Changing 8' fluorescent to something else

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
My garage has become very dark because of lights being out. Bulb, ballasts, dunno. Comes and goes.
What I do know is I want to swap out all 10 (5 x 2) 8 ft. fluorescents lights to something newer and brighter.
I would like to keep the fixtures as I painted around them and it is pretty ugly under there for sure.
What is the best way?
Cost isn't a problem, but I want to get it right so I don't have to set up my scaffolding again anytime soon.
Thanks
Rod
Lights.jpg
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
Convert your fixtures to led's. That's the easiest and probably the most cost effective route since 90% of the work has already been done. There are 8' ballast bypass lamps available, but I think they are a pos. I get kits that have new sockets and covers that will turn each fixture into one that will accept four 4' led tubes. Figuring out how to put the first one together was a pita, but after that, about 15 minutes per fixture. Being in Canada, I have no idea where you would get such an animal, but someone on here could point you in the right direction. I would imagine that shipping from my supplier would not be very cost effective.
 
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
That would work Sparky.
I really want to get rid of the ballast.
How hard is it to mount the 4’ receptacles
Have any pics?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
I don't have any pictures, but you scrap your existing ballast, fixture covers, shields, and sockets, leaving just the 8' long housing. The kits snap together and mount to the sides of the old fixture housing using self tapping screws. I have to leave for awhile, if I get back early enough I will throw a kit together and take a picture. There may be someone here that can post a link. The supplier I use doesn't have them on the website.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,764
Location
NW Iowa
High output or slimline?

The retro kits are a nice option but often don't work with reflectors. If it was me I would want to keep the reflectors. Not as much need for them with a directional lamp but they look nice in a garage.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
High output or slimline?

The retro kits are a nice option but often don't work with reflectors. If it was me I would want to keep the reflectors. Not as much need for them with a directional lamp but they look nice in a garage.
If the reflector is the ballast cover, then it goes away. It doesn't make any difference with the lamps I use because they don't shine any light off to the side or up, hence no need to reflect. I don't know if there are led tubes that are multi directional or not. If one wanted to keep the reflectors, then 8' lamps would work since they are available with either socket configuration. I converted 12 fixtures in a county parts room using 8' lamps and was not impressed one bit. With one of my customers, I am, one or two fixtures at a time retro fitting t8 and t12 HO's to these, and side by side, the led's using four 50k frosted lamps have a better light output according to the eye test.

I was going to put a four foot section of a kit together tonight, but discovered I already had one. Please don't pay any attention to the dust. It's the surviving half on an 8'er that had a collision with a fork lift. I get the universal adjustable width kits, but they are made to fit any width. I just get the adjustable because I never know what I am going to be up against. Put it together and screw it to the sides of the fixture. They are also made to fit tight to any width of fixture, but I haven't used that style yet.
 

Attachments

  • retro 1.jpg
    retro 1.jpg
    204.9 KB · Views: 99
  • retro 2.jpg
    retro 2.jpg
    136.6 KB · Views: 94
  • retro 3.jpg
    retro 3.jpg
    143.5 KB · Views: 94
  • retro 4.jpg
    retro 4.jpg
    196.3 KB · Views: 115
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,764
Location
NW Iowa
If the reflector is the ballast cover, then it goes away. It doesn't make any difference with the lamps I use because they don't shine any light off to the side or up, hence no need to reflect. I don't know if there are led tubes that are multi directional or not. If one wanted to keep the reflectors, then 8' lamps would work since they are available with either socket configuration. I converted 12 fixtures in a county parts room using 8' lamps and was not impressed one bit. With one of my customers, I am, one or two fixtures at a time retro fitting t8 and t12 HO's to these, and side by side, the led's using four 50k frosted lamps have a better light output according to the eye test.

I was going to put a four foot section of a kit together tonight, but discovered I already had one. Please don't pay any attention to the dust. It's the surviving half on an 8'er that had a collision with a fork lift. I get the universal adjustable width kits, but they are made to fit any width. I just get the adjustable because I never know what I am going to be up against. Put it together and screw it to the sides of the fixture. They are also made to fit tight to any width of fixture, but I haven't used that style yet.
Yes the reflector wouldn't really be needed. I just think it's a nice aesthetic.

