sberry
Banned
I might be mistaken but I believe the uffer requirement came with 2008?
Poco is coming out to verify neutral with the beast.
Recommendation is to install a dielectric union to the water meter. They have had this issue and make this recommendation. They do not want the current on the water lines, it is a safety issue.
I have to install the union.
They do not want the alternative "backup" path.
I might be mistaken but I believe the uffer requirement came with 2008?
Can you get to the transformer? If so use a long piece of wire and check continuity from the transformer to your neutral. Analog meter would work best. If you can isolate the utility neutral from your ground system safely, you should be able to check the integrity of your neutral connection.
that is insane.......
I think this is actually pretty noticeable in residential areas, sometimes several service from same transformer, a nick in an underground wire somewhere is as likely as anything. The earth is loaded with stray currents from many things. These stray currents come from many sources. One is the fact that between your grounding electrode at home the system transformer, there are currents through the earth in parallel with your service neutral. These are a fact of life and how much current depends on a lot of things. Also, you, or your neighbors could have a piece of UF going out to a yard light that has a nick in the insulation. Black or white, it don't matter. Some current is leaking out of this nicked insulation and will find it's way back to the electrical system through the earth.
is there cable TV? isolating the water pipe doesnt fix the problem, all it does is mask it (and possibly damage your electronics in the process)
Another suggestion would be if the utility can't isolate this problem is to get a real electrical contractor involved one with a engineer or forensic engineer on staff. What I mean by "real" is not one of those phony franchise outfits that advertise on TV and Radio, call a local outfit that takes on big projects, they usually have the guys who have the smarts and troubleshooting abilities along with the latest in diagnostic toys that could resolve this issue in short order. Sometimes a utility will not find a problem until they are challenged by a electrical engineering firm or contractor that has some pull or some contacts with the higher ups in the utility
Unfortunately there are stray voltages all over, especially in cities, there are countless cases where people have been killed from stray voltages when they walk over man hole covers, touch light poles, etc. Here are a couple article links that will emphasize the dangers of stray voltage and the one story is how the city had to hire a outsider because their guys and the utility couldn't figure out how the deadly shock happened; which drives home my theory why you might need someone beyond the utility.
http://www.wkyc.com/news/news_article.aspx?storyid=6186http://findarticles.com/p/articles/mi_qn4188/is_20030613/ai_n11389430/
http://www.kdvr.com/news/kdvr-dog-electrocute-lawsuit-txt,0,4480982.story
Come on, this is ridiculous. Do you think that some "forensic" clowns know more than the combined knowledge of the Poco power quality EE, the linesman, and ME, another EE??? We have real EE's not electrical contractors.
It all makes sense now after study. This is not some crazy scenario. My prior post late last night explained exactly what is happening and what should be happening with the current divider. The current is splitting back on the service neutral and the ground, which is a very low impedance path back in my scenario. Most houses on the block are putting current in that water pipe. The water pipe is smoking hot. I'm surprised that the City has not put in plastic meters or dielectric unions yet. I imagine they have to jumper the water main before working on it. They may have a dielectric union that will fit the water meter tailpiece.
The poco and their Beast confirmed that the neutral is perfect (and I did not have any voltage fluctuations anyway. We disconnected the ground wire from the water bond to make it safe to open the system. Turns out there are other paths for current to get on that cold water pipe so I will have to shut down before opening the water supply to install the bushing.
This is a common problem/scenario. Putting 30-40 percent of neutral current down the water line is not uncommon. That was the question that I was trying to get answered last night and the poco answered it today.
What is the difference between that and a plastic meter or a plastic water line?
This is the only solution if you want to keep the power out of that pipe. The path on the ground wires simply another low impedance path for the neutral current.
Think about the current paths here. On the one hand you have 1/0 aluminum about 50 feet to the junction block in the handhole. On the other path you have #4 copper (about 30 feet), about 6 feet of 1 inch type L copper, a few feet of steel or cast iron 8 inch main - there are houses right behind me in the alley - another service lateral or laterals of your neighbor(s), then their #4 ground wire, which may be very short to their panel(s), and then the alum neutral(s), which may be quite short compared to yours.
Copy of 2004 house inspection section attached:
Nothing in the garage, the meter can is on the outside wall directly behind the panel. There is pipe that runs into the ground from the meter can, so the poco may be using that. I'll do a closer look-see next time we're over there. I did describe what I was seeing to the engineer and they will come right out to look it over good when we take possession of the house. He was concerned and wanted to see the inside panel.
