I have a older Bridgeport vertical mill (3 phase wired low voltage) that I have powered by a VFD. I went out to finish a job yesterday morning and the motor won't start. I first suspected the Chinese VFD but I want to check the motor before I order another VFD.
Confused as to how to "ohm out" the motor because it has nine leads. Can anyone help a bro out?Bridgeport Motor.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,023
Location
Fernley, Nevada, about 30 miles east of Reno.
First unsplice all the leads them ohm each one to the motor frame. All should be infinite resistance (open circuit).

Next, look at resistance from 1 to 4. It should be very close to 2 to 5 and 3 to 6.

7 to 8, 8 to 9 and 9 to 7 should be the same but close to double the other readings.

This is not a complete thorough test but if it fails, the motor is shot.
 
OP
A

Artfrombama

Member
Joined
Aug 3, 2010
Messages
18
have you confirmed with a multimeter that the VFD is outputting power?
Yes, all three
First unsplice all the leads them ohm each one to the motor frame. All should be infinite resistance (open circuit).

Next, look at resistance from 1 to 4. It should be very close to 2 to 5 and 3 to 6.

7 to 8, 8 to 9 and 9 to 7 should be the same but close to double the other readings.

This is not a complete thorough test but if it fails, the motor is shot.
1-4=Open, no resistance
2-5=233.5 Ohms
3-6=3.8
7-8=6.8
8-9=7
9-7=7
#4 to frame=.4ohms

Smoked
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,875
Location
NJ
Running motors from VFDs is hard on insulation due to the fast edges of the output. They make motors with better insulation that are rated for inverters. They also make output filters but I haven't seen those used much. Not saying that is what caused the problem but it could be.
Based on the apparent age of the motor, I would say that the vfd is the cause of insulation puncture.

If rewinding this motor, make sure to mention vfd driven.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Running motors from VFDs is hard on insulation due to the fast edges of the output. They make motors with better insulation that are rated for inverters. They also make output filters but I haven't seen those used much. Not saying that is what caused the problem but it could be.
definitely get a VFD rated motor for the replacement
 

Ag 85

Member
Joined
Apr 27, 2023
Messages
12
Location
Bellville Texas
The motor was originally nameplate rated for 460 volt not 480 Volt which is now seen in modern distribution and or VFD.
I have worked with motors rated for 440 Volts wound in 1930's. Higher torque output but longevity is reduced at higher than rated voltage. Inverter duty rated they are not. Nore info here.
A good rewind shop can make that motor new and inverter duty. Then it fits and looks original.
Good luck.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
The motor was originally nameplate rated for 460 volt not 480 Volt which is now seen in modern distribution and or VFD.
I have worked with motors rated for 440 Volts wound in 1930's. Higher torque output but longevity is reduced at higher than rated voltage. Inverter duty rated they are not. Nore info here.
A good rewind shop can make that motor new and inverter duty. Then it fits and looks original.
Good luck.
probably cheaper to buy used...
 
To avoid these ads, REGISTER NOW!

kngelv

Well-known member
Joined
May 25, 2011
Messages
2,216
Location
Detroit, MI
I can’t tell if that‘s a delta or wye motor. Use a megger. These are for low voltage. If a delta put these pairs together 6-7, 4-8, 5-9 and leave 1, 2 and 3 apart. These are your L1, L2 and L3. Check 1,2 and 3 to ground. Should be over 100 megaohms. Will still be ok over 10 megaohms. Phase to phase should be low ohms. If open you have broken windings. Do the check with a wye. Jump 4,5, and 6 together. Your L1, L2 and L3 are 1-7, 2-8 and 3-9.

James
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,875
Location
NJ
I can’t tell if that‘s a delta or wye motor. Use a megger. These are for low voltage. If a delta put these pairs together 6-7, 4-8, 5-9 and leave 1, 2 and 3 apart. These are your L1, L2 and L3. Check 1,2 and 3 to ground. Should be over 100 megaohms. Will still be ok over 10 megaohms. Phase to phase should be low ohms. If open you have broken windings. Do the check with a wye. Jump 4,5, and 6 together. Your L1, L2 and L3 are 1-7, 2-8 and 3-9.

James
It's a wye, but why bother with anything further testing?
2 of the 6 windings are clearly messed up as reported. Those 3 point connected windings have 2x the value as the apparent remaining single good winding as would be expected.

If each separate winding and the 3 connected internally (sometimes broken out as 10, 11, 12) all showed good values, then a megger would be a good test for possible further info.
 

kngelv

Well-known member
Joined
May 25, 2011
Messages
2,216
Location
Detroit, MI
I agree with your earlier methodology suggestion but I suggested the megger because sometimes you get weird ohm readings on windings depending on what meter you’re using. Plenty of people use **** meters and get screwed up readings. Using a decent megger to put a load on it is the best way to test a 3-phase motor.

James
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,285
Location
Illinois near St. Louis, Missouri
That's a good suggestion and they have 460V units (460, 480 whatever it takes... Seriously I wouldn't get too hung up on that small difference). Have used Automation Direct before but not for line inductors. Was not aware they had those and prices are reasonable.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,875
Location
NJ
Every piece of electrical equipment was built with smoke secretly installed at the factory, once the smoke leaks out your equipment won't work like new; if it will work at all.
Most stopped putting the special bbq sauce inside however.
 