I do not go by the "eye test", too subjective. I have seen people put in a high color temp lamp that is actually much dimmer but then claim it's brighter. I want to measure footcandles.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
Yes the reflector wouldn't really be needed. I just think it's a nice aesthetic.

I do not go by the "eye test", too subjective. I have seen people put in a high color temp lamp that is actually much dimmer but then claim it's brighter. I want to measure footcandles.
I totally understand wanting to measure footcandles, but I don't have a way to measure it and in all honesty, probably never will. In the example I gave, I mistakenly stated 50k lamps. I'm actually using 40k at that customer. Hundreds of 40k frosted lamps with hundreds still to go across all of the shop and office buildings they have. As stated, I don't know the footcandles but I do know there is more usable light out of the led tubes. Really the only places I have seen the led tubes lose out to florescents are 8' and lower ceilings but it hasn't been bad enough to go back to florescents.
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
I bypassed the ballast and installed the 5k LEDs available at HoDe for 50 bucks a pair. They are exceptional.
 
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
Great info here guys. Thanks.
Personally I'd like to keep the reflectors. Looks nicer and I feel and 12' up probably won't make a difference.
Looks plug and play (with a lot of swearing) if I could just screw the new fixture to the reflector that would be ideal.
Rather go with 4' as 8' is a PITA for numerous reasons, unless they cost twice as much.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
If you want to keep the reflectors, look into 8' ballast bypass lamps. I don't like them, but have to admit to only using one type. If you go this route make sure you get the right style. Single pin vs. HO so the lamp fits the existing socket.
 
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
If you want to keep the reflectors, look into 8' ballast bypass lamps. I don't like them, but have to admit to only using one type. If you go this route make sure you get the right style. Single pin vs. HO so the lamp fits the existing socket.
I've done a bit of research and these are very plug and play. (I will bypass the ballast) What do you not like about them?
My current set up is single pin. Should I be concerned?
Is HD okay or should I go to my local electrical supply store?

 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
The tubes that I used didn't put out as much light as I expected, but in all honesty, were probably as good as a new T12 lamp, but nowhere near 18 watt four foot leds. Also, they sagged in the middle. I wound up screwing 1" minerallac straps to the center to help support them.
 

Meursault74

Well-known member
Joined
Apr 1, 2019
Messages
22,027
Location
Southern California
Last year I converted the 8' fluorescent fixtures in my kitchen (drop ceiling) and garage to these:


I didn't measure the light output, but I've was able to run 1 of these LED bulbs per fixture instead of the 2 Fluorescent and it "looks" about the same to me.

If you put 2 in each fixture, you'll definitely have a much brighter workshop than you do now.

I haven't had any issues with mine, electrical or sag-wise.

edit, holy ****!!! they cost a shitload from amazon Canada, WTF?
 
Last edited:
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
Went into my local Westburne electrical supply supplier. They are getting me prices on Philips.
These are glass. Are the ones that are sagging plastic?
 

Masheen365

Active member
Joined
Aug 8, 2021
Messages
39
Location
South GA
January of 2020 I replaced the existing fluorescents with these. 8 fixtures with two bulbs a piece and another 2 fixtures in the garage. I bypassed the ballast and rewired for the new LEDs and have not been disappointed. The single pin connection makes the 8ft bulb a whole lot easier to work with. In a 30x50 shop it makes for good general lighting. We still use additional task lighting for specific areas.
 

Attachments

  • 5D88C978-EA83-4190-93DF-FE0EFA5D4068.jpeg
    5D88C978-EA83-4190-93DF-FE0EFA5D4068.jpeg
    350.8 KB · Views: 91

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
Went into my local Westburne electrical supply supplier. They are getting me prices on Philips.
These are glass. Are the ones that are sagging plastic?
Yes. Those junkers were plastic that had some kind of metal, aluminum?, strip down the back. I suppose that was for support, but it didn't do a very good job. I don't believe I have ever seen a glass led tube, that would solve the problem of the sagging lamps.
 

Meursault74

Well-known member
Joined
Apr 1, 2019
Messages
22,027
Location
Southern California
Yes. Those junkers were plastic that had some kind of metal, aluminum?, strip down the back. I suppose that was for support, but it didn't do a very good job. I don't believe I have ever seen a glass led tube, that would solve the problem of the sagging lamps.
The ones I have, the metal back is about 1/3 of the circumference and the metal is ribbed. More than just a strip. I just checked the ones in my garage. No sag. They've been up for 1 year. These are the only ones I've ever used, so no experience with any other type.

