I have my meter base installed with conduit through the wall into my 200amp breaker panel. What size cable do I need to run from the meter base to the panel?
 
To avoid these ads, REGISTER NOW!

Fueler

Well-known member
Joined
Jun 22, 2006
Messages
1,620
Location
Urbana, IL
I wired my whole shop to code and beyond but that part I paid a Union Pro to do. That is some big nasty wire to fool with and needs to be done just so. It was well worth it to me and he gave me a few tips while he was here..
 

katmat

Well-known member
Joined
Jan 10, 2007
Messages
91
If this is a home, you can use #2/0 copper, if part of it is outside, make sure the wire has a thwn rating. If this is a commerical application, it needs to be #3/0 copper. If the pipe is metal, make sure you use grounding bishings & then a copper jumper wire (#4). Also make sure you ground it correctly!!!
 

markb1

Well-known member
Joined
Jan 24, 2007
Messages
241
Don't use cable use individual wires.
4/0 AL type USE, THHW,THW,THWN are all acceptable for the 2-Hot leads
2/0 for the neutral
Use anti oxidant!

If you want copper go 2/0-2/0-1/0 same type insulation as above.

Bond as stated above with the bond bushing on the panel side and a plastic bushing on the meter side of conduit. Disregard bonding conduit if plastic.
Hope this is helpful
Mark
 
OP
Y

Yotaforce

Well-known member
Joined
Aug 24, 2007
Messages
377
Location
Western NC Mountains
It is for service into my new steel shop building. It is going through PVC conduit. I see two contacts in top of the meter box and then two main contacts in my service panel. Is there a ground? Or is it simply two cables taht run from the transformer to the meter and on to the panel?
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
markb1 has it right, but so does Fueler.
I am a great beliver in DIY but, your questions are so basic that I think you should hire a pro for this part.
After the panel you have CB's to protect you from any mistakes you may have made.
Between the meter and box there is no such protection. You have to do it right the first time.
Plus it will make the power co more comforable.
 
OP
Y

Yotaforce

Well-known member
Joined
Aug 24, 2007
Messages
377
Location
Western NC Mountains
There is no power yet. I have to have all of this finished up before I can even call the power company to get on their schedule. I also have to have the inspector come out before that. I am not willing to pay someone to install 7' of wire that would take me about 10 minutes and a trip to Lowes. I built the building, ran my plumbing, and wired the whole thing myself, so to waste money now on something so simple would be stupid. I have had working experience in all these feilds but I have never worked for the power company or on the 'other side' of the breaker panels. I just need to know what size wire comes out of the meter and into the breaker panel.
 

bluesman2a

Well-known member
Joined
Aug 16, 2005
Messages
1,312
Location
Atlanta, Ga.
On mine (which was a 400A service with 2 X 200A panels on it), I used 4/0 - 3 wire + ground service wire. I *THINK* you may be able to drop a size if you're 200A all the way through.

Also, don't forget you need to do your grounds too. I believe there you'll need 2 8' long ground rods approximately 10' apart with #4 bare copper bonding the two, then back into the cut-off. You'll also need to ground to your foundation (see some of my issues a while back) and ground that to the panel as well.

As mentioned above get some no-lox (anti-oxidation gunk) and make sure all the ends of your service wires are gooped up where they go into the lugs.

I'm doing all this from memory, so I may stand corrected, but you get the idea. Also FWIW, I DID get all the supplies from Lowes.
 

g17jimmy

Well-known member
Joined
Sep 21, 2007
Messages
83
I just installed mine at the beginning of Dec. I used 2 4/0 AL for the hot leads and 1/0 AL for the neutral. Duke energy had left several yards of the stuff at my brother's house when they installed his service last year, so all I had to do was get the antioxidant.
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I have my meter base installed with conduit through the wall into my 200amp breaker panel. What size cable do I need to run from the meter base to the panel?

Copper THHN/THWN:
3/0 phases
1/0 grounded(neutral)

Aluminum USE:
250kcmil phases
3/0 grounded(neutral)

If this were for a house the wire sizes would be slightly smaller. Rule of thumb is 2 sizes smaller on the grounded(neutral) conductor.
 

Farmallgray

Well-known member
Joined
Nov 30, 2007
Messages
95
Location
Spring Mills, Pa
When I did mine I got it at Lowes. I think they just called it 200A SE.
It was 3 individual conductors on a big spool. IIRC it was 2 4/0 and 1 2/0 aluminun with black insulation. The 2/0 neutral had a yellow stripe.

Mine is overhead with a mast. I fed the wires in the mast and from the meter to the panel, but had an electrican make the connections just to be safe.
I was a little unsure of myself for that part and just wanted him to double check my work before the inspection.
 

markb1

Well-known member
Joined
Jan 24, 2007
Messages
241
Utility conections are always on top, load connection on the bottom, neutral could be a lug to one side attached to inside of meter box.
No grounding in the meter, that will take place in breaker panel.

See my previous post for wire size, make sure you color code the neutral with white tape on each end.

I could quote code sections for wire size etc. if you want.
Mark
100aoverheadmeterbaselineload.jpg
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Don't use cable use individual wires.
4/0 AL type USE, THHW,THW,THWN are all acceptable for the 2-Hot leads
2/0 for the neutral
Use anti oxidant!

If you want copper go 2/0-2/0-1/0 same type insulation as above.
Mark

See my previous post for wire size, make sure you color code the neutral with white tape on each end.

