Something shorted to ground, that was the bang.

Cooked the internals of the breaker in the process, or is still in a state that the breaker won't reset. Investigate what the breaker feeds, rule out all issues and then try the breaker. Replace if still bad.

Wait until you're around when it happens to a 480v 600A feed, that'll make you jump!
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,942
Location
Amarillo,TX and Stinnett,TX
Something shorted to ground, that was the bang.

Cooked the internals of the breaker in the process, or is still in a state that the breaker won't reset. Investigate what the breaker feeds, rule out all issues and then try the breaker. Replace if still bad.

Wait until you're around when it happens to a 480v 600A feed, that'll make you jump!

I know the circuit feeds three receptacles on the west wall, i.e. a small water heater on one recept and the ceiling fan, stereo etc on the other two?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I know the circuit feeds three receptacles on the west wall, i.e. a small water heater on one recept and the ceiling fan, stereo etc on the other two?

3 receptacles? Whats the receptacle rating?

And 5-15 or 5-20 receptacles shouldnt be on a 30a breaker.

Agree with charles. Major code violation!

Do u have pics of this?

Sounds like something shorted to ground and the fault hasnt cleared itself so the short is still there.

Fix the short then try resetting breaker...
 

Hawk

Well-known member
Joined
Oct 21, 2009
Messages
1,019
Location
Kannapolis, NC
Check the elements in the water heater. Then the rest of the circuit. Before turning it back on run a dedicated circuit for the water heater.
 

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
Something shorted to ground, that was the bang.

Cooked the internals of the breaker in the process, or is still in a state that the breaker won't reset. Investigate what the breaker feeds, rule out all issues and then try the breaker. Replace if still bad.

Wait until you're around when it happens to a 480v 600A feed, that'll make you jump!


480s got nothing on 138kV. Was standing in a station when a tent blew into a 138kV bus. Not fun.


Sent from my iPhone using Tapatalk
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,390
Location
VT
480s got nothing on 138kV. Was standing in a station when a tent blew into a 138kV bus. Not fun.


Sent from my iPhone using Tapatalk

Yeah that would be a show. Had an issue one night that took the building down, started powering backup and when we kicked on one piece of equipment heard a "whumuumpfff" and watched the control cabinet bulging out towards me. Turns out the 3 month old 125hp motor threw a bearing and dropped 3", causing a dead short to ground.

Scary part was the equipment just had a recall to reinforce the door a week before.
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
22,942
Location
Amarillo,TX and Stinnett,TX
No open short in the heating element, showing 7 ohms? I unplugged everything on the circuit and the breaker will reset.
 

Attachments

  • 20160210_125418.jpg
    20160210_125418.jpg
    144.4 KB · Views: 56
  • 20160210_125407.jpg
    20160210_125407.jpg
    137 KB · Views: 65
  • 20160210_125827.jpg
    20160210_125827.jpg
    136.6 KB · Views: 69
Last edited:
To avoid these ads, REGISTER NOW!

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,028
Location
NJ
No open short in the heating element, showing 7 ohms? I unplugged everything on the circuit and the breaker will reset.

Good news. If you unplugged or disconnected all 'devices' from the circuit in question and the breaker resets fine (no light show or sound effects :lol_hitti ), then the circuit breaker itself and the circuit wiring -seem- to be OK.

Which means that one (or more!) of your 'devices' is NG.

Or, in plugging in and unplugging your 'devices', you jostled something in the receptacles or their wiring or the wiring in the boxes and now the short circuit is not currently (no pun intended) present.

Standard troubleshooting procedure is to check/change one thing at a time. But check them all, one by one, with circuit/operational checks after each 'thing' is checked/changed. So you know if/when the behavior changes.

I'd lean towards the high amp water heater is the prime suspect.

But would still go through the entire circuit, section by section, to really verify that other things are OK. Turn circuit off at breaker (lock out - tag out !!) and maybe pull the actual breaker off the bus to make sure that the circuit isn't and can't become live. And then pull all the cover plates and check the receptacles/outlets and the wiring in the boxes for anything loose or melted or 'smoky'.

If all that checks out OK, then move onto checking the previously connected devices (on a bench and/or on another circuit). And maybe use a simple 'test device' (drop light :D ) on all the outlets in the misbehaving circuit.

Check/change one thing at a time, but check everything that you can. Don't stop if you find one 'bad' thing, check everything (as you could have multiple 'faults' going on at the same time).

Oh, and that 'wiring' of the water heater plug is horrible. Fix it.
 

G_P

Well-known member
Joined
Jul 11, 2010
Messages
7,135
Location
Central CT
Water heater likely drew too many amps and blew the breaker. Plug everything but the water heater back in and it will probably be fine. You really should run a dedicated circuit for the heater, and swap the 30a breaker for a 20a breaker (as long as you have at least 12ga wire) to protect the outlets.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Water heater likely drew too many amps and blew the breaker. Plug everything but the water heater back in and it will probably be fine. You really should run a dedicated circuit for the heater, and swap the 30a breaker for a 20a breaker (as long as you have at least 12ga wire) to protect the outlets.

Breakers that trip from overload, don't go "bang". They just trip, quietly.

There is a short or ground fault issue along with the obvious "plugging household 120v appliances into a 30 amp circuit issue."
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA

Elginz

Well-known member
Joined
Dec 29, 2014
Messages
431
Location
Oconto, WI
:shocking: :lol_hitti This is a good one. I thought the post was about a circuit breaker. When it is the circuit breaker that is the only thing working like it is meant to. When I did inspections it would be called undersized branch wiring if the breaker was sized to large. I don't know what size the wires are, but, ya there are a lot of other things wrong.

I know lots of things that I should do/change too, and some day I will get to them.
Good Luck
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
:shocking: :lol_hitti This is a good one. I thought the post was about a circuit breaker. When it is the circuit breaker that is the only thing working like it is meant to. When I did inspections it would be called undersized branch wiring if the breaker was sized to large. I don't know what size the wires are, but, ya there are a lot of other things wrong.

I know lots of things that I should do/change too, and some day I will get to them.
Good Luck

:beer::beer::beer::beer::beer::beer::beer:
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,254
Location
Coastal NJ
:eyecrazy:Replace the breaker with a 100A breaker. :eyecrazy: That way next time the extension cord shorts you will have enough current to burn the short clear!

Yes I'm kidding.
 