Looking for some advice/recommendations. My garage is 21’ by 25’. The ceiling joists are 2x8x21’ that are 16” on center.

I would like to install drop down stairs to gain access to the space to utilize for storage.

Right now, there is no weight in the attic space and I can already see some of the beams sagging. It’s also noticeable on the Sheetrock where some of the beams are sagging.

What can I do to reinforce the joists in order to utilize the space. Ultimately I would like to lay down plywood and store basic stuff. I don’t want to worry about sagging and questioning if there’s too much weight up there.

Thank you in advance.
 

Attachments

  • IMG_8749.jpeg
    IMG_8749.jpeg
    605.9 KB · Views: 78
  • IMG_8754.jpeg
    IMG_8754.jpeg
    762.8 KB · Views: 78
To avoid these ads, REGISTER NOW!

lonestarky

Well-known member
Joined
Mar 28, 2011
Messages
367
Location
Lindenhurst IL
Not much you can do to improve the strength for sagging, other than tie them to the structure above. If you're storing light stuff, just throw some 1/2 ply down. Youll be ok. I would rather do that than run vertical sections to your rafters or ridge. You could run collar beams between the rafters to add queen posts and kind of truss it up, but then you're limiting space, and hanging more weight off the ridge.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,042
Location
West central Indiana
You can not store anything on those joist. At that length they are for a 5 psf load, basically drywall and insulation only.

You would have to sister 2"x12" floor joist on 16 inch centers to have a 30 psf storage load. Or place a support beam or wall under the ceiling joist down the middle to reduce the span.

Any other modifications will need and engineer.
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,579
Yeah, those are marginal for any added load. But, you can help a bit by adding a strong-back on top of the joists. Won't really add much load capacity, but will definitely help with the sagging you have now.
Every stick built roof I've seen that was built in the 70s or older had them.
Simple to install by laying a 2x6 flat on top center of the existing joists. Block under it at the top plate at both ends to transfer some load to the wall. Use ring shank nails driven at opposing angles, 4 per joist. Jack the existing joists up so they are slightly crowned up in the center. I use a temporary wall under the ceiling, just a board at the top to project the sheetrock, and temp studs cut slightly long. Now add a vertical 2x to the side of the 2x6, sides if you want. Nail it every 12 inches and tow-nail to the joists also, with ringshank.

Remove temp supports. The ceiling should now be flat. And maybe support some light storage. You can do a bounce/deflection test to determine that.



 

Old Moparz

Well-known member
Joined
Jan 21, 2005
Messages
1,171
Location
Newburgh, NY 12550
Yeah, those are marginal for any added load. But, you can help a bit by adding a strong-back on top of the joists. Won't really add much load capacity, but will definitely help with the sagging you have now.
Every stick built roof I've seen that was built in the 70s or older had them.
Simple to install by laying a 2x6 flat on top center of the existing joists. Block under it at the top plate at both ends to transfer some load to the wall. Use ring shank nails driven at opposing angles, 4 per joist. Jack the existing joists up so they are slightly crowned up in the center. I use a temporary wall under the ceiling, just a board at the top to project the sheetrock, and temp studs cut slightly long. Now add a vertical 2x to the side of the 2x6, sides if you want. Nail it every 12 inches and tow-nail to the joists also, with ringshank.

Remove temp supports. The ceiling should now be flat. And maybe support some light storage. You can do a bounce/deflection test to determine that.

Reminds me of what was being done in this method that I posted ages ago....


Be prepared for the naysayers to chime in. :ROFLMAO:
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,042
Location
West central Indiana
Reminds me of what was being done in this method that I posted ages ago....


Be prepared for the naysayers to chime in. :ROFLMAO:
That method works very well if you use good glue and structural screws. If it slips at all it’s not going to help.

While it might help the sagging especially any additional amount, it’s still not enough to allow for storage like the op wants to do.
 