I'm replacing the roof on my 19' x 21' garage with gambrel attic trusses. I'm putting a door on the rear for a deck and stairs. I'd like to put a door on the front and add a short cantilevered balcony. The cantilevered boards would run perpendicular to the truss joists. They would rest on the garage header and under the trusses. I would like the balcony to extend 4'. Is this feasible?
 
To avoid these ads, REGISTER NOW!

p_mori7

Well-known member
Joined
Mar 23, 2010
Messages
3,340
Location
Montreal, QC., Canada
Cantilever means that the joists supporting the balcony run further back into the structure than what sticks out beyond the wall. Normally these joists would run in the same direction as floor joists or bottom chords of the trusses.

It reads like you are going to lag bolt into the header or some other type of mechanical fastening. Therefore the outer corners of your balcony would need to be supported back to the garage structure with angled support posts, or supported vertically down to a concrete piling that is as stable as the garage foundation itself (to avoid heaving).
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
I'm replacing the roof on my 19' x 21' garage with gambrel attic trusses. I'm putting a door on the rear for a deck and stairs. I'd like to put a door on the front and add a short cantilevered balcony. The cantilevered boards would run perpendicular to the truss joists. They would rest on the garage header and under the trusses. I would like the balcony to extend 4'. Is this feasible?

Yes.

Needs to be engineered.
 

boobag

Well-known member
Joined
Aug 15, 2010
Messages
397
If you go out 4' you have to go back in 8', don't know about setting this up with trusses though

this is the case for floor joists, but attaching to trusses is a whole other deal i'd imagine.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,727
Location
SE Michigan
One of the biggest issues is that you can't just extend SPF framing members out of the building and expect them to last in a deck/outdoor environment. That would leave a very large problem for down the road.

Alternatives are steel or pressure treated but the length of inner extension and the fastening method isn't trivial.
 
To avoid these ads, REGISTER NOW!

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,028
Location
NJ
I'm replacing the roof on my 19' x 21' garage with gambrel attic trusses. I'm putting a door on the rear for a deck and stairs. I'd like to put a door on the front and add a short cantilevered balcony. The cantilevered boards would run perpendicular to the truss joists. They would rest on the garage header and under the trusses. I would like the balcony to extend 4'. Is this feasible?

Feasible?

Yes. With engineering design and stamped drawings for the design.

Note: It is not as simple as just running some cantilevered deck joists under the truss and out into the air. Hence the engineering requirement.
 

Cyberbear

Well-known member
Joined
Nov 23, 2013
Messages
1,524
Location
California
Old Rule of thumb was 1/3 for porch/deck and 2/3 for leveraged support. Resting on the header is a good idea if it can adequately support it's usual load and the weight of the extension for materials and live load for people.
If you incorporated the correct size beams and reinforced the bottom truss stringer and used Simpson ties for strength, you could possibly do this. I imagine as with most building departments, wanting to accept no liability, you'd need an engineer's stamp on a set of drawings. Beware of liability issues w/o approval.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,156
Location
SE MI
Are we talking a balcony the people are going to stand on or a roof to shield the doorway from precipitation ? If people are going to stand on it, forget cantilever.

Doing ANY MODIFICATION to the bottom chord (or any chord for that mater) of a truss, including adding any kind of load, need to be approved by the company that engineered the truss.
 

Slednut

Well-known member
Joined
Dec 20, 2012
Messages
2,550
Location
Washington state
Here's what I did on my recent addition. 2x12x12s on 16 inch centers making up a 4 foot deck.
 