Building my shops infloor heat system

fuelie74

Well-known member
Joined
May 17, 2009
Messages
48
Location
Monroe WI
I have spent the last several months researching and now I pulled the trigger and started ordering stuff. I have almost everything and am starting to dry fit before final assembly. Hopefully tomorrow night my boiler will be in. I am looking forward to suggestions especially at this stage before sweet it all together.

Here is what I have so far. I am running two zones.
20131016_215957_zps542aebf4.jpg

How should I be supporting the expansion tank?

Sent from my SCH-R970 using Tapatalk 2
 
To avoid these ads, REGISTER NOW!
OP
F

fuelie74

Well-known member
Joined
May 17, 2009
Messages
48
Location
Monroe WI
Need more info.

What boiler, how big of an area, insulation?

We love commenting, just need more to work with.

KO

The building is 45x56x16 with R38 in the ceiling and R19 in the walls. 2 inch high density foam board under the slab and around the perimeter. Two zones. One zone is 420 sq with 2 - 250 ft loops and the second zone is 2100 sq with 12 - 250 ft loops. I have a Navien combi tankless boiler that should be in tonight or tomorrow.

Sent from my SCH-R970 using Tapatalk 2
 

koditten

Well-known member
Joined
Apr 10, 2008
Messages
5,528
Location
Midland, Michigan
****!

I didn't even notice your question, I thought it was just part of your signature. I was sitting here thinking "shelf bracket?" Why did Tony post that?

anyways, on mine I used 2 shelf brackets, one on eash side. The plumbing is suspended by those clamp on pipe supports, a small threadded rod goes to each shelf bracket.

KO
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
If you look at the bottom of your air separator you notice a plug , that is where you should be installing your pressure tank. It doesn't have to go there but it should.
One other thing , I can not tell from the pic but your pumps should pump away from the boiler and your air purging valves should be on the return side of your loops.
 
Last edited:
OP
F

fuelie74

Well-known member
Joined
May 17, 2009
Messages
48
Location
Monroe WI
Are the cool looking clear plastic ones ok are is it best to stay away from them and go with a brass one? Thought it would be nice having as sort of a sight glass.
 
OP
F

fuelie74

Well-known member
Joined
May 17, 2009
Messages
48
Location
Monroe WI
I was told this gauge would be a good idea for monitoring the system. It has temperature and pressure. Where does it go in the system? I thought was that it should be right after the boiler but I don't really know. Also how should I mount it in the system with the long probe?

20131019_132252_zpsc85bc8d7.jpg

20131019_132300_zps6b1d33e9.jpg
 
To avoid these ads, REGISTER NOW!

anthony666

Well-known member
Joined
Dec 29, 2007
Messages
987
Location
kirkfield ontario
a temp gauge going into the slab and one coming out is good so you can verify your net delta t .. at the boiler its not so vital .. you can feel it's hot

a pressure gauge is always a good call, i put it in the primary loop opposite the pump
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
You should have a boiler operating temp gauge and gauges for the pex manifold too. You should be running a continues primary loop and then take your runs off from that .
 

Sureshot

ALLIANCE MEMBER
Joined
Jan 3, 2011
Messages
3,134
Location
Bridge Creek, OK
You will be fine with one temp gauge coming off the boiler but one on the return wouldn't hurt. You will want to have a temp gun to check the floor temp, individual lines, and general diagnostics and knowledge.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Whatever you do, don't tighten that gauge by hand! Geez, they totally ruined that gauge with the warnings.

With a simple closed system using no primary/secondary you would need to know the temp in one place, going into the floor, but knowing before and after the boiler would be even better.

That gauge is fine but the temperature range is quite high for slab heat. Is there an option of a lower temp range like maybe 30-130?

Also, lower pressure like 0-50?
 

Sureshot

ALLIANCE MEMBER
Joined
Jan 3, 2011
Messages
3,134
Location
Bridge Creek, OK
I find the return temp quite useful as well as that seems to be closer to the floor temp and tell you when things are "stable". Best to diary the numbers on startup and once it is running good then if you have a problem it will make the diagnostics easier.
 
OP
F

fuelie74

Well-known member
Joined
May 17, 2009
Messages
48
Location
Monroe WI
Is it ok to put the pumps and the boiler on the second story directly above the manifolds that are on the first floor? Just thinking it would be best for the boiler to be away from the dust and grime.
 