Changed thermostat, now hot air on cool setting...

onelochevy

Well-known member
Joined
Jan 28, 2011
Messages
331
Location
Louisiana
And cool air on heat setting. I'm attaching pictures of the wiring from the old one and the new. Any idea on what wire is causing this issue? 1st pic is the old unit. 2nd is the new.
 

Attachments

  • PXL_20210109_134722977.jpg
    PXL_20210109_134722977.jpg
    86.7 KB · Views: 98
  • PXL_20210128_015558892.jpg
    PXL_20210128_015558892.jpg
    81.9 KB · Views: 102
To avoid these ads, REGISTER NOW!

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
Is new thermostat compatible with heat pump ??
Heat pump has a reversing valve


Sent from my iPhone using Tapatalk
 
OP
O

onelochevy

Well-known member
Joined
Jan 28, 2011
Messages
331
Location
Louisiana
This unit isn't a heat pump. Haven't tried swapping any wires yet, wanted to get some opinions first.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,026
Location
Peace Valley,mo
Did you program the new stat tell it what you want. Gas heat ,electric, heat pump

Sent from my KFDOWI using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,871
Location
NW Iowa
This unit isn't a heat pump. Haven't tried swapping any wires yet, wanted to get some opinions first.

Might be helpful to know what you do have then. It's not just a single stage gas furnace with that many wires

Probably a setting in the thermostat.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
Orange wire looks broken in both pics where the insulation is pulled back in the bunch.
 
To avoid these ads, REGISTER NOW!
OP
O

onelochevy

Well-known member
Joined
Jan 28, 2011
Messages
331
Location
Louisiana
Thanks everyone. I did set it up for my particular system. It's a conventional electric air/heat unit. I'll double check the settings this evening.
 

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,225
Location
Connecticut
It looks to me like he has a heat pump. That is consistent with description of an electric heating/cooling system. Note that the old thermostat had the orange wire connected to the “w” terminal for a non-heat pump system, but connected to the “O” terminal ifgoing by the heat pump legend. On the new thermostat, he has it connected to the white, with the “O/B” not used.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,871
Location
NW Iowa
It's pretty rare to see an electric furnace with A/C only. Only the outdoor unit is different and not even that much.

Seeing that orange wire makes me think heat pump since orange is normally used for the reversing valve.

Agree with the above post saying the orange wire is possibly on the wrong terminal.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
Looks like heatpump wiring on the old tstat, so the new one would be wired improperly, or the usual color code was not followed.

If you are getting cool air while calling for heat, that means Y is energized, thus the tstat must be setup for a HP (or there’s a short.)

Orange wire looks broken too.
 
Last edited:

ant.foste

Well-known member
Joined
Aug 14, 2016
Messages
403
Location
Maryland
Orange wire is broken.
Default o/b setting in tstat for needs to be adjusted. Read the manual.
 