Just put a new WEG 5HP motor on my compressor, need to add a mag starter with overload protection.
The WEG motor is rated at 21.5A @ 230v

The Mag starters listed for 5HP are 22-32 amp,,
I found one listed for 3HP that is 18-26 Amp.

Which one?

Slack
 
To avoid these ads, REGISTER NOW!

foghorn1966

Well-known member
Joined
Aug 18, 2012
Messages
228
Location
N. Alberta
Easy, 5 HP motor = 5 HP starter. There is a reason they are rated in HP, mostly due to the inrush current of the motor.
 
To avoid these ads, REGISTER NOW!

FTG-05

Well-known member
Joined
Oct 11, 2012
Messages
1,541
Location
TN
Even though my compressor has a 5 hp motor, it has a 7.5 hp pump. Hence, I got a 7.5 hp rated Mag starter in case I ever want to upgrade the compressor. Not much more $$ over a 5 hp. I got a WEG version, I'll have to dig up the model # later whne I find my phone.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,961
Location
East Cobb County, Georgia
Also look at the Square D 8911 starters on Amazon. I would get the larger one and tune it down to match the load. As long as the contactor is big enough, you can tune the overload setting or heaters to better match the actual load. Do not oversize the protector setting too much. A starter can prevent a motor burn-out by tripping if it is overloaded because of a mechanical issue like a seized pump or drive problem.
 