That should work well. Make sure you establish a normal drop under load baseline by doing that test on a known normal circuit. This way you will have something to compare against on the drop test. You should only drop a couple volts on this for a good circuit.
Check the dirt drop while you are doing this too. Give us the dirt drop under load and with no load. I think you said you had 12.5 volts with no load. Measure across the exact same spots.
I plugged in a small heater - only dropped 3 - 4 V on the circuit, but the reading when I put the positive probe in the large slot, and the negative probe in the ground terminal was almost 2 volts at the tail end (.6V on the first outlet - then went to 1.1V - then to 1.9v on the last outlet) - I am thinking that the voltage from the neutral to ground should be les than .5 V.
On a good circuit, there was almost no drop, and the voltage between the neutral wire and ground was 0.
OK - the dirt drop - today I have about 12.5V between my pool water and the metal handrail, no change when I put a load on - but my "dirt load" drops from about 10V down to 8.5V (it is a little dry) - the whole voltage has been lower the last two - or three days - I have seen over 30 V in the ground a couple of weeks ago.
So - what does this tell me - should I replace and check the ground on the outlets where the drop starts? I have about a 3V drop with no load.