Chimney pipe help?

188slo50

Well-known member
Joined
Jul 26, 2009
Messages
643
Location
Virginia
Putting a woodstove in my new shop but not sure about the chimney for it. I know I'm going to run it through the roof but not sure of what pipe to use. I planed on just running black pipe but I've been reading on here and people talk about double/triple walled. What's the difference and do I have to run it or is my black pipe sufficient?.
 
To avoid these ads, REGISTER NOW!

JohnKal

Well-known member
Joined
Mar 24, 2014
Messages
1,780
Location
New York State
Most chimney pipe is double wall. I believe its called " all fuel" pipe. I just installed one in my garage. There's a ton of info if you google it. It's expensive, but you can save a boat load doing it yourself. Hope this helps.

Good luck.
 

sms1974

Well-known member
Joined
Jul 9, 2014
Messages
210
Location
Grafton Ohio
Wood burners require a class A pipe... Most of what i see having a class A rating is triple wall stainless and it's quite pricy...
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,927
Location
Amarillo,TX and Stinnett,TX
From the stove to the ceiling box support you can use black single wall pipe. From the top end of the ceiling support box through the roof/attic etc most use triple walled because it allows for a 2" clearance to combustibles. This pic is a ceiling support box.

A few things I've learned during my install research;

1. Black pipe is much cheaper but cools down quicker = possible increase in creosote build up= cleaning more often.

2. double/triple pipe is insulated= hotter pipe temps= better draw.

3. Black pipe will radiate heat into the shop more.
 

Attachments

  • 100_1288.jpg
    100_1288.jpg
    72.2 KB · Views: 97
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Chimney and flue pipe are brand specific. You must use matched components. Go HERE for lots of good information. Probably two of the better known chimney and flue systems are Dura Vent and Selkirk. If you are in Canada, they have special rules and different pipe.

Also look at THIS brief installation guide.

The Northline Express site is a very good resource. I had to buy a couple of flue pipe sections for my used oil heater installation, beyond what was provided with it. I was able to match the brand and series of pipe from Northline Express.

Charles
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,076
Location
SE MI
Check the installation guide for clearance between the stove an single wall pipe and combustible surfaces. Even when you meet the minimum requirements the surface behind will be very very warm. If you are concerned, light gauge metal with several inches of air on both sides is an excellent heat shield.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
I suggest using the double wall. It has a good warranty, is stainless interior and performance is better. Pricey, but the right tool for the job. As well once you pass through a wall or ceiling you have to go to a UL103HT rated pipe. The UL103 pipe is L vent and approved for oil. the 103 was found to be inadequate for wood and coal and the 103HT was created. I'm doing my new chimney in Selkirk Ultra-temp.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
I think we're all saying the same thing but I've done a few with permits and the code says you may use black stove pipe from the appliance to the first pentration of a wall or ceiling at which point you must transition to class A (double wall insulated, we don't use triple wall) pipe which is not always stainless steel from that point to the cap.

The black stove pipe is available in single wall (18" clearance) and double wall (6" clearance). The double wall is much more expensive but better performance and since it is stainless steel on the inside it lasts much longer than regular steel single wall.

The class A is very expensive and usually glossy stainless steel but you can buy cheaper class A rated with a galvanized steel exterior. 2" clearance and that means clearance, no insulation or other junk within 2".

Here's mine. 10 feet of single wall, ceiling box, 9 feet of class A to cap.
 

Attachments

  • IMAG0828.jpg
    IMAG0828.jpg
    82.7 KB · Views: 160

plott hound

Well-known member
Joined
Apr 19, 2014
Messages
114
if you have a steel roof heres a word from the wise,dont go through it!buy a TEE and go through as wall.if you want to know why not,drive around and look at other peoples chimney going through steel roofs.95% will be gooped up with black **** trying to stop the leaks.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
if you have a steel roof heres a word from the wise,dont go through it!buy a TEE and go through as wall.if you want to know why not,drive around and look at other peoples chimney going through steel roofs.95% will be gooped up with black **** trying to stop the leaks.

A deck-tite type flashing used with the proper screws and sealant will last a long time and not leak, the people using a flashing designed for a shingle roof on a steel roof will always have problems.

This type will work on a steel roof.

http://www.bestmaterials.com/detail.aspx?ID=16187
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
DekTites.jpg


I have never used the Dek Tite flashing system, but clearly, it is well designed and apparently works like it is intended to.

If you go thru the roof, use the Dek Tite brand and you will probably be way ahead of the game.

