Can 8-2 Romex be used for machine cord?

estesbubba

Member
Joined
Jul 29, 2014
Messages
20
i ran 8-2 with ground on a 40 amp circuit for my dust collector. The machine doesn't have a cord and you have to wire into its switch. Can I use the leftover Romex and wire it into the box and put a plug on it? If not what should I use for a cord? it's interesting the machine uses 12-2 wire from the switch to the motor but calls for a 40 amp circuit. The motor is rated at 22 amps.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
The answer is no.

In regards to sizing wire, motor circuits are sized differently because the breaker doesnt protect the wire. The overloads do. The breaker is sized higher to prevent nuissance trips due to in-rush currents. Size wire for motor circuits at 125% of NEC FLC table current. And the 12-2 on the machine probably has a higher temperature rating!
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
But if a plug is used, the overcurrent protection cannot exceed the rating of the plug / receptacle. The only way for those ratings to be used is when hardwired.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
But if a plug is used, the overcurrent protection cannot exceed the rating of the plug / receptacle. The only way for those ratings to be used is when hardwired.

Based on the FLA of the motor, its rated at more than 3hp so it needs to be hardwired...
 