In my new (to me) garage:
![]()
![]()
What type of appliance, tool or torture device would one plug into these?

![]()
This socket or pin shape is what we use in Australia. Although it is upside down and a very unusal and perhaps old looking socket. The same pisn pattern is now also used in China and upside down. In this situation the top centre hole would be earth.
That range receptacle is considerably larger in size then the receptacles used in OZ & NZ, which in turn is a copy of a obsolete US configuration.
OK, it looks the same as this to me, except the photo posted would be upside down to me 
OK, it looks the same as this to me, except the photo posted would be upside down to me
![]()


Top outlet is a 30 amp 220 volt outlet
bottom is an 50 am 220 outlet
Top outlet is a 30 amp 220 volt outlet
bottom is an 50 am 220 outlet
Top outlet is a 30 amp 220 volt outlet
bottom is an 50 am 220 outlet
I think the top one is actually 15 amps...look at the chart I posted earlier and compare the sizes of 15 and 30 amp receptacles; they have the same plug configuration, but the 30 amp is quite a bit bigger.
The larger outlet is an old-style 125/250v 50a receptacle (NEMA 10-50R). It can be used for a welder, but you have to be careful and may need to do some work to use it safely.
Right now it will most likely be wired with black and red Hot conductors and a white Neutral. This is an ungrounded receptacle, the range would have obtained 250v across the 2 hots and 125v from hot to neutral.
A modern welder uses a 50a 3-prong plug also, but expects 2 hots and a ground (6-50R). There is no neutral in this system, since the welder just uses 250v across the 2 hots.
If that receptacle is wired back to the main panel then you may be able to re-identify the neutral as a ground with green electrical tape at both ends, and replace the existing receptacle with a new 6-50R. If it's on a sub-panel you'll also need to move the panel end of the ground wire from the neutral bus to the ground bus, since they are not interchangeable in a subpanel.
I don't know about any of you but . . . That poor outlet from HOTFR8, looks so sad!![]()
Why such a sad face?
Teken . . .
I would have said it was more like 
If that receptacle is wired back to the main panel then you may be able to re-identify the neutral as a ground with green electrical tape at both ends, and replace the existing receptacle with a new 6-50R.
I agree that it's not usual practice, but you could make an argument that it would be allowed by 250.119 (B).pattenp said:I'm not trying to be a NEC cop, but just wanted to let you know it is not approved code to re-identify a non green insulated wire as a ground by placing green tape on it.
That said, the correct method would be to replace the existing wiring with a new run that has 2 ungrounded circuit conductors and a bare or green-insulated ground.2008 NEC said:Multiconductor Cable. Where the conditions of maintenance and supervision ensure that only qualified persons service the installation, one or more insulated conductors in a multiconductor cable, at the time of installation, shall be permitted to be permanently identified as equipment grounding conductors at each end and at every point where the conductors are accessible by one of the following means:
(1) Stripping the insulation from the entire exposed length
(2) Coloring the exposed insulation green
(3) Marking the exposed insulation with green tape or green adhesive labels
It would allow you to plug in the welder, since it will have a 6-50P 250v grounded plug, not a 10-50P 250/125v ungrounded plug. The point I was trying to make is that *if* the outlet is connected to a subpanel then the current neutral wire is not electrically the same as the ground wire required by the welder.tdkkart said:And exactly difference would this make, function or safety wise??
I agree that it's not usual practice, but you could make an argument that it would be allowed by 250.119 (B).
Originally Posted by 2008 NEC
Multiconductor Cable. Where the conditions of maintenance and supervision ensure that only qualified persons service the installation, one or more insulated conductors in a multiconductor cable, at the time of installation, shall be permitted to be permanently identified as equipment grounding conductors at each end and at every point where the conductors are accessible by one of the following means:
(1) Stripping the insulation from the entire exposed length
(2) Coloring the exposed insulation green
(3) Marking the exposed insulation with green tape or green adhesive labels
As it says, the conditions of maintenance and supervision ensure that only QUALIFIED persons service the installation............ This would have to be a factory, industrial, large commercial or other environment where you have "plant maintenance" or permanent or near permanent electrical maintenance personnel. You still run the risk of something undesirable happening.
Not something you could do in a home.Charles