I have a question about 8-304...
I am installing LED fixtures into a room in my house. They are recessed and sealed, so they can not have higher output bulbs put in them. (Trenz TL4W)
The total wattage draw on these lights will be 86W total for the 8 lights.
Also, in the room, are 7 120V receptacles. That brings the number of "outlets" up to 15 on the 15AMP circuit.
Now, am I interpreting Rule 3 correctly? The definition of connected load is the sum of all the loads connected in the circuit irrespective of the fact that whether it is being currently operated or not.
Therefore, my thinking is;
120V x 15A = 1800W @ 80% = 1440W or 12 A
Rule 2 says my receptacles are classed at 1 A each, so 7 A or 840W for the receptacles.
840 W receptacles + 86W lighting = 926 W. Leaving me with 514 W or 4 A left on the circuit....
Is this correct, in that, in this example, I will be permitted to have 15 outlets on the one circuit?
Thanks!
8-304 Maximum number of outlets per circuit
(1) There shall be not more than 12 outlets on any 2-wire branch circuit, except as permitted by other Rules
of this Code.
(2) Such outlets shall be considered to be rated at not less than 1 A per outlet, except as permitted by
Subrule (3).
(3) Where the connected load is known, the number of outlets shall be permitted to exceed 12, provided that
the load current does not exceed 80% of the rating of the overcurrent device protecting the circuit.
(4) Where fixed multi-outlet assemblies are used, each 1.5 m or fraction thereof of each separate and
continuous length shall be counted as one outlet, but in locations where a number of electrical appliances
are likely to be used simultaneously, each 300 mm or fraction thereof shall be counted as one outlet.
Thanks!