I have a newer house with 200a main service, but the garage wiring *****. I've got 2 outlets, 2 lights, and plugs for the garage door openers, but that's it. Its a 3 car 22 x 30 garage.
I'm going to run a 100a sub panel to fix the problem and allow my to have a few dedicated 20a plugs, juice for a welder, compressor, and possibly a powder coat (kitchen) oven. I'm going to leave the original lights and garage opener circuits alone, so that the sub is dedicated to the tools.
I'm calculating 70' conservatively as the run from the main panel to the sub.
The garage is *attached*, and the cable will go through the basement the entire way.
My plan is stay conservative side of the NEC codes in case the inspector gets a bug up his ***, which he tends to do here in the sticks.
I'm thinking aluminum 2-2-2-3 SER cable (no conduit) would do the trick and I will connect it to a 100a breaker in the main panel. No ground rods for the sub, everything goes back to the main panel.
It looks like 2-2-2-3 is a fairly common size, and almost no one stocks copper anymore? Hopefully Depot or Lowes will have the aluminum, otherwise I'll have to pay a bit more the electric supply house.
Let me know if I'm missing anything?
Thanks,
John
I'm going to run a 100a sub panel to fix the problem and allow my to have a few dedicated 20a plugs, juice for a welder, compressor, and possibly a powder coat (kitchen) oven. I'm going to leave the original lights and garage opener circuits alone, so that the sub is dedicated to the tools.
I'm calculating 70' conservatively as the run from the main panel to the sub.
The garage is *attached*, and the cable will go through the basement the entire way.
My plan is stay conservative side of the NEC codes in case the inspector gets a bug up his ***, which he tends to do here in the sticks.
I'm thinking aluminum 2-2-2-3 SER cable (no conduit) would do the trick and I will connect it to a 100a breaker in the main panel. No ground rods for the sub, everything goes back to the main panel.
It looks like 2-2-2-3 is a fairly common size, and almost no one stocks copper anymore? Hopefully Depot or Lowes will have the aluminum, otherwise I'll have to pay a bit more the electric supply house.
Let me know if I'm missing anything?
Thanks,
John