I could quote code sections for wire size etc. if you want.
Mark

Table 310.15(B)(6) does not pertain to shops. He must use Table 310.16. These are the MINIMUM sizes:

Copper THHN/THWN:
3/0 phases
1/0 grounded(neutral)

Aluminum USE:
250kcmil phases
3/0 grounded(neutral)

For the members online without a codebook, Art. 310 pages 144-145.
http://www.nfpa.org/freecodes/free_access_agreement.asp?id=7005SB
 
Last edited:
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Last I bought was the triplex on a spool. Needed some for a service entrance down a mast to the meter/disconnect/8 pos breaker panel, and it was USE-2, 4-0 is good for 205 amps per 310.16. Was a case of overkill, the panel is only supplying a 5 hp deep well pump and a 360 watt lighting system, nothing else, never will, out in a field. I used the GE combo meter socket/disconnect/breaker panel to simplify the installation.

I used a short section of this same stuff (USE-2 4-0) to connect the meter thru a wall (PVC conduit, meter and panel back to back) to a breaker panel in my shop. Metal building, sounds like the same thing Yotaforce is trying to do.

Charles
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
You can't use the 90C column Charles. The wire may be rated for a temp of 90C but the equipment/terminations aren't, which limits you to the 75C column.

110.14(C)(1)(4)(b)
 

markb1

Well-known member
Joined
Jan 24, 2007
Messages
241
Aceman

You are right, I stand corrected.

Thanks for catching that.
 

Flatmotor

Well-known member
Joined
Nov 29, 2007
Messages
58
Location
Arkansas
You might want to get a set of specs from the utility that is suppling the power to save you some headaches. Most follow the NEC but not always. Bill
 

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,639
Location
Iowa
You might want to get a set of specs from the utility that is suppling the power to save you some headaches. Most follow the NEC but not always. Bill

Although you may get some good advice from the local utility co, Most do not follow the NEC as it has NO jurisdiction over them.

William....
 

Flatmotor

Well-known member
Joined
Nov 29, 2007
Messages
58
Location
Arkansas
Although you may get some good advice from the local utility co, Most do not follow the NEC as it has NO jurisdiction over them.

William....

Thats correct, the utility is the authority having jurisdiction over the service and will have the final say if they will tie on to it or not. If this is about the load side of the meter I would stay with NEC requirements. Bill
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Aceman

You are right, I stand corrected.

Thanks for catching that.

No big deal:)

Thats correct, the utility is the authority having jurisdiction over the service and will have the final say if they will tie on to it or not. In my area you have to follow the utility specs or it will not get hooked up. Bill

The utilities in my area are only concerned with the wire before the meter base. The wire after the meter, is the electrical inspectors job.
 

HSS

Member
Joined
Jan 31, 2008
Messages
5
Location
Arkansas
No one mentioned what size ground wire to run. Here it's a #10 solid copper from one ground rod to the breaker panel. The inspector won't pass it without the ground.
 

Flatmotor

Well-known member
Joined
Nov 29, 2007
Messages
58
Location
Arkansas
No big deal:)



The utilities in my area are only concerned with the wire before the meter base. The wire after the meter, is the electrical inspectors job.

Sorry, I thought the question was about the service to the meter. Bill
 

HSS

Member
Joined
Jan 31, 2008
Messages
5
Location
Arkansas
you're right, but, as long as he is pulling his on wire and it has to be inspected he might as well pull it all and not have to have the inspector do a reinspection. Just a thought.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
No one mentioned what size ground wire to run. Here it's a #10 solid copper from one ground rod to the breaker panel. The inspector won't pass it without the ground.

You can bet that is the one thing the inspector, anywhere in the country, will look for, they might ignore everything else, but not the ground.

#10 is too small, that I'm sure of..... :) NEC 250.66 lists sizes based on Service Entrance size, and #8 is the smallest allowed. For 4/0 and 250 kcmil, the required size is #4 copper.

Charles
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
You can't use the 90C column Charles. The wire may be rated for a temp of 90C but the equipment/terminations aren't, which limits you to the 75C column.

110.14(C)(1)(4)(b)

So it is. I'm not going to get real concerned about it, you ought to see what the power company ran to the meter on my shop, no where near as big as 4/0. I questioned the guy, but he "assured" me I would not have any problems:shocking:

I haven't come close to a 100 amp load yet, let alone 200 amps.

Charles
 

markb1

Well-known member
Joined
Jan 24, 2007
Messages
241
As an electrician we are taught to learn the code and follow it. I don't think we ever really learn it all, but learn how to find what applies, to a given installation. Many times more than one code reference will apply and a lot of times these are up for interpretation. Inspectors point out our mistakes with code reference and help us learn.

As Aceman pointed out my mistake he backed it with a code reference, this keeps things on track. The code is the bible so to speak and keeps systems consistent and standardized in the name of safety.

The code is a minimum standard.
What works for you may not work for the next person that owns your property and inherits your wiring. When the next person maxs out the 200a panel that you didn't have a problem with, the one little detail you cut a corner on or didn't do to code, could lead to a chain reaction of failures, sometimes over a long period of time, like the lug that overheats repeatedly gradually loosening up and then, starts arcing, or slowly burning the insulation back unnoticed, until you have a real problem.

Shock and fire, not to be taken lightly.


Power Companys have their own set of standards that don't apply to building wiring.

Thats my rant, I feel better, and hope it helps people understand the reason behind the code.