Southern Oregon
I had an HVAC company install 24k Mitsubishi mini splits in my new shop. The day after they called and told me it went fine but that I need to replace the breakers with 20a ones. The breakers the electrician installed for those circuits was 25a or 30a, I can't remember which. Wiring was supposed to be suited to match and I assume it is. The spec I gave him was for Mr Cool 24k mini splits.

Of course I will replace the breakers with 20a ones. But I was wondering as a theoretical question, what would be the risk of using the larger breakers, or advantage of using the 20a ones? Do they trip sooner on a fault?
 
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,889
Location
oregon
Maybe give us the model number of the unit? If it has more than one way to configure then give those details also.

lg
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,819
Check the manual or info sticker on it, one should say what the max breaker size is.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
Wire gauge is used to determine the max breaker size but the circuit doesn't require that size be used
No........not in a motor circuit. AC unit is just a special case of a motor circuit. This random ac unit label is for 2 motors in the unit on the same circuit and calculated accordingly.

As a random example:
1759588398714.png
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,733
Location
Richmond, VA
No........not in a motor circuit. AC unit is just a special case of a motor circuit. This random ac unit label is for 2 motors in the unit on the same circuit and calculated accordingly.

As a random example:
1759588398714.png
I know that. Wire gauge is part of determining that limit
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,989
Location
Lebanon, TN
I bet $1 the OP unit has a nameplate that calls for a fuse and this can be fixed (if it's even wrong) at the disconnect...
Not likely with a modern Mitsubishi unit. They will typically allow a fuse or HACR breaker. Photo of the nameplate on my Mitsubishi 15k unit, note: "APPROVED FOR HACR BREAKERS OR TIME DELAY FUSES"

PXL_20251004_133721362.jpg
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,228
Location
VT
Not likely with a modern Mitsubishi unit.

I had Mr. Cool in my mind from reading it last night. Now that I read OP again I see it's a Mitsubishi installed...

I remember my Mr. Cool being a PITA if conflicting information until I had the actual unit/label in front of me
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
I know that. Wire gauge is part of determining that limit
Not really.
MCA determines min conductor size from 125% of comp FLA plus 100% of fan fla.
MOC is determined from 175- 225% of comp FLA plus 100% of fan fla depending upon type of circuit protection permitted.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,733
Location
Richmond, VA
Not really.
MCA determines min conductor size from 125% of comp FLA plus 100% of fan fla.
MOC is determined from 175- 225% of comp FLA plus 100% of fan fla depending upon type of circuit protection permitted.
So I can use whatever size wire I want as long as I breaker to what the compressor mfr states?

That's my point. It's part of the equation
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
So I can use whatever size wire I want as long as I breaker to what the compressor mfr states?

That's my point. It's part of the equation
You can use whatever size wire equal to or greater than required by mca.

Moc has nothing to do with wire size.

FLA's are the input into each different equation.
310.16B gets you to wire size once you have mca.

Moc could care less about 310.16B.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
Interesting that the label states "minimum circuit capacity" is 23Amps. What would you get if you asked an electrician to install a 23 Amp minimum circuit? Seems like to be installed compliment with manufacture spec. That is what you would need to do and arguing over inductive or resistive, 80% rule etc. would have no bearing. Would it force a 10ga , 30 Amp circuit?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
Interesting that the label states "minimum circuit capacity" is 23Amps. What would you get if you asked an electrician to install a 23 Amp minimum circuit? Seems like to be installed compliment with manufacture spec. That is what you would need to do and arguing over inductive or resistive, 80% rule etc. would have no bearing. Would it force a 10ga , 30 Amp circuit?
Conductor ampacity limits are based on insulation temp rating and termination temp ratings.
Other derating factors could be present also.
For the simplest case, Sparky will run 10-2 nmb.

Mca covers the continuous load/125% branch circuit upgrade that a random motor circuit would otherwise need.

MCA and MOC are just dumbbed-down NEC code requirements for the HVAC crowd.
 
