I still disagree.
Any electromagnet in a 60 Hz AC circuit can cause a mechanical buzz. Electromagnets are typically made up of "plates" (laminations) of steel with copper windings around them. At 60 cycle per second they can vibrate.
For a better picture of the internals of a
typical breaker see this article on
How Stuff Works From the 3rd section
Your
typical breaker does not "sense" thermal overload (although these type of breakers do exist and are typically self-resetting).
Power factor has nothing to do with the buzz from inside the breaker.
sorry but youre wrong.
From square D QO brochure: "QO® (plug-on) and QOB (bolt-on) one-, two- and three-pole
thermal-magnetic circuit breakers provide
overcurrent protection and switching on ac and dc systems." look up homelinw, CH or whatever other residential breaker you like and you will see the same.
next lets address the electromagnet. I see what youre saying, BUT you need enough current flowing through the coil to create a magnetic field to get a buzz. The magnetic trip coil in a breaker is different than say a solenoid. It doesnt do anything until you get the right amount of current going through it, which is quite a bit more than the breaker rating. Once you approach the lower boundary of this current level, the magnetic trip element will not generate a field strong enough to trip the breaker but will make noise. Again, look at a breaker spec sheet, view the trip curve and where you find the instant trip range -thats where the electromagnet comes into play, everything before that is thermal.
now ill explain the three types of miniature circuit breakers and their applications.
thermal-magnetic -these are the most common and are used in 90% of branch circuit applications. The thermal element provides a time delay function that prevents the breaker from tripping on inrush from turning on cold heating elements and from starting motors. The magnetic trip element provides an instant trip function that clears faults and extreme overloads.
hydraulic-magnetic -this type of breaker replaces the time delay function of the thermal element with a plunger moving through a viscous fluid. The advantage is immunity to temperature both ambient and internal, as well as precise calibration and repeatable operation. You will find these used where ambient temperature is an issue (one very common place is in the portable power distribution used on movie sets where circuits are heavily loaded and the breakers are sitting directly in the sun) , and they are used to protect circuits supplied through semiconductors such as in professional lighting dimmers. They are also used in telecommunications and industrial settings.
magnetic only - i cant give much application info on these, but they have no time delay function. Exceed the rating by even a fraction of an amp and they trip instantly. Maybe theyre used in airplanes or something.
With regard to your comment about power factor having nothing to do with the buzz, in this situation it does. The noise is coming from the magnetic trip element which makes noise when a ton of current is passing through it. The CFL with poor power factor draws a ton of current, but does it so fast that the thermal element isnt heating up and tripping the breaker and he is under the magnetic trip threshold. Look at my 13w CFL with a peak current draw of 1.33 A. If I put 50 of these on a circuit, my load would be 650 W (plus whatever the ballasts eat) but the breaker is going to be seeing current spikes of ~66 amps and the magnetic element is going to make quite a racket.
note: the breakers (actually called supplimental protectors) in outlet strips, push to reset breakers on appliances and the such are thermal only. These are not suitable for or listed for branch circuit use -entirely different UL class.