Cinderblock Walls- PVC or EMT?

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
I purchased a house that has a garage made of cinderblock walls... no studs. There is only a couple of outlets, and there is Romex stapled to the mortar between the blocks.

I have plenty of Romex lying around, but no THHN. Should I run PVC or EMT conduit? Romex in the conduit or buy some rolls of THHN? I've used EMT before, and find it significantly harder to cut, debur, attach, etc than PVC.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
Buy some THHN, the reason being that you have to measure NM at it's widest point, thus some big conduit will be needed in order to keep from exceeding the wirefill requirement.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,776
Location
NW Iowa
Emt is little harder to work with in some cases but looks 10x better. Use PVC in underground or corrosive locations.
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,846
If you want it to look neat then use EMT. PVC sags and looks bad within just a few weeks. EMT if put up straight and square is still that way 30 years later..
 
To avoid these ads, REGISTER NOW!

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
3,977
Location
Upstate NY
Emt is little harder to work with in some cases but looks 10x better. Use PVC in underground or corrosive locations.

I agree 100%! A little extra effort put into EMT produces much better looking results than PVC. If I see PVC on garage or basement walls, it just looks to me like the guy really didn't know what he was doing.
 