Can I add 220v here?

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
I just wanted to know if it is possible to add a similar breaker in this spot next to the meter. Like how the AC one is done instead of the subpanel inside the garage since the sub is packed as it is.

Behind the wall is the garage as well so the wire can go out easily.

I would like to add a 40 or 30 amp for a compressor if it is indeed possible I will have a electrician come out and wire it.
 

Attachments

  • image.jpg
    image.jpg
    12.5 KB · Views: 327
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You lost me. There is no spot to add another breaker. There's only two spots, the main and the AC are using them.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,718
Location
Long Island
If you're right!

ROTFL!

So that "Main" feeds a panel somewhere? And the AC breaker feeds an AC directly? If it were my problem, I'd pull the AC breaker and use that to feed a new sub, and feed the AC (and whatever else you need) from that new subpanel.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
ROTFL!

So that "Main" feeds a panel somewhere? And the AC breaker feeds an AC directly? If it were my problem, I'd pull the AC breaker and use that to feed a new sub, and feed the AC (and whatever else you need) from that new subpanel.

Bingo! We have a winner. If I'm right? :spit:
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,861
You may can use a double double pole breaker. I have seen them with 50 amp and then 30 amp together that fit a double pole space. These are usually for a stove/dryer or stove/water heater. Other wise it's going to take a sub-panel and probably an electrician to do the work if you are not comfortable working on hot boxes.
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Ok I was just wondering if this can be expanded at all. I understand there is currently no space visually but can parts be changed out to add another breaker?

For example my previous house only have a single 100 amp, this has another one, do they have a bigger box that accommodates 3 or more?
 
Last edited:

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,622
Location
The romantic hills of central Umbria, Italy,
I would almost bet that your ac breaker is subordinate to your main breaker. Meaning your main breaker feeds the 2 bus bars in the panel, and the AC breaker feeds FROM those 2 bus bars to give you your 220 for your air conditioner...

I would instead slit this off to a pair of subs - your household and your A/C or shop (or whatever) and then run whatever you need from those subpanels...
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I would almost bet that your ac breaker is subordinate to your main breaker. Meaning your main breaker feeds the 2 bus bars in the panel, and the AC breaker feeds FROM those 2 bus bars to give you your 220 for your air conditioner...
WHY would you think this??

That is a 4-space meter/main enclosure. Both of those breakers are mains.
 
To avoid these ads, REGISTER NOW!

bjcouche

Well-known member
Joined
Sep 11, 2010
Messages
509
Location
Ohio
It looks like by the picture, you have a Square D Homeline meter main. I'm guessing they wired your air conditioner to the 2nd main because the meter box is close to the air conditioner and they saved $5 in wire...

Anyhow, If indeed it is a Homeline panel, you cannot use the breaker that PattenP linked to, even though it may fit and work. Breakers have to be "listed" for use in the particular panel. Generally manufacturers only "list" the breakers that they make, and not those from other manufacturers. There are some exceptions however, but they get pricey and very difficult to find.

The only Homeline "quad" breakers that I have seen only have the two inner poles tied together and not the outer two. Since you are trying to add a 240V feed, this will not work for you.
This is all that Square D offers and it won't work for you:
http://www.lowes.com/pd_8934-296-HOMT2020230CP_0__?productId=3129819

What I would do is install a subpanel. Move the air conditioner breaker to the subpanel, then feed your subpanel from where the air conditioner breaker originally was.

It's more work but you'll have many more spaces in the subpanel for future additions.

Brian
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,774
The breakers look like Challenger before Westinghouse bought them, and are now defunct.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
ROTFL!

So that "Main" feeds a panel somewhere? And the AC breaker feeds an AC directly? If it were my problem, I'd pull the AC breaker and use that to feed a new sub, and feed the AC (and whatever else you need) from that new subpanel.

This would be the way.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,774
BTW, no quad breakers will fit that meter can as they will not have the notches to accept a CTL quad or twin. Only a non-CTL type made for panels manufactured prior to 1968 & not sure quads for that purpose are made anymore, it would improper to even use them.
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
ROTFL!

So that "Main" feeds a panel somewhere? And the AC breaker feeds an AC directly? If it were my problem, I'd pull the AC breaker and use that to feed a new sub, and feed the AC (and whatever else you need) from that new subpanel.

So I an going to talk to a electrician soon, the best way is to change that ac breaker to a 100 amp and go to a new subpanel, where I will have the air compressor and welder circuit plus the original AC breaker, and hopefully the AC wiring is able to reach it? Likely the sub will need to be on the back side of this wall in the pic. I also like a new 20 amp 120v if possible so I can use a shopvac and tablesaw together one day.
 
Last edited:

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
the best way is to change that ac breaker to a 100 amp and go to a new subpanel...

Asking and getting advice from a local electrician is a great start, and they will tell you what you need to do, and how to get there!

Good luck, and let us know what they say, and what your final plan of action is!

Jim
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,452
Location
SE MI
So I an going to talk to a electrician soon, the best way is to change that ac breaker to a 100 amp and go to a new subpanel, where I will have the air compressor and welder circuit plus the original AC breaker, and hopefully the AC wiring is able to reach it?

Not likely, but not a big deal. The current AC line can be spliced inside that box and the additional wire can be run through the same conduit to the new sub.

Likely the sub will need to be on the back side of this wall in the pic. I also like a new 20 amp 120v if possible so I can use a shopvac and tablesaw together one day.
Good place for it. Just make sure you install a box with a "main breaker" to act as the disconnect and enough slots for future expansion.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,774
A main is not required but desirable, main breaker load centers are not a common item in CA but not impossible to find.
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
My thoughts exactly.:lol_hitti
Tommy

Hey, don't laugh. I have a friend whose wife has dyslexia. She would probably say it was 204v instead of 240v, and believe it!

When she talks about her retirement, she says she can't wait to start taking money out of her 401-OK account. No amount of prompting over the last 25 years has been able to get her to say it or write it the right way...

Jim
 

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
Always been one of my pet peeves. The correct voltages to refer to are 120 and 240 not 110 and 220.


Sent from my iPhone using Tapatalk
 