I have a Carrier 60k BTU furnace that is short cycling with a 31 code. This is low pressure switch not closing after 5 minutes of run time so it's just running 5 minutes every 20. This translates to condensate drain blockage or vent issues.
The catch is that we just put an addition on our house and extended the venting. The book says up to 100ft of 2", even with all the elbows and the distance I can't calculate longer than ~85 ft so I'm hoping that's not it. I pulled the condensate trap today and it wasn't blocked by any means. We've been running the furnace for a couple of weeks and I'm not certain it hasn't been happening the whole time as it's been pretty mild so far. The temp dropped a be few days ago and it seems like it started struggling then.
I've got a cleaning scheduled for tomorrow but I'm wondering if you guys have any ideas. Could the LPS actually just be bad?
The catch is that we just put an addition on our house and extended the venting. The book says up to 100ft of 2", even with all the elbows and the distance I can't calculate longer than ~85 ft so I'm hoping that's not it. I pulled the condensate trap today and it wasn't blocked by any means. We've been running the furnace for a couple of weeks and I'm not certain it hasn't been happening the whole time as it's been pretty mild so far. The temp dropped a be few days ago and it seems like it started struggling then.