Nothing in anything I post ever has any element of AI (unless I specifically call it out as AI). So clearly you're not understanding what I'm writing. Let me try again. Perhaps you missed the pertinent details or don't understand the difference between AC and MC.
In
MC, you will find an actual ground wire
with green insulation. This is the EGC (equipment grounding conductor). If it includes a bonding wire (more on this in a moment), then the armor can be used as a code compliant EGC as well.
In
AC, there is no
insulated ground wire. Instead, the ARMOR itself is the EGC, and a bonding wire is provided underneath and
in intimate contact with the armor, that ensures the armor is a safe EGC. The bare wire is NOT an EGC, it is not a ground wire, and it is not mean to be connected to anything. As a matter of principle, I usually bend the bonding wire around the end of the armor and wrap it up a few turns so it gets hit by the clamp screw, but it's not a requirement. Anyway, the bonding wire is NOT considered a conductor.
The Southwire website diagrams are great. Starting here:
https://www.southwire.com/wire-cable/metal-clad-cable/c/c-mcmain
Filter for type "AC".
All four examples show an aluminum bonding wire OUTSIDE of the paper that wraps the conductors.
Then filter for "AC90", and the copper wire type shows a copper bonding wire in contact with the aluminum armor.
If you turn off the filter and browse through all 76 variants, you'll notice that only the AC types have paper surrounding the conductors, a bonding wire OUTSIDE of the paper, and no green wire. All of the MC types have a plastic wrapper and include a green insulated ground wire with the rest of the conductors. The green armored MC types also include a bare bonding wire between the plastic wrapping and the armor.
Actual BX predates the bonding wire. Without the bonding wire under the armor, the armor isn't considered a safe and reliable EGC.