While researching my purchase, I read that the all plastic ones sag and they sell clips for the middle or some used zip ties for support in the middle. It gets hot in my garage in the summer. I have no doubt all plastic would sag and would need some additional support.
 
To avoid these ads, REGISTER NOW!
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
When you say LED tube, are you referring to the ones that you can see the LED's? To me most look like regular fluorescent bulbs. Are they directional?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
When you say LED tube, are you referring to the ones that you can see the LED's? To me most look like regular fluorescent bulbs. Are they directional?
The tubes with the visible led's have a clear lens. The tubes that look like a florescent have a frosted lens. Inside, they are the same with differences between brands. As far as I know, they are all directional, but some can be rotated.
 

Masheen365

Active member
Joined
Aug 8, 2021
Messages
39
Location
South GA
When you say LED tube, are you referring to the ones that you can see the LED's? To me most look like regular fluorescent bulbs. Are they directional?
They may be directional but most of the ones I’ve seen advertise around a 270* throw.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,764
Location
NW Iowa
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
It might end up being similar to what you have now. A good F96T12 is 5500-6000 lumens each. The led tube will have less fixture loss. Power use will be quite a bit less
This is the only one they have. Should I look elsewhere or is this enough compared to my old ones? Everything is on one switch so I can't pick and choose which ones I want on.
 
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
I went to another electrical supplier and this is what they have. Plastic and made in China.
$36 each and the Philips were $31.50 each.
 

Attachments

  • E-CT Star bulb.jpg
    E-CT Star bulb.jpg
    190.5 KB · Views: 63

Meursault74

Well-known member
Joined
Apr 1, 2019
Messages
22,027
Location
Southern California
I went to another electrical supplier and this is what they have. Plastic and made in China.
$36 each and the Philips were $31.50 each.
Here it says glass + film. whatever that means.

I wonder how the Phlips can be less. I would consider Philips a known brand name.
 
OP
R

Rod N

Well-known member
Joined
Jul 21, 2011
Messages
835
Location
Keswick, Ontario
Maybe because the Philips is from a electrical supplier that does mostly to the trades and the other one looks to be retail?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,764
Location
NW Iowa
Most retrofit lamps are designed to produce the same amount of light as what they are replacing. Some offer a couple different lumen outputs but I doubt you will find that with 8'ers since it's a limited market
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Make sure you report back as I have an area with the 8' tubes and I just used the last of my bulbs .. have one ballast left. Mine are open twins (two bulbs). Have two rows of them end to end on a garage cathedral ceiling (each side) .. Have zero desire to switch out the fixtures.

Going up there once to bypass the ballast and pop in the bulbs sounds nice
 

redragoon

Well-known member
Joined
Jun 12, 2018
Messages
296
Location
Greenville SC

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,764
Location
NW Iowa
For my Father's 40x40 shop, I am looking at using the LED High Bay lights. Should be able to light everything with 4 of them.
Using standard 110V outlets and a wood eye screw should be a lot easier than setting up a bunch of tube fixtures.
Amazon LED High Bay Light

I may get 2 for my own garage, but that may be overkill.

Another member on here has done it in this thread.
https://www.garagejournal.com/forum...8-high-bay-ufo-led-lights-impressions.457403/
That's going to give very poor lighting. Might be very bright underneath each light but there will be a lot of shadows.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,989
Location
Central Iowa
For my Father's 40x40 shop, I am looking at using the LED High Bay lights. Should be able to light everything with 4 of them.
Using standard 110V outlets and a wood eye screw should be a lot easier than setting up a bunch of tube fixtures.
Amazon LED High Bay Light

I may get 2 for my own garage, but that may be overkill.

Another member on here has done it in this thread.
https://www.garagejournal.com/forum...8-high-bay-ufo-led-lights-impressions.457403/
I put five 150 watt UFO fixtures with similar specs in a 20X30X16 room at one of my customers shops. The five 8' T12HO fixtures they replaced did a better job of lighting it up when the lamps were new. Good luck. The UFO style lights are blinding bright to look at, but they just don't do a very good job unless it's a really high ceiling.
 