OP
E

ericm

Well-known member
Joined
Apr 17, 2016
Messages
1,963
Location
Southern Oregon
Maybe I used too many words in the original post. The manual says 20a. What would be the advantage of a 20a vs 25a breaker?
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
It also wouldn't be the first time the HVAC contractor didn't have a clue. Twice I've installed a circuit for an AC when I had the spec's before it was installed. Once the spec was #14 wire and a 25 amp breaker, (I used #12 because that's what I had), the other was #12 and a 30. Both times the AC contractor told the customer I effed up because #12 is limited to a 20 amp breaker and no amount of explaining could convince anyone that I was right so I gave up and put 20's in. AFAIK, the smaller unit was fine, but the larger unit would occasionally trip the breaker on start up; of course, that was my fault. After about two weeks of back and forth I finally called an inspector friend of mine from another jurisdiction and had him tell them that I was right and the reason a 30 amp breaker was suggested by the manufacturer was to allow the compressor to start. I could have easily installed #10 just to shut everyone up, but out of principal I wasn't gonna do it, that would have been no different than admitting I was wrong in the first place.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
It also wouldn't be the first time the HVAC contractor didn't have a clue. Twice I've installed a circuit for an AC when I had the spec's before it was installed. Once the spec was #14 wire and a 25 amp breaker, (I used #12 because that's what I had), the other was #12 and a 30. Both times the AC contractor told the customer I effed up because #12 is limited to a 20 amp breaker and no amount of explaining could convince anyone that I was right so I gave up and put 20's in. AFAIK, the smaller unit was fine, but the larger unit would occasionally trip the breaker on start up; of course, that was my fault. After about two weeks of back and forth I finally called an inspector friend of mine from another jurisdiction and had him tell them that I was right and the reason a 30 amp breaker was suggested by the manufacturer was to allow the compressor to start. I could have easily installed #10 just to shut everyone up, but out of principal I wasn't gonna do it, that would have been no different than admitting I was wrong in the first place.
I would not have changed anything.

I would have shoved the mca/moc concept and the nameplate into their face and told them to go learn their trade.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
I would not have changed anything.

I would have shoved the mca/moc concept and the nameplate into their face and told them to go learn their trade.
The AC guys were long gone both times and I was dealing with a pissed of HO that had been convinced that I was a hack (which is true, but not in this case). I did call the HVAC company and when whoever I talked to pointed me to 310.16 I just gave up.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,216
Location
SE MI
Maybe I used too many words in the original post. The manual says 20a. What would be the advantage of a 20a vs 25a breaker?
Breakers/fuses are sized to protect the wire to the load. If the wire is sized for 25A, no benefit for going to a 20A breaker.

The load "should" protect itself.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
The AC guys were long gone both times and I was dealing with a pissed of HO that had been convinced that I was a hack (which is true, but not in this case). I did call the HVAC company and when whoever I talked to pointed me to 310.16 I just gave up.
It should have been inspected mechanical and electrical.

An HVAC company that knows nothing about NEC 440 should shut down.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
Interesting that the label states "minimum circuit capacity" is 23Amps. What would you get if you asked an electrician to install a 23 Amp minimum circuit? Seems like to be installed compliment with manufacture spec. That is what you would need to do and arguing over inductive or resistive, 80% rule etc. would have no bearing. Would it force a 10ga , 30 Amp circuit?
If THHN/THWN conductors were used 12 AWG would be fine.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
It should have been inspected mechanical and electrical.
An inspection would require a permit... and that's something I don't do very often unless the POCO is involved.
An HVAC company that knows nothing about NEC 440 should shut down.
You wouldn't believe the number of "lectricians I've had that argument with. I almost made one guy cry when he saw I used #8 on an 80 amp breaker for a 7-1/2 HP single phase air compressor...
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
An inspection would require a permit... and that's something I don't do very often unless the POCO is involved.
Wouldn't the AC replacement have triggered a mechanical permit required from HVAC contractor and then rolled into needing an electrical permit?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
Wouldn't the AC replacement have triggered a mechanical permit required from HVAC contractor and then rolled into needing an electrical permit?
Yes but this was a new install on an old house with no central AC. It should have been permitted, but nobody does it; get in, get done, get out. The only time I've ever pulled a permit for an AC install was a rental house and only because the rental inspectors check for things like that.
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,074
Location
Fernley, Nevada, about 30 miles east of Reno.
An inspection would require a permit... and that's something I don't do very often unless the POCO is involved.

