Bulbs burning out

bls2dpj

Active member
Joined
Dec 2, 2009
Messages
42
Location
Wichita, KS
I have a standard outside wall light on the garage. It's a motion sensing light. It's been going through bulbs about 1 every 10 days. It functions correctly, I.e. Comes on at night when it senses motion and it goes off at he time I specified (5 minutes). But it keeps burning through bulbs like crazy. I've tried the old filament style bulbs and the coiled up fluorescent but it still burns them out. Any ideas of why???

I've put up a replacement light in the meantime but would like to keep the fixture because it matches the house quite nicely.

DJ
 
To avoid these ads, REGISTER NOW!

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Interesting.... I have a bathroom bulb that does the same thing(it is in a row of 4 but the same one burns out all the time)
Going to keep an eye on this for answers......

P.S. sorry im not help :p
 

manioso

Well-known member
Joined
Mar 7, 2010
Messages
64
Location
Princeton, NJ
Not sure why you're burning out old fashioned incandescents, but spiral compact fluorescents won't tolerate that type of motion controller. They work by passing a small current through the bulb when off. The electronics (ballast) will burn out prematurely. I had same problems with several porch lights in wall sconces around my house and garage. Each sconce had three bulbs, and I had five sconces for a total of 15 lamps. With 40 watt bulbs that was 600 watts total. Since the rather expensive CFL candelabra doesn't last, I had to switch to incandescent.

If you're still getting poor life out of incandescents, I'd suggest you look at the voltage delivered to the fixture. If higher than 120v nominal, that could be the source of your problem.
 
OP
B

bls2dpj

Active member
Joined
Dec 2, 2009
Messages
42
Location
Wichita, KS
What's crazy is I've had the fixture for over two years and used the coil type bulbs without any issues up until about a month or two ago.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
Have you installed any equipment that is running and causing vibration near this fixture?

Are any other bulbs not lasting, or just in this fixture?

How is the garage fed power, from the residence, separate pole feed, or?
 

IOWNJUNK

Well-known member
Joined
May 22, 2013
Messages
758
Had the same problem when I lived in military housing, as long as the bulb was on it was good, once you turned it off it would never work again, just a pop and then replace the bulb. We just quit turning the lights off and bought lamps for the bedrooms. I would just replace the fixture and be done with it. You have probably paid for a new one already in bulb replacement costs.
 

raiderhillbilly

Well-known member
Joined
Jul 14, 2013
Messages
610
Location
NC
If you can find a "rough service" bulb that says 130v instead of 120v it will last longer. You will not have quite as many lumens, however.
 

tractordude

Well-known member
Joined
Nov 16, 2009
Messages
2,226
Location
WI
I had the same problem with a ceiling fan in our kitchen. Now, the fan part was never used, so rule out vibration. I tried different brands of bulbs,Etc. Tested the voltage Etc. I finally just bought a different ceiling fan, now we don't burn out bulbs like before.
My thoughts were the cheap wiring, all that stuff is made in china and elsewhere
 
OP
B

bls2dpj

Active member
Joined
Dec 2, 2009
Messages
42
Location
Wichita, KS
Voltage test showed everything was good and all the connections were tight. So either a bad wire or just a cheaply made fixture. I replaced it with a basic security light and installed two flood lights. Not as aesthetically pleasing as the other but it going to function better then what I had.

Thanks for all the input

DJ
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,751
A neutral being used from another circuit can cause premature incandescent lamp failure. It's a easy mistake to make.
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
If it were me, and if it isn't very expensive, I would just replace the unit. That will probably fix the problem, but even if it doesn't fix it you won't be out very much.
 

DIC

Well-known member
Joined
Aug 2, 2009
Messages
698
I had the same problem with my front porch light It would only last a week or two. I finally figured mine out, when the door shuts it shakes the fixture. I put it a rough service drop light bulb and now it does not burn out.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I had a fixture problem with a motion and it was a neural issue. The handyman that installed it had not used a connector on the box at the service, must have taken a while to chafe thru but the N was arcing on the can. Its been a while so the details are fuzzy but fixed it and never had another problem.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
I have two 500Ws on my barn that do the same thing. Put a bulb in and it lasted an hour. Went with heavy duty bulbs - same thing. I THINK it's the contacts on the sides of the bulb being too tight, but I'm not sure. It ***** as they are 20' up.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
I had a fixture problem with a motion and it was a neutral issue. The handyman that installed it had not used a connector on the box at the service, must have taken a while to chafe thru but the N was arcing on the can. Its been a while so the details are fuzzy but fixed it and never had another problem.

Neutral arcing on the can? That doesnt make sense...neutral and ground should be at the same potential at the main service panel!
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
even in well grounded systems a small voltage exists between ground and neutral at remote locations. the closer you get to the main bonding jumper the less voltage is present
 

mtne

Well-known member
Joined
Dec 3, 2007
Messages
113
Location
Denver
A loose neutral can cause micro arcing which will shorten the life of the lamps. Imagine each arc as an on/off cycle. If you feel safe doing it tighten all the lugs in your panel. While worse with AL wiring, the load cycle over time causes expansion and contraction loosening the lug. If nothing is amiss there, and it is happening only in one lamp base I would suspect an internal wiring issue causing micro arcs. Generally voltage isn't an issue unless it is + or - 10% or even more.
 