BX or plastic conduit? Need quick, safe, and neat looking rewire

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,889
Location
Essex Co., NJ
OK, the house we recently moved into needs to help with wiring in the garage. It's got decent power, but just oddly placed. I want to relocated some of the outlets.

I'm kind of **** about wiring that is exposed/surfaced mounted, but the idea of moving stuff is not appealing. I guess I should have thought about this before I finished everything but I didn't.

Is there any reason why I shouldn't use BX or should I do it right and run plastic pipe?

I don't want to use metal conduit for I need to go through a dividing wall and other crazy bends that it just makes sense to use plastic pipe.

Thoughts?

Thanks,

Tim
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Either will work, just depends on what you like better, probably easier to use bx but pipe would look straighter
 

kd3pc

Well-known member
Joined
Aug 10, 2013
Messages
3,630
Location
Northern Neck
if exposed to heat, the plastic will sag in a few months and be ugly as all get out, unless you set a ledge under it....

emt will not sag...

which ever you like best
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,788
What you see in the big box stores is not BX, it's MC, Metal Clad cable, BX (AC ,Armored Cable) and MC have their own sections in the NEC.


MC has the same limitations as NM cable with requirements for protection from physical damage.
 
Last edited:
OP
B

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,889
Location
Essex Co., NJ
Why can't you tear out the drywall and run the wires inside the wall?

I've installed/place all of the shelving, work bench and tool boxes. It would be more work to do it that way.

So does "true" BX offer more protection than metal clad wire? I'm assuming you'd get it from a supply house.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,788
I've installed/place all of the shelving, work bench and tool boxes. It would be more work to do it that way.

So does "true" BX offer more protection than metal clad wire? I'm assuming you'd get it from a supply house.

AC also has the same limitations.

AC cable is NEC art.320, MC is art. 330.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
So does "true" BX offer more protection than metal clad wire? I'm assuming you'd get it from a supply house.


"True" BX does not exist. It was a generic name applied to the metal clad cable of the past.

A version of M/C cable that has a heavy steel armor is as close as you'll come.

It's still subject to the physical damage provision.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
EMT, PVC, MC and such, you just don't want to use those types of wiring protection in a location where the risk of damage is high. I will venture to guess you're not installing your wire where it will get smashed by a car or by swinging a wild hammer here and there. I'd lean towards to the PVC over MC. By code the PVC is to be supported at least every 3 feet and secured within 3 feet of every box. If supported correctly you should not have any big sagging problems. If you live where the temperature swings by a large amount and you have a long straight continuous run from wall corner to wall corner, use a slip joint in the line to allow the pipe to expand and contract.
 
OP
B

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,889
Location
Essex Co., NJ
The correct wording is: or should I do it right and run EMT?
Answer: Yes



Agreed, leave the PVC for underground installations and use EMT for aboveground exposed work.

My previous garage had all EMT, but it was cleared out when I did the job. I guess I remember what a PITA is was bending it with nothing in the way. I need to be able to locate some new outlets without having to remove the stuff in the garage for my current location.

I thought PVC would help in that.
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Just use pvc if you want. It's ridiculous that people are saying to use emt to do it right. That's like saying to rip down all the Sheetrock and run romex in the walls to do it right.
 

kd3pc

Well-known member
Joined
Aug 10, 2013
Messages
3,630
Location
Northern Neck
unless it is attached every foot or less, the PVC will sag. even more so, when the temps fluctuate. If you don't mind a saggy noodle mounted on your wall, then go for it.

If looks are important use emt and a level, if properly bent and attached it will stay that way for decades. PVC not so much
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Oh come on now.... needs to be supported every foot or less. :lol_hitti


unless it is attached every foot or less, the PVC will sag. even more so, when the temps fluctuate. If you don't mind a saggy noodle mounted on your wall, then go for it.

If looks are important use emt and a level, if properly bent and attached it will stay that way for decades. PVC not so much
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
it's true if you don't want sag. we have process areas that we use surface mount pvc in and in 6 months it looks like hell. it works, it just looks like hell
 
OP
B

Banjorear

Well-known member
Joined
Jul 22, 2013
Messages
1,889
Location
Essex Co., NJ
This is a garage that will heat up and cool down like a house so I don't think the PVC will see any extremes swings in temps.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Emt, or mc cable IMO. The rules regarding mc and Romex are only slightly similar. If your on the surface of the wall your fine. I would def not use PVC. For looks reasons. I would go emt all the way. I'm doing it in my own building.
 

LifeLongWNYer

Well-known member
Joined
Oct 23, 2013
Messages
1,231
Location
South of Rochester, NY
I'm in the planning stages of a garage and know just enough about the NEC to be dangerous.

I'm guessing from the previous comments that the the newer NEC versions specify that wiring in a garage needs to be in some form of conduit, either EMT or PVC. My questions, if someone was taking the time and trouble to pipe a garage with conduit, why would he run Romex inside of it? Why take up all the space that Romex does in the conduit, when running THHN would be easier and less expensive?



.
 

tmunsch

Well-known member
Joined
Nov 10, 2013
Messages
49
Location
Baytown, Texas
Have you thought about wiremold? They sell it at most Home Improvement stores. It's modular, constructed of metal and can be installed with basic hand tools, no conduit bender etc. required. Makes a nice looking job too.

Someone correct me if I'm wrong, but I think any PVC run above grade is supposed to be schedule 80. I don't think the intent for PVC was to wire shops or garages. Can you do it, yes. Should you do it...NO...a couple of reasons....

Plastic conduit of any kind is brittle. In cases of extreme cold it can crack if subjected to impacts, where as not so much with metal conduit....

The other downside about running it inside a structure is flammability. In the case of an arc fault, PVC can be exposed to high temperatures and could ignite if the arc fault duration is excessive, it is plastic after all...

Run it in something metal and err on the side of caution......IMHO..