NOTE THE SPELLING, IF YOU USE GOOGLE........ DEK TITE

Here is the manufacturers page for the flashing system.... They also make a lot of other neat stuff for construction, mostly unique fastening systems for roofs, and such.

http://ejot-usa.com/products/fasten...construction/deks-metal-roof-flashing-systems

Charles
 
OP
1

188slo50

Well-known member
Joined
Jul 26, 2009
Messages
643
Location
Virginia
Ok so I'm going to run black pipe to the ceiling, class a thru roof, use a rubber seal like noted above, than a cap on the outside to keep birds out. Do you use anything to keep the pipe together or does it hold itself?
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
The double wall comes with locking bands. The triple wall can be screwed. Make sure you secure each section. I've seen people unlock section while cleaning the chimney.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,076
Location
SE MI
I think we're all saying the same thing but I've done a few with permits and the code says you may use black stove pipe from the appliance to the first pentration of a wall or ceiling at which point you must transition to class A (double wall insulated, we don't use triple wall) pipe which is not always stainless steel from that point to the cap.

The black stove pipe is available in single wall (18" clearance) and double wall (6" clearance). The double wall is much more expensive but better performance and since it is stainless steel on the inside it lasts much longer than regular steel single wall.
Highbeam - I notice from your picture you have "cement board" behind the stove and I assume all the way up, correct ? Are you using single wall pipe up to the ceiling transition ?

I would ! You are trying to heat the interior.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Highbeam - I notice from your picture you have "cement board" behind the stove and I assume all the way up, correct ? Are you using single wall pipe up to the ceiling transition ?

I would ! You are trying to heat the interior.

Cement board all the way up but not required, just a little safer. Yes single wall but the stove is the heater. Double wall would cost a lot more.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
The double wall comes with locking bands. The triple wall can be screwed. Make sure you secure each section. I've seen people unlock section while cleaning the chimney.

Not anymore. Double wall stove pipe pushes together and you add screws to secure it. Same as single wall.

Class a is threaded on each end. No screws.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
Not anymore. Double wall stove pipe pushes together and you add screws to secure it. Same as single wall.

Class a is threaded on each end. No screws.

I was talking the chimney, not the vent connector. Yes, double wall vent connector uses short screws. Make sure you do not penetrate the inner liner. There are different types of Class A. Dura-vents Dura-Plus is triple wall and uses screws. The double wall class A does have a twist lock but requires the use of the locking bands for security purposes.
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,927
Location
Amarillo,TX and Stinnett,TX
I think we're all saying the same thing but I've done a few with permits and the code says you may use black stove pipe from the appliance to the first pentration of a wall or ceiling at which point you must transition to class A (double wall insulated, we don't use triple wall) pipe which is not always stainless steel from that point to the cap.

The black stove pipe is available in single wall (18" clearance) and double wall (6" clearance). The double wall is much more expensive but better performance and since it is stainless steel on the inside it lasts much longer than regular steel single wall.

The class A is very expensive and usually glossy stainless steel but you can buy cheaper class A rated with a galvanized steel exterior. 2" clearance and that means clearance, no insulation or other junk within 2".

Here's mine. 10 feet of single wall, ceiling box, 9 feet of class A to cap.

Just wondering how much clearance you have to the back wall?
 
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Just wondering how much clearance you have to the back wall?

There is right at 19" between the single wall pipe and the face of the studs behind the cement board. The studs are the first combustible surface so I am over by 1".

The stove itself is of course closer to the back wall but not by much and there is a blower bolted onto the back that hangs out in that space. You can't easily walk behind the stove.
 
OP
1

188slo50

Well-known member
Joined
Jul 26, 2009
Messages
643
Location
Virginia
What's the cheapest place to buy black pipe? The best I've found is $1.50 an inch which adds to be a lot for 10' ceiling.
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
Used to be you could get black in two thickness. Any more all I ever see available is one thickness at almost all stores. I bought ten feet initially, now every couple of years I replace the one closest to the stove. For the house, I burn 24-7 for 4 to 5 months every year. Upstairs? Everything is triple wall!
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,855
Location
Northern Central Ohio
What's the cheapest place to buy black pipe? The best I've found is $1.50 an inch which adds to be a lot for 10' ceiling.

I bought my last two pices at the local True Value hardware store. Do you have a TSC locally or even Menard's carries single wall black pipe.
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,927
Location
Amarillo,TX and Stinnett,TX
I picked up (5) 24"x8" pieces at Lowes for $12.95 each. Here's my install and I still want to add a second wall. The ceiling hole was already there from the furnace I removed and I wanted the stove as far away from the wall as possible so the pipe angle is goofy.:willy_nil
 

Attachments

  • 100_1305.jpg
    100_1305.jpg
    90.4 KB · Views: 78
  • 100_1308.jpg
    100_1308.jpg
    97.4 KB · Views: 63
Last edited:

Bubbles

Well-known member
Joined
Jun 23, 2006
Messages
278
Add your elbows at the top before it goes to class a , you can get a couple of 22's or 45's to get that pipe straight.
 

