I decided to use these

https://www.menards.com/main/lighting-ceiling-fans/indoor-lighting/work-shop-lights/smart-electrician-reg-45-5000-lumen-led-shop-light/gt-sl5000-link/p-1521873022724-c-1472133557086.htm

lights for my new garage. Had originally planned 18 total, 3 rows of 6 to light 24x50 feet with the lights hanging some 12' above the floor.

Well, so far I have only bought 10 of them (other 8 would be done with next pay check) and decided to start putting them up. I changed my mind and will be going with 2 rows of 5 and only use the ones I have already. I have only 4 of them up so far, but that's enough to realize I don't need 18,
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,750
Any receptacles you install for them in a garage/shop/outbuilding must have GFCI protection, this is one disadvantage of cord and plug connected lighting.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
22,976
Location
Minneapolis
Why is that? Mine passed inspection without a GFCI outlet.

Depends on when yours were installed, and also what revision of the NEC the original poster's state is using. Per the 2017 NEC GFCIs are required, but some states use earlier versions that may or may not have that requirement.
 

tom-ky

Well-known member
Joined
Mar 11, 2017
Messages
512
Location
Morgantown, Ky
Depends on when yours were installed, and also what revision of the NEC the original poster's state is using. Per the 2017 NEC GFCIs are required, but some states use earlier versions that may or may not have that requirement.

Mine was done about 18 months ago. Curious as to how a GFCI on a outlet in the ceiling protects anyone.
 

tom-ky

Well-known member
Joined
Mar 11, 2017
Messages
512
Location
Morgantown, Ky
Just because something passed inspection does not always make it right.

What would their purpose be on a light circuit? Their purpose is to prevent shock to a person. How would they do that in a ceiling? Just trying to learn, seen several garages done in my area without them and inspected by different inspectors.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,442
Location
USA
What would their purpose be on a light circuit?

If you have that circuit terminated in receptacles, then it's not a lighting circuit...it's just considered a bunch of receptacles in the ceiling. And anyone can plug anything into them. In a garage, especially, there is a fair likelihood of something being plugged in that could cause an issue. An example might be a cord reel that is plugged into a ceiling receptacle that is being used by someone standing in a puddle.
CD
 

tom-ky

Well-known member
Joined
Mar 11, 2017
Messages
512
Location
Morgantown, Ky
If you have that circuit terminated in receptacles, then it's not a lighting circuit...it's just considered a bunch of receptacles in the ceiling. And anyone can plug anything into them. In a garage, especially, there is a fair likelihood of something being plugged in that could cause an issue. An example might be a cord reel that is plugged into a ceiling receptacle that is being used by someone standing in a puddle.
CD

I added GFCI’s to my garage but was none when it was inspected. Things really must vary by area.
 

coljar

Well-known member
Joined
Sep 26, 2010
Messages
6,243
Location
Belpre, Ohio
My lights are hard wired, but nothing is inspected beyond the meter here. All my receptacles are GFCI, except the ones used to power neon signs. Those lights look like they'll work great, by the way.
 
Last edited:
OP
M

mvusse

Well-known member
Joined
Aug 21, 2018
Messages
87
Location
Strasburg, Ohio
Any receptacles you install for them in a garage/shop/outbuilding must have GFCI protection, this is one disadvantage of cord and plug connected lighting.

Thank you for the heads-up.

I think I will install an easier to reach GFCI outlet so I can reach the test/reset buttons and have it protect the rest of the string (the two outlets in the ceiling). The ceiling ones won't be easy to reach as they'll be 12'6" up from the floor.
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,209
Location
Indy
My non-electrician understanding was that outlets installed in the ceiling for lighting (and possibly garage door openers) proposes didn't require a gfci but that may not be current code. I can see the logic in both directions. Outlets placed for lights or garage door openers are high above areas that may get wet and are generally single purpose. However, as I did in my own garage, if you don't have many outlets you tend to use what you can find. I have an extension cord plugged into the opener outlet because it best reaches my car and my garage currently has too few outlets (I'm working on that).

If you are doing a new install it wouldn't be hard to add a single gfci to feed the lighting outlets.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,750
There is no exception to the GFCI requirements & the GFCI must be accessible.
 
To avoid these ads, REGISTER NOW!

gmtech

Well-known member
Joined
May 22, 2018
Messages
85
Location
nc
Not to hijack this, as it pertains to the conversation, but it's something I've been wondering for my current garage build. Is it legal to just use a gfci outlet on the first outlet and let it protect the others down stream?

Sent from my SAMSUNG-SM-G890A using Tapatalk
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,750
Not to hijack this, as it pertains to the conversation, but it's something I've been wondering for my current garage build. Is it legal to just use a gfci outlet on the first outlet and let it protect the others down stream?

Sent from my SAMSUNG-SM-G890A using Tapatalk

That is the way it's done in most cases, cheaper then a GFCI circuit breaker which is the other way it can be done.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,307
Location
Dutzow Missouri
Not to hijack this, as it pertains to the conversation, but it's something I've been wondering for my current garage build. Is it legal to just use a gfci outlet on the first outlet and let it protect the others down stream?

