I have a 220Volt, 2 phase, 40A breaker where i ran romex to a plug. for my air compressor/Tig welder.

If it was possible to daisy chain my 110vm 1 hase 30amp electrical wiring into this plug and run that wiring in a rigid conduit to the other plugs on my wall, that would be helpful. I would avoid using another breaker and not have to deal with the tight space in the panel that i am already dealing with.

Thanks for the advice
 
To avoid these ads, REGISTER NOW!

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
I have a 220Volt, 2 phase, 40A breaker where i ran romex to a plug. for my air compressor/Tig welder.

If it was possible to daisy chain my 110vm 1 hase 30amp electrical wiring into this plug and run that wiring in a rigid conduit to the other plugs on my wall, that would be helpful. I would avoid using another breaker and not have to deal with the tight space in the panel that i am already dealing with.

Thanks for the advice

The main reason for no is you will now have outlets and wiring rated for less than 40 amps protected only by a 40 amp breaker.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,254
Location
Coastal NJ
You mentioned an air compressor and a TIG welder. Not sure if you have 1 receptacle that you share for these tools or not, but ultimately they would be best served with separate circuits. Sounds like you should consider a subpanel.
 

rjacobs

Well-known member
Joined
Jul 24, 2015
Messages
3,858
Location
Dallas, TX
The biggest problem is there is/should be no neutral in that box. 2 hots and a ground. At least I have never run anything other than 3 wires into a welder receptacle.

The other, as was mentioned, are regular 110v outlets are generally only 15/20 amp outlets let alone the 14g(most likely) wiring that you would be using isnt rated to 40 amp either.
 

marinusdees

Well-known member
Joined
Oct 30, 2012
Messages
1,325
Location
Edgewood, Washington
There is such a thing as two phase. It was rare but may still be used in some places. This is not what he is dealing with. If he doesn't know any better than his, he should consult with/hire someone who does to do what he wants. IMHO
 
OP
B

Bigmansm

Member
Joined
Jan 4, 2010
Messages
24
Are you talking real two phase or what everyone calls single phase 220?
Bob
This may be true. I just thought it was two phase because of the way the breakers look.

The main reason for no is you will now have outlets and wiring rated for less than 40 amps protected only by a 40 amp breaker.
I was afraid of this. I was thinking i could use a GFCI outlet on that strand for protection.

You mentioned an air compressor and a TIG welder. Not sure if you have 1 receptacle that you share for these tools or not, but ultimately they would be best served with separate circuits. Sounds like you should consider a subpanel.

I do share a single plug. I have never needed both running at the same time.
 

Dragfluid

ALLIANCE MEMBER
Joined
Sep 15, 2013
Messages
17,471
Location
Pillager, MN
I do share a single plug. I have never needed both running at the same time.
Once my shed is completed, I'll have a Mig, Tig, and plasma cutter, sitting next to each other. I won't be using them at the same time, either. And each one will have its own outlet. Same circuit, though.

Every time you plug and unplug one of those, it takes just a little bit of life away from the receptacle. Do it nice, do it right. Give them each their own outlet.:)
 
Last edited:

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
A GFCI provides zero overcurrent protection. You would need a breaker.

But if you used a standard plug for a welder/compressor, there is no neutral.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
There is such a thing as two phase. It was rare but may still be used in some places. This is not what he is dealing with. If he doesn't know any better than his, he should consult with/hire someone who does to do what he wants. IMHO

Yeah, in 1901. :shocking:

Actually, I seem to recall there's a town in PA that still uses it in the government buildings...

Tommy
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Once my shed is completed, I'll have a Mig, Tig, and plasma cutter, sitting next to each other. I won't be using them at the same time, either. And each one will have its own outlet. Same circuit, though.

Every time you plug and unplug one of those, it takes just a little bit of life away from the receptacle. Do it nice, do it right. Give them each their own outlet.:)

To do it right is a dedicated circuit with one outlet, not multiple outlets on one circuit.
 

grzellmer

Member
Joined
Dec 17, 2015
Messages
20
If its two hot wires and a ground = No. If two hots a neutral and ground then yes BUT as others have said you'd need to put a main lug box in the middle so its 40A to the welder and 15A (14 GA wire) or 20A (12 GA wire) to the outlet. Since this is kind of a hack job (Safe but a hack job) I would recommend against it.
 

Ironhorse74

MEMBER EMERITUS
Joined
Nov 10, 2014
Messages
998
Location
The Pacific North Wet
It would be kind of hard since there's no such thing as 2 phase...:lol_hitti

Tommy

Not so fast. I worked for a short line RR, the CRANDIC. It was owned by an electric utility and used to run elecric street cars. I worked in the old house which was 2 phase. Each leg separated by 90 degrees. Antique as hell and pretty sure the only reason it was allowed to continue is that it was owned by the electric utility.

Brad
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I have a 220Volt, 2 phase, 40A breaker where i ran romex to a plug. for my air compressor/Tig welder.

If it was possible to daisy chain my 110vm 1 hase 30amp electrical wiring into this plug and run that wiring in a rigid conduit to the other plugs on my wall, that would be helpful. I would avoid using another breaker and not have to deal with the tight space in the panel that i am already dealing with.

Thanks for the advice

What is the HP rating on the compressor?

This may be true. I just thought it was two phase because of the way the breakers look.

I was afraid of this. I was thinking i could use a GFCI outlet on that strand for protection.

I do share a single plug. I have never needed both running at the same time.

GFCIs are NOT breakers. Read up on GFCIs!
 

Dragfluid

ALLIANCE MEMBER
Joined
Sep 15, 2013
Messages
17,471
Location
Pillager, MN
To do it right is a dedicated circuit with one outlet, not multiple outlets on one circuit.

In the OP's case, yes. It wouldn't be good for the compressor to be kicking in while he's laying a bead.

In my case, no. I can't use 2 welders at the same time. Not that talented.
And not going to make 3) 70' runs of 6-3.
 

70R

Well-known member
Joined
Feb 22, 2010
Messages
48
Location
West Lafayette, IN
Last edited:
OP
B

Bigmansm

Member
Joined
Jan 4, 2010
Messages
24
I'll just run another line if that is the case. It's extra work but not the end of the world.
 