Ironhorse74

MEMBER EMERITUS
Joined
Nov 10, 2014
Messages
998
Location
The Pacific North Wet
DekTites.jpg


I have never used the Dek Tite flashing system, but clearly, it is well designed and apparently works like it is intended to.

If you go thru the roof, use the Dek Tite brand and you will probably be way ahead of the game.

NOTE THE SPELLING, IF YOU USE GOOGLE........ DEK TITE

Here is the manufacturers page for the flashing system.... They also make a lot of other neat stuff for construction, mostly unique fastening systems for roofs, and such.

http://ejot-usa.com/products/fasten...construction/deks-metal-roof-flashing-systems

Charles


Hi Charles

I am in the hearth business and pretty **** about playing by the rules. There are flashings made for class A chimney that look like those Dek-tite flashings. They do however have to be UL (Warnock-Hershey) Listed for the chimney that is being used. I couldn't find a listing for any class A chimney with those jacks. All of the ones like that I have seen have been red in color. High temp? They also covered a roof brace.

Just my .02

Brad
 
OP
1

188slo50

Well-known member
Joined
Jul 26, 2009
Messages
643
Location
Virginia
So let me get clear on a few things. I can run black pipe up to the ceiling, than I run a triple wall in the attic with 6" distance around it away from insulation. What do I run through the roof? Is there something I need to do at the ceiling where the drywall and pipe meet?
 
Last edited:

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,855
Location
Northern Central Ohio

Bubbles

Well-known member
Joined
Jun 23, 2006
Messages
278
The ceiling kit will hold the weight of the class a. It will also give you the required clearances.
 
OP
1

188slo50

Well-known member
Joined
Jul 26, 2009
Messages
643
Location
Virginia
But that's $250 which means my chimney will cost more than the woodstove. To me that's a lot of money to spend at one time something I might use 60 days out of the yr.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Hi Charles

I am in the hearth business and pretty **** about playing by the rules. There are flashings made for class A chimney that look like those Dek-tite flashings. They do however have to be UL (Warnock-Hershey) Listed for the chimney that is being used. I couldn't find a listing for any class A chimney with those jacks. All of the ones like that I have seen have been red in color. High temp? They also covered a roof brace.

Just my .02

Brad

While I did not find any mention of UL listings, I did find this............. "Available in Black and Grey EPDM or Red Silicone
EPDM will withstand constant temperatures at the roofline of -50°C (-58°F) to 115°C (239°F) and up to 150°C (302°F) intermittently
Red Silicone will withstand constant temperatures at the roofline of -50°C (-58°F) to 200°C (392°F) and up to 250°C (482°F) intermittently"

Charles
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,855
Location
Northern Central Ohio
But that's $250 which means my chimney will cost more than the woodstove. To me that's a lot of money to spend at one time something I might use 60 days out of the yr.

I was just linking that kit as a reference on how the drywall meets the pipe, your question.

But as 930Dreamer mentioned, it's cheaper than burning down your shop. If you improperly install your stove/chimney and have a fire due to this issue, your insurance company may elect not to pay a claim due to negligence.

Also keep in mind, what you're buying is an investment, not just in shop safety but a heating investment. Every year that you use that wood stove to heat your shop, it's giving you a return on your investment.
 
OP
1

188slo50

Well-known member
Joined
Jul 26, 2009
Messages
643
Location
Virginia
But it's cheaper then burning down your shop.

True but being that I have a metal roof I can't use most those parts. I know there's cheaper ways than buying that kit and wasting money on parts I won't use when I can build something for less.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,855
Location
Northern Central Ohio
True but being that I have a metal roof I can't use most those parts. I know there's cheaper ways than buying that kit and wasting money on parts I won't use when I can build something for less.

Other then mentioning in one post about using that rubber seal, you never mentioned having a metal roof.

That kinda makes it hard for use to give advice when we don't have all the information.

:dunno:
 
OP
1

188slo50

Well-known member
Joined
Jul 26, 2009
Messages
643
Location
Virginia
I didn't mention it but also didn't think it made a difference other than exterior wise, which is why I was going to use the rubber boot thing. In the link you gave for northern tool what is the purpose of the chimney support box? Does it keep the needed distance between pipe and insulation or is it just support? I can piece it together from lowes for what parts I need just not sure what is needed?
 

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,927
Location
Amarillo,TX and Stinnett,TX
I didn't mention it but also didn't think it made a difference other than exterior wise, which is why I was going to use the rubber boot thing. In the link you gave for northern tool what is the purpose of the chimney support box? Does it keep the needed distance between pipe and insulation or is it just support? I can piece it together from lowes for what parts I need just not sure what is needed?

The support box is required when going through a ceiling(i.e. in a house), it's used for clearance to combustibles and support.
 
To avoid these ads, REGISTER NOW!