Trying to figure out if I have the correct load calculated for my T5 HO lights.
5 fixtures, 2 ballasts each. 1 ballast runs 2 lamps, the other runs 4
2 lamp ballast says .99 amp on 120v voltage,
4 lamp ballast says 2 amp on 120.
also have a 69w LED wallpack for an overhead exterior light on the circuit.
I come up with 15.525 amps.
Should work fine on a 20amp circuit right?
5 fixtures, 2 ballasts each. 1 ballast runs 2 lamps, the other runs 4
2 lamp ballast says .99 amp on 120v voltage,
4 lamp ballast says 2 amp on 120.
also have a 69w LED wallpack for an overhead exterior light on the circuit.
I come up with 15.525 amps.
Should work fine on a 20amp circuit right?