As said earlier, NO you can not notch an I-joist.
You can NOT cut/drill/notch the flanges (except to cut to length).
There are limits on holes in the web (size, spacing, location). RTFM from the manufacturer.
example:
http://www.gp.com/build/product.aspx?pid=1390
You do NOT just go and cut a joist mid-span and leave it like that.
If you have to cut a joist (I-joist or any other type) mid-span, you go and 'box' out the cut section and run cross-joists to the adjacent joists in order to tie everything back together. Examples of having to cut joists mid-span would be for stairs or plumbing.
Or depending on the manufaturer's design/installation guidelines, you may be 'allowed' to shift one floor joist up to 3" for plumbing clearance (Georgia-Pacific manual, YMMV depending on the manufacturer so RTFM).
http://www.gp.com/build/DocumentViewer.aspx?repository=BP&elementid=4372
If your 'designer' said "OK, just leave a cut in the mid-span of a floor joist", then FIRE him/her/them right NOW. Cause they are an idiot.
If the floor joist was needed, it was needed. If the floor joist wasn't needed, then it shouldn't have been installed in the first place.
G-P I-Joist simple-span maximum span L/480 (stiffer than 'code', but results in a firmer and less bouncy floor and is recommended by G-P) with a 12" deep (actual is 11-7/8" deep) joist and a 24' span at 16" OC says you need a GPI-90 series joist (OSB web and LVL flanges) at that 16" OC spacing. That floor joist is needed.
IMNSHO.
You can NOT cut/drill/notch the flanges (except to cut to length).
There are limits on holes in the web (size, spacing, location). RTFM from the manufacturer.
example:
http://www.gp.com/build/product.aspx?pid=1390
You do NOT just go and cut a joist mid-span and leave it like that.
If you have to cut a joist (I-joist or any other type) mid-span, you go and 'box' out the cut section and run cross-joists to the adjacent joists in order to tie everything back together. Examples of having to cut joists mid-span would be for stairs or plumbing.
Or depending on the manufaturer's design/installation guidelines, you may be 'allowed' to shift one floor joist up to 3" for plumbing clearance (Georgia-Pacific manual, YMMV depending on the manufacturer so RTFM).
http://www.gp.com/build/DocumentViewer.aspx?repository=BP&elementid=4372
If your 'designer' said "OK, just leave a cut in the mid-span of a floor joist", then FIRE him/her/them right NOW. Cause they are an idiot.
If the floor joist was needed, it was needed. If the floor joist wasn't needed, then it shouldn't have been installed in the first place.
G-P I-Joist simple-span maximum span L/480 (stiffer than 'code', but results in a firmer and less bouncy floor and is recommended by G-P) with a 12" deep (actual is 11-7/8" deep) joist and a 24' span at 16" OC says you need a GPI-90 series joist (OSB web and LVL flanges) at that 16" OC spacing. That floor joist is needed.