Sent from my SAMSUNG-SM-G890A using Tapatalk

The instructions that come with most GFIC outlets set a limit on the number of outlet one is allowed to protect. Often the number is six but read your instruction sheet. Yes a home inspector did teach me that lesson.


Walta
 

Krang

Well-known member
Joined
Oct 22, 2018
Messages
185
Location
Hawaii
Because I think it would be useful for us in this thread, I got some CHEAP T5 LED’s from amazon, didn’t work well for my intended application but I’m going to use them for workbench lighting for sure.

IMG_4126.jpg

“ put up some of the new lights to test fit... and I really don’t like them. They are 6000k and just WAY to blue/white for my liking. I’m going to pick up some alternate fixtures today that are 4000k and see how it works. That aside, my system for attaching the lights works like a charm! 80lb magnets on the back of a PVC trim board:”

98baafd4143db49da267baff06ef2416.jpg

d791af821167dedd42c8be6fea2a04bd.jpg

af30b897b82522222122baebbfee8ac6.jpg

fb376748b3458827f90be108a511779e.jpg

However, they work great for my other - storage specific container. Super easy installation and I don’t care what the light looks like, only that there is some light:

d6808ee9a2df120147e9999682c8ce9e.jpg


Sent from my iPhone using Garage Journal
 

Attachments

  • IMG_4126.jpg
    IMG_4126.jpg
    51.3 KB · Views: 35
  • 98baafd4143db49da267baff06ef2416.jpg
    98baafd4143db49da267baff06ef2416.jpg
    161 KB · Views: 0
  • d791af821167dedd42c8be6fea2a04bd.jpg
    d791af821167dedd42c8be6fea2a04bd.jpg
    128.5 KB · Views: 0
  • af30b897b82522222122baebbfee8ac6.jpg
    af30b897b82522222122baebbfee8ac6.jpg
    169.9 KB · Views: 0
  • fb376748b3458827f90be108a511779e.jpg
    fb376748b3458827f90be108a511779e.jpg
    191.1 KB · Views: 1
  • d6808ee9a2df120147e9999682c8ce9e.jpg
    d6808ee9a2df120147e9999682c8ce9e.jpg
    222.3 KB · Views: 1

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,442
Location
USA
You can get little magnets with a threaded post on them. Put the post thru the hole in the clip and attach the magnet to the ceiling. No trim board necessary.
CD
51%2BimW%2BjOmL._SX342_.jpg
 

Krang

Well-known member
Joined
Oct 22, 2018
Messages
185
Location
Hawaii
You can get little magnets with a threaded post on them. Put the post thru the hole in the clip and attach the magnet to the ceiling. No trim board necessary.
CD
51%2BimW%2BjOmL._SX342_.jpg

Very true, but these lights don't have any way to utilize yours in that way. They are not even 1" wide, and the brackets are dinky.

I picked up some of the Costco 4000 lumen 4k lights and like them so far, going to set them up this weekend and I know I will need that trim board - they don't have any easy way to attach other than eyelets like you would find on a power strip..... I might just drill some holes.

I definitely know a few uses for your magnets though, there are some things I want to attach that I can't easily screw into, yours would work perfectly.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,442
Location
USA
Very true, but these lights don't have any way to utilize yours in that way. They are not even 1" wide, and the brackets are dinky.

I know they are. I use them. You can get the magnets small enough so that the post fits thru the hole in the mounting clip.
CD
 
Last edited:

Krang

Well-known member
Joined
Oct 22, 2018
Messages
185
Location
Hawaii
I know they are. I use them. You can get the magnets small enough so that the post fits thru the hole in the mounting clip.
CD

Mind blown.
giphy.gif


Well, now I must scour the Internet for them, unless you have a link, lighting wizard.
 

gungatim

Well-known member
Joined
Jan 8, 2013
Messages
8,101
Location
west mich
I have 4 of those in my outside shop, I love them, super bright, no delay, dheap to run.

only complaint is when I replaced my fluorescent's in my wood shop, I found Harbor Freight sells the exact same light for $20 with coupon. bought 3 of those and saved some coin. wish I would have known about the HF lights before spending $40 each at Menards....
 

bjcouche

Well-known member
Joined
Sep 11, 2010
Messages
509
Location
Ohio
And when installing outlets on the ceiling, make sure they are tamper resistant. My inspector specifically looked to see that the garage door opener outlet was tamper resistant. "all outlets must be tamper resistant, no exceptions". Actually the NEC does have a couple exceptions, but I wasn't about to argue with the inspector when he was about to pass my install.
Brian
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Not to hijack this, as it pertains to the conversation, but it's something I've been wondering for my current garage build. Is it legal to just use a gfci outlet on the first outlet and let it protect the others down stream?

Sent from my SAMSUNG-SM-G890A using Tapatalk

Every plug run in my shop is like that. One is usually in front of 8~10 downstream outlets.
 