DC73
Well-known member
I had an interesting (to me) circuit breaker tracing experience recently. Thought I would share in case someone else comes across the same issue I did.
Background: I've been in this house about 18 months and decided to replace the poor quality outlets and switches the builder used. The circuit breaker panel was very poorly labeled so the first step was to buy a Klein Circuit Breaker Finder and map out which breakers fed which outlets and fixtures. For those who don't know, these tools consist of a transmitter that plugs into an outlet and a receiver that is used to find which breaker is feeding that circuit. I also picked up a screw in adapter so I could use the transmitter on light fixtures. The tool works well (read the instructions - you have to make one pass over each breaker in the panel to calibrate the receiver and then make a second pass to actually find the breaker).
The circuit breaker finder worked well on all but two circuits. On those two circuits, it would not work at all. It turned out the problem was identical EFI brand surge protectors plugged into outlets on each of those circuits.
On a whim, I tried unplugging one of the EFI surge protectors and sure enough, the circuit breaker finder worked again. Unplugged the other one and got the same results. So, these two surge protectors were somehow blocking the signal sent by the transmitter.
I didn't pick up on this right away because I have 7 or 8 point of use surge protectors around the house including 3 high quality Tripp Lite devices for my sensitive electronics. None of the other surge protectors caused this issue, only the two EFI units. It didn't matter where the transmitter was plugged in, nor did it matter where the EFI surge protector was plugged in. As long as one of the EFI surge protectors was plugged in somewhere on the circuit, the circuit breaker finder would not work on that circuit.
So, what's different about these two EFI surge protectors? As best I can tell and without opening them up for inspection, the major difference between the two EFI units and the other surge protectors I have including the Tripp Lites is that when the surge protection fails in the EFI units, the entire device fails so that the outlets no longer work. In my other units, the outlets keep working when the surge protection fails (an indicator light goes out to indicate failure of the surge protection).
DC
Background: I've been in this house about 18 months and decided to replace the poor quality outlets and switches the builder used. The circuit breaker panel was very poorly labeled so the first step was to buy a Klein Circuit Breaker Finder and map out which breakers fed which outlets and fixtures. For those who don't know, these tools consist of a transmitter that plugs into an outlet and a receiver that is used to find which breaker is feeding that circuit. I also picked up a screw in adapter so I could use the transmitter on light fixtures. The tool works well (read the instructions - you have to make one pass over each breaker in the panel to calibrate the receiver and then make a second pass to actually find the breaker).
The circuit breaker finder worked well on all but two circuits. On those two circuits, it would not work at all. It turned out the problem was identical EFI brand surge protectors plugged into outlets on each of those circuits.
On a whim, I tried unplugging one of the EFI surge protectors and sure enough, the circuit breaker finder worked again. Unplugged the other one and got the same results. So, these two surge protectors were somehow blocking the signal sent by the transmitter.
I didn't pick up on this right away because I have 7 or 8 point of use surge protectors around the house including 3 high quality Tripp Lite devices for my sensitive electronics. None of the other surge protectors caused this issue, only the two EFI units. It didn't matter where the transmitter was plugged in, nor did it matter where the EFI surge protector was plugged in. As long as one of the EFI surge protectors was plugged in somewhere on the circuit, the circuit breaker finder would not work on that circuit.
So, what's different about these two EFI surge protectors? As best I can tell and without opening them up for inspection, the major difference between the two EFI units and the other surge protectors I have including the Tripp Lites is that when the surge protection fails in the EFI units, the entire device fails so that the outlets no longer work. In my other units, the outlets keep working when the surge protection fails (an indicator light goes out to indicate failure of the surge protection).
DC