I am replacing my lamp post cable and live in northwest Illinois. What is the recommended depth to bury the cable?
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
Using google, it appears min depth is 24" with 26-36" recommended for direct burial cable.
 
To avoid these ads, REGISTER NOW!

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Yes, thank you. I asked an electrician and he said 12" is fine. I don't think it is.

12" is NEC code compliant. IF it is a residential use AND protected by a 20A or less breaker AND is a 120V or less circuit AND is GFCI protected. It is allowed to be run in UF cable. NEC 300.5(A)

Steve
 
OP
S

Sal Bandini

Well-known member
Joined
Aug 30, 2012
Messages
994
12" is NEC code compliant. IF it is a residential use AND protected by a 20A or less breaker AND is a 120V or less circuit AND is GFCI protected. It is allowed to be run in UF cable. NEC 300.5(A)

Steve

All the boxes are checked except the GFCI part.
 
OP
S

Sal Bandini

Well-known member
Joined
Aug 30, 2012
Messages
994
Only with horse shoes and hand grenades. Not with the NEC.

Well, the way it is now the wire comes out of the ground with no conduit and goes to a transformer. Then a short piece of cord with plug goes into a receptacle on the house wall. That's how it was when I bought the house.

I just need to figure out how I'm going to add GFCI and conduit.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,591
Location
Long Island
Well, the way it is now the wire comes out of the ground with no conduit and goes to a transformer. Then a short piece of cord with plug goes into a receptacle on the house wall. That's how it was when I bought the house.

I just need to figure out how I'm going to add GFCI and conduit.

Transformer? So is the buried wire 120V or low voltage (class 2)?
 
OP
S

Sal Bandini

Well-known member
Joined
Aug 30, 2012
Messages
994
It's 120V. The transformer is for some low voltage cable that is not used. The wire coming out of the ground is wire nut to the cable with plug going into receptacle.

That's the way it was when I bought the house, but now that I need to repair it I'm going to do it right.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Using google, it appears min depth is 24" with 26-36" recommended for direct burial cable.

goodle? why not go straight to the horses mouth? :lol_hitti:D:D:beer: