Prior to my mini-split install I watched numerous videos and read many threads to familiarize myself with the tools and the process. Install was successful (seemingly) and had been running for about 24 hours. I thought to check my four lineset connections one last time before buttoning up things. While slightly moving the 1/4" line at the connection point near the indoor unit I heard a leak. Mind you the whole system had held a vacuum prior to releasing any refrigerant, and I had leak tested all connections with soap bubble solution while on heating and cooling mode. (I did not do a nitrogen pressure test) But now there was a definite leak, that I could hear more or less depending on how I wiggled the line. Everything I had read had addressed how to deal with leaks prior to refrigerant being in the system, or perhaps how to correct slow leaks (where you could pump-down system, fix leak, add back proper amt of refrigerant). I did not know what to do with a significant leak on a pressurized system. I decided to torque it down, thinking that perhaps it was just under-torqued, increasing torque from 11 ft-lbs to 13 didnt seem to work, and in fact the leak was getting worse from the manipulation. (I had turned system off upon first noticing the leak). And then *POP*, the flare broke off completely releasing all refrigerant. At this point, all i could think to do was the close the high and low side valves at the outdoor unit, cap off and seal both ends of the open copper, leave the toxic vicinity, and rack my brain as to what went wrong.
My conclusion is that I must have either forgotten to, or applied an inadequate amount of nylog on the outside of the flare. Then when torquing it down to spec, the nut was grabbing the flare and twisting it. My attempt to tighten the connection to stop the obvious leak was the final straw that broke the flare clean off. That or the factory copper lineset and/or flare was faulty/poor quality.
It's quite likely and worth noting that even though the issue passed my vacuum test and initial leak detecter tests, It most likely would have failed and been noticed by a proper nitrogen pressure test, avoiding this disaster.
My initial response was to throw my hands in the air, and hire an HVAC professional to re-flare, re-connect, pressure test, vacuum, and re-charge.
My secondary response was to do more research, and figure out how to fix this problem myself. I am generally pretty precise about things and don't make mistakes like this often. I have no reason to believe that I'm just totally inept and shouldn't touch my system any more that I already have. Or maybe I'm just stubborn and want to fix what I mucked up.
In any case I've begun to familiarize myself with the process of adding refrigerant, and weighing it in. (after re-doing the flare, and evac-ing the system again)
My little questions regard the valves of the outdoor unit, and whether they should both by opened now when I draw a vacuum again. (previously the valves were closed when vacuuming because the ODU was full of refrigerant and I was only to vacuum the IDU & lineset. But now there is no refrigerant in the system, so I imagine it is proper to draw a vacuum on the ODU as well, by having both high and low valves open. I just want to make sure that there is no issue drawing a vacuum on the ODU, and that this is proper procedure for an empty system.
The second question is, while adding refrigerant, would I leave both high and low valves open, or perhaps close the low side so no liquid r410a enters the outdoor unit? (when I say high and low valves I'm referring to the outdoor unit valves, and not the high and low pressure guages on the AC guage set) Most youtubes concerning this step are in reference to a system where the outdoor unit is factory charged, and thus valves remain closed, extra refrigerant is added to the lineset to account for longer lines, and then valves are opened to release factory refrigerant. In my case the factory refrigerant has all been released to the atmosphere, and thus I'm charging the entire system with external r410a.
I much appreciate any expertise and advice!
My conclusion is that I must have either forgotten to, or applied an inadequate amount of nylog on the outside of the flare. Then when torquing it down to spec, the nut was grabbing the flare and twisting it. My attempt to tighten the connection to stop the obvious leak was the final straw that broke the flare clean off. That or the factory copper lineset and/or flare was faulty/poor quality.
It's quite likely and worth noting that even though the issue passed my vacuum test and initial leak detecter tests, It most likely would have failed and been noticed by a proper nitrogen pressure test, avoiding this disaster.
My initial response was to throw my hands in the air, and hire an HVAC professional to re-flare, re-connect, pressure test, vacuum, and re-charge.
My secondary response was to do more research, and figure out how to fix this problem myself. I am generally pretty precise about things and don't make mistakes like this often. I have no reason to believe that I'm just totally inept and shouldn't touch my system any more that I already have. Or maybe I'm just stubborn and want to fix what I mucked up.
In any case I've begun to familiarize myself with the process of adding refrigerant, and weighing it in. (after re-doing the flare, and evac-ing the system again)
My little questions regard the valves of the outdoor unit, and whether they should both by opened now when I draw a vacuum again. (previously the valves were closed when vacuuming because the ODU was full of refrigerant and I was only to vacuum the IDU & lineset. But now there is no refrigerant in the system, so I imagine it is proper to draw a vacuum on the ODU as well, by having both high and low valves open. I just want to make sure that there is no issue drawing a vacuum on the ODU, and that this is proper procedure for an empty system.
The second question is, while adding refrigerant, would I leave both high and low valves open, or perhaps close the low side so no liquid r410a enters the outdoor unit? (when I say high and low valves I'm referring to the outdoor unit valves, and not the high and low pressure guages on the AC guage set) Most youtubes concerning this step are in reference to a system where the outdoor unit is factory charged, and thus valves remain closed, extra refrigerant is added to the lineset to account for longer lines, and then valves are opened to release factory refrigerant. In my case the factory refrigerant has all been released to the atmosphere, and thus I'm charging the entire system with external r410a.
I much appreciate any expertise and advice!