Copy of 2004 house inspection section attached:
Nothing in the garage, the meter can is on the outside wall directly behind the panel. There is pipe that runs into the ground from the meter can, so the poco may be using that. I'll do a closer look-see next time we're over there. I did describe what I was seeing to the engineer and they will come right out to look it over good when we take possession of the house. He was concerned and wanted to see the inside panel.
Well, the union is going to be underground and not accessible. There is no way a human is going to be able to use his or her body to jumper this. Most of it will be under concrete and only the part of the ****** that connects to the meter will be touchable - with some digging inside the water meter box.
I thought of this last night but I just let the poco engineer do the talking and he made this recommendation. I didn't tell him I wanted to do this. But, I didn't fight him either, because it all seemed to make sense.
The SCE engineer said that many local cities have this problem and some require the unions or have switched to plastic meters. This is a safety issue for the City water departments and it is a safety issue for plumbers within the house.
I get your point and i would go with whatever the poco says to do, but it doesnt seem good to me -i need to educate myself more on the matter and what is accepted practice in this situation
that is insane.......
Chris,
Look on the other side of that panel. On mine, for example, there is a customer bus bar that faces the outside (through wall panel) "reverse all in one." The ground wire that goes to the UFER or ground rods and the water bond comes up and lands on the bus bar on the outside facing part of the panel. You wouldn't see my wire either if you took a picture of mine like the one you posted.
That bus bar I referred to would be connected to that neutral wire that lands on the combined neutral/ground buss that you are looking at there.
I think the reverse all in one panels are the only way to fly.
A
I didn't think so as long as the transformers accesible and close. The outside of the case should be bonded to their neutral and be at ground potential, and if you can safely isolate their neutral from your system you could check the resistance back to the transformer through both the neutral and the waterlines seperately. OP seemed to have the no how as to whether he could do this safely or not.
I also agree with the OP and the Poco that if the impendance of the Neutral and the water mains are similar then you'll have neutral current through both.
My suggestion was based on a small padmount transformer. Do they even guard those things? Its the first of the month, and I've got to go INSIDE the switchhouse of a 43/4.16 40MVA transformer to read the meters. Should I be nervous?
I perform a very similar test on the entire grounding system of a large plant annually.
A
I didn't think so as long as the transformers accesible and close. The outside of the case should be bonded to their neutral and be at ground potential, and if you can safely isolate their neutral from your system you could check the resistance back to the transformer through both the neutral and the waterlines seperately. OP seemed to have the no how as to whether he could do this safely or not.
I also agree with the OP and the Poco that if the impendance of the Neutral and the water mains are similar then you'll have neutral current through both.
My suggestion was based on a small padmount transformer. Do they even guard those things? Its the first of the month, and I've got to go INSIDE the switchhouse of a 43/4.16 40MVA transformer to read the meters. Should I be nervous?
I perform a very similar test on the entire grounding system of a large plant annually.
I am suspect of the plastic ****** fixing the issue. Sure it will make the return through ground a higher resistance, but what path will the current now take? Separating this may very well force the real issue to be visible. I am still curious how much current would be on your neutral and the ground system if you only have one active circuit on one leg.
Thanks,
Jeff
Come on, this is ridiculous. Do you think that some "forensic" clowns know more than the combined knowledge of the Poco power quality EE, the linesman, and ME, another EE??? We have real EE's not electrical contractors.
It all makes sense now after study. This is not some crazy scenario. My prior post late last night explained exactly what is happening and what should be happening with the current divider. The current is splitting back on the service neutral and the ground, which is a very low impedance path back in my scenario. Most houses on the block are putting current in that water pipe. The water pipe is smoking hot. I'm surprised that the City has not put in plastic meters or dielectric unions yet. I imagine they have to jumper the water main before working on it. They may have a dielectric union that will fit the water meter tailpiece.
The poco and their Beast confirmed that the neutral is perfect (and I did not have any voltage fluctuations anyway. We disconnected the ground wire from the water bond to make it safe to open the system. Turns out there are other paths for current to get on that cold water pipe so I will have to shut down before opening the water supply to install the bushing.
This is a common problem/scenario. Putting 30-40 percent of neutral current down the water line is not uncommon. That was the question that I was trying to get answered last night and the poco answered it today.
Turns out there are other paths for current to get on that cold water pipe so I will have to shut down before opening the water supply to install the bushing.
.