Can I use a power meter like this?

BioHazard

Banned
Joined
Feb 3, 2010
Messages
743
I'm installing a subpanel and it would be nice if attached to that subpanel I had a submeter. Since most electric co's are going to "smart" meters, older analog meters are cheap and abundant. I'd like to just install a regular meter before the new subpanel.

Problem: I have three phase power. (208Y) The new panel is only getting 2 phases. Will a normal single phase, 120/240 analog meter work with my 120/208v setup?
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
I dont think it will read correctly since they operate on 240v. Might want to look into an emon-dmon, theyre like $300 though.

I also dont think you can stick a normal electric meter before your subpanel. Arent most meter cans listed as "suitable only for use as service equipment"
 

JBurgess

Well-known member
Joined
Mar 1, 2008
Messages
372
Location
Arizona
The normal 120/240 meters are 4 jaw. The 120/208 meters are 5 jaw.

You need the 120/208 meter to read correctly.
 
OP
B

BioHazard

Banned
Joined
Feb 3, 2010
Messages
743
I dont think it will read correctly since they operate on 240v. Might want to look into an emon-dmon, theyre like $300 though.

I also dont think you can stick a normal electric meter before your subpanel. Arent most meter cans listed as "suitable only for use as service equipment"
Damn...going for cheap here. I'm not sure how the meter sockets are "listed", but I don't necessarily care either. :) I was actually thinking about a meter/breaker box combo, but I haven't shopped around yet. There's a local demolition/recycle place I need to go dig through, they have TONS of cheap building materials, but you literally have to dig to find what you want...

The normal 120/240 meters are 4 jaw. The 120/208 meters are 5 jaw.

You need the 120/208 meter to read correctly.
Right...but a normal 3 phase meter is metering 3 hot lines. I only want to measure 2/3 of that.

I don't know, maybe I can find a cheap 3 phase analog meter...
 
Last edited:

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
The single phase meter may work for what you want to do. Find some EE and see if he can come up with a correction factor.
 

JBurgess

Well-known member
Joined
Mar 1, 2008
Messages
372
Location
Arizona
Right...but a normal 3 phase meter is metering 3 hot lines. I only want to measure 2/3 of that

The three phase meter takes a 7 jaw socket, the 120/208 "network" you want to meter takes a 5 jaw socket, line and load for the two phases plus a neutral connection is the 5th jaw.

I see used meters at one the local surplus stores (Phoenix) on a regular basis for about $100.
 
To avoid these ads, REGISTER NOW!

JBurgess

Well-known member
Joined
Mar 1, 2008
Messages
372
Location
Arizona
He is only using two "Hots" and a Neutral plus Ground on the sub panel.

Like this as I understand

network.jpg


The meter requires a neutral connection that a 120/240 does not.
 
OP
B

BioHazard

Banned
Joined
Feb 3, 2010
Messages
743
Still not quite sure I understand. A normal 1 phase meter just measures two hots. 120 in/out times two. But they run on 240v? How does it measure if you're only using a 120v load? I thought they metered each line seperately.

I can get an old analog 4 jaw meter for about $20 and the socket for $15-30. I could probably find a cheaper 5 jaw meter, but the socket is going to be the *****...(no such thing as "cheap" 3 phase stuff!)
 