Work starts on our 28x40 next week. 11' walls with scissor trusses. I'm interested in these lights:

yhst-81563436181518_2122_65882334


$214 for each set of 4. I'm thinking 4 sets. A separate switched plug for each would add versatility. Thoughts or ideas? Thanks in advance. I've learned so much in a short time here.
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,135
Location
Minneapolis
Do you have a make, model, part number, or a web link? They look nice but it's difficult to comment without more information.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
interesting, but i highly doubt that product is UL listed, and i also question if installation as shown is nec compliant.
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
It doesn’t look like anything you couldn’t do with Wiremold.

But if it new construction, why not do it right?

A $1000.00 should buy you some good wiring.
 

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,971
Location
Akron-Canton area OH
I was looking at them in Menards last year. The last time I was in there they didn't have them. They were pricey. But on the other hand they were a neat idea.
BTW there are 4 lights for $216
 
Last edited:
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,764
I see the wiring between the fixtures as violating NEC 400.8(1) and (4).

400.8 Uses Not Permitted. Unless specifically permitted
in 400.7, flexible cords and cables shall not be used for the
following:
(1) As a substitute for the fixed wiring of a structure
(2) Where run through holes in walls, structural ceilings,
suspended ceilings, dropped ceilings, or floors
(3) Where run through doorways, windows, or similar
openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted
to be attached to building surfaces in accordance with the
provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located
above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted
in this Code
(7) Where subject to physical damage


The exception to #4 does not apply here as it pertains to busway.


This a copy & paste from the 2008 NEC, which is unchanged from the 2002 & 2005 editions.
 

swaterbenny

Well-known member
Joined
Nov 22, 2009
Messages
215
Location
New Richmond, WI
I see the wiring between the fixtures as violating NEC 400.8(1) and (4).

400.8 Uses Not Permitted. Unless specifically permitted
in 400.7, flexible cords and cables shall not be used for the
following:
(1) As a substitute for the fixed wiring of a structure
(2) Where run through holes in walls, structural ceilings,
suspended ceilings, dropped ceilings, or floors
(3) Where run through doorways, windows, or similar
openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted
to be attached to building surfaces in accordance with the
provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located
above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted
in this Code
(7) Where subject to physical damage


The exception to #4 does not apply here as it pertains to busway.


This a copy & paste from the 2008 NEC, which is unchanged from the 2002 & 2005 editions.

The way I see the product is that the cord is not attached it simply lays under a plastic cover, which is attached, but not a raceway.

Ben
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
has someone emailed the seller to see if the product is listed? i would be suprised if it is.
 

djb2

Well-known member
Joined
Apr 3, 2010
Messages
639
Location
Redwood forests
There isn't any code problem with a regular outlet feeding a detachable power cord for this type of lighting, nor with having both IEC C13 and C14 connectors on the lighting.

You commonly see this type of chained lighting under kitchen counters using IEC C5+C6 or C7+C8 connections.

I could see an inspector requiring a single hard-wired permanent lighting fixture in order to consider this plug-in lighting. But it would be stretch to disallow this lighting when other surface mounted or hanging plug-in shop lights are unquestionably allowed as the primary and permanent lighting.

The situation would be completely different with recessed or built-in lighting.

Oh, and make certain to always call that channel a "trim cover" not a "raceway" so as to not raise the issue. Covered wiring is the most likely aspect to be a problem.
 