You wouldn't believe the number of "lectricians I've had that argument with. I almost made one guy cry when he saw I used #8 on an 80 amp breaker for a 7-1/2 HP single phase air compressor...

That's the wire and breaker I would have chosen too.

Perfectly code compliant.

P.S. I don't get permits unless I absolutely have to.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
You wouldn't believe the number of "lectricians I've had that argument with. I almost made one guy cry when he saw I used #8 on an 80 amp breaker for a 7-1/2 HP single phase air compressor...
Maybe he was related to the lectrician who was the buddy of the GC doing a kitchen model for a previous customer. He told the customer my earlier 48a evse charger wiring was wrong. I got a call from the customer. He told me wires were undersized!
What??? I ran 2 #6 and 1 #10 grn. (Didn't I?, oh ****....)
I show up and find I did run what I mentioned. I calm down the HO and tell him all is ok. You want it inspected, no problem. Let's do it.
I find Sparky on the job and ask him WTF are you talking about? That's to code. Why are you slamming me with my customer.

He said we always run the same size grd as hot wire. We dont look at any table in 250.
DUMB MF'r. Ever looked at a piece of 6-2 nmb?? Huh??? Deer in headlights look.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
Maybe he was related to the lectrician who was the buddy of the GC doing a kitchen model for a previous customer. He told the customer my earlier 48a evse charger wiring was wrong. I got a call from the customer. He told me wires were undersized!
What??? I ran 2 #6 and 1 #10 grn. (Didn't I?, oh ****....)
I show up and find I did run what I mentioned. I calm down the HO and tell him all is ok. You want it inspected, no problem. Let's do it.
I find Sparky on the job and ask him WTF are you talking about? That's to code. Why are you slamming me with my customer.

He said we always run the same size grd as hot wire. We dont look at any table in 250.
DUMB MF'r. Ever looked at a piece of 6-2 nmb?? Huh??? Deer in headlights look.
He would have really beat me up when he saw I didn't pull a ground at all if EMT was used.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
An inspection would require a permit... and that's something I don't do very often unless the POCO is involved.

Glad I'm not the only one.

I like doing farm wiring, a permit and inspection is usually not required. Sometimes the service needs it. Once an inspector told me what came down the chain, "don't get in the way, unless it's a serious issue". They usually look at grounding and bonding then it's see you later!

I'm the next couple weeks I'll start installing a 600A 480V service. No inspection required.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,005
Location
NJ
Glad I'm not the only one.

I like doing farm wiring, a permit and inspection is usually not required. Sometimes the service needs it. Once an inspector told me what came down the chain, "don't get in the way, unless it's a serious issue". They usually look at grounding and bonding then it's see you later!

I'm the next couple weeks I'll start installing a 600A 480V service. No inspection required.
Lucky you! I'm being harassed over a permit/inspection for changing a friggin meter pan!! POCO threatens no re-connect w/o cut-in card.

How hard can 6 wires be to connect and confirm correct? The lineman are laughing their tales off.
 
OP
E

ericm

Well-known member
Joined
Apr 17, 2016
Messages
1,963
Location
Southern Oregon
another request for a pic of the nameplate

I'm not on site.

I wasn't asking for you guys to figure out what breakers to use. The manual says 20a and the HVAC company says 20a, so I will replace the 25 or 30a ones in there with 20s. I'm pretty sure they're 25s. What I was asking was what would the theoretical benefit be to using 20s on a circuit made for 25s. Is it just following the manual? Do the 20s trip easier? What sort of situation would happen where the 25s would not trip and the 20s would, and would it matter?

With automotive fuses, the smaller fuse burns out quicker, more likely saving the wiring in the case of a short. Is it the same for breakers? Or does a short trip the 20 and 25a breakers equally fast?
 