I installed a 4 post lift a few years ago. I ran a dedicated 12/2 20 amp circuit. Once in a while the breaker would trip when starting the pump. Just recently I took out the 20A breaker and installed a 25A breaker. It doesn't trip any more, but I am wondering if this is good for a permanent fix or should I replace the 12/2 with 10/2 and a 30A breaker?
The motor is 3 horse.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If cord and plug, the circuit for 3hp should be wired with #12 thhn or #10 nm-b. The #12 thhn can be on a max of a 25A breaker. The #10 nm-b can be on max 30A breaker. What does the installation manual say? If hardwired you have leeway to increase breaker size to account for startup load, but the supply conductors still need to be as above.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
I installed a 4 post lift a few years ago. I ran a dedicated 12/2 20 amp circuit. Once in a while the breaker would trip when starting the pump. Just recently I took out the 20A breaker and installed a 25A breaker. It doesn't trip any more, but I am wondering if this is good for a permanent fix or should I replace the 12/2 with 10/2 and a 30A breaker?
The motor is 3 horse.
12/2 is limited to 20a
 
To avoid these ads, REGISTER NOW!
OP
J

jaw22w

Well-known member
Joined
Dec 28, 2019
Messages
195
Location
indiana
It is a plug-in 3 HP motor. It is wired with 12/2 nm-b. I think it takes a little over a minute to make the trip from the ground to topped out. I had never heard of a high magnetic breaker. I will look into that. I am not too concerned about code. I just want it to be safe.
I'd leave it alone if it were mine. How long does a lift run? 30 seconds at a time? Nothing bad is going to happen.


I'm kinda leaning towards Spark1971.
 

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
901
Location
San Diego County
When I installed my lift, the first time I used it the breaker tripped. I'm thinking I hit the button twice quickly or something because it's never tripped since.

At that time I used an extension cord plugged into a 20A receptacle (20A breaker - no Romex). I've since run a dedicated circuit overhead and have the lift plugged into the drop cord. Still no issues...
 