I want to run a series of outlets and pole lights around my yard. 20 Amps is a bit shy of what I need to do this so I'm thinking of running 30 amps on 10 gage wire out to the light/outlets. The breaker would be a GFI.
Question is: Can I use standard 20 amp outlets on the poles and still be OK code wise even though the breaker is 30 amp?
 
Last edited:
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
I want to run a series of outlets and pole lights around my yard. 20 Amps is a bit shy of what I need to do this so I'm thinking of running 30 amps on 10 gage wire out to the light/outlets. The breaker would be a GFI.
Question is: Can I use standard 20 amp outlets on the poles and still be OK code wise even though the breaker is 30 amp?

Yes, thats how i would do it.


You cannot use 30A breakers on 20A receptacles, you could put a small outdoor loadcenter at each receptacle location but that would get costly, a 20A multi-wire circuit would be a cost effective way to run it alternating receptacles between each leg.
 