Moved into a new house about a month ago. First week in I replaced a few outlets in the master with newer outlets that have USB in them. Fast forward to today, I come home to a dead circuit. It will stay for about 10 seconds and then trip. Nothing on, nothing plugged in.

Now the new outlets seem an obvious culprit, by why all of a sudden. Everything has worked great for the last 3 weeks. We did also have a good storm today, but not the first since moving.

Assuming it's not the new circuit, what kind of damage would I be looking for? What would cause a circuit to just quit like that after seeming to work just fine?

I have not had a chance to look at anything since wife is in the hospital and I'm home with 2 little ones.

Sent from my Moto Z (2) using Tapatalk
 
To avoid these ads, REGISTER NOW!

jhelrey

Well-known member
Joined
Sep 15, 2010
Messages
7,293
Location
MN
You might have loose wiring or something is getting warm and then tripping.
 

retDAC

Well-known member
Joined
Oct 28, 2011
Messages
1,253
Location
near Huntsville, Ala.
Make sure the breaker itself is okay. Switch it into another circuit if necessary to test unless you can put a load elsewhere on the circuit.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Moved into a new house about a month ago. First week in I replaced a few outlets in the master with newer outlets that have USB in them. Fast forward to today, I come home to a dead circuit. It will stay for about 10 seconds and then trip. Nothing on, nothing plugged in.

Now the new outlets seem an obvious culprit, by why all of a sudden. Everything has worked great for the last 3 weeks. We did also have a good storm today, but not the first since moving.

Assuming it's not the new circuit, what kind of damage would I be looking for? What would cause a circuit to just quit like that after seeming to work just fine?

I have not had a chance to look at anything since wife is in the hospital and I'm home with 2 little ones.

Sent from my Moto Z (2) using Tapatalk

Im confused. You said you put some new outlets in but then mentioned a new circuit. Did you also install a new circuit?

You might have loose wiring or something is getting warm and then tripping.

A breaker will not trip just because something is warm.

It is an AFCI

Sent from my Moto Z (2) using Tapatalk

I have not heard of this but i wouldnt be surprised if the USB outlets might be causing an issue that the AFCI is seeing as an arc.

Try removing the new outlets and see if the nuisance tripping stops. Also, check the wiring in the junction boxes to make sure you dont have a hot wire touching neutral or ground.
 
To avoid these ads, REGISTER NOW!

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,354
Location
Alexandria, VA
I had a similar problem after changing out some receptacles, and it turned out that I had a broken wire in one of the white leads.

My white wires were twisted together in a wire nut and one probably broke partially when first installed, but then stayed in enough contact to keep working. When I installed the new receptacle I disturbed the wiring and it created more of a break in the bad wire. Everything showed normal with a standard plug in receptacle tester, but the GFCI tripped as soon as I plugged in any actual load.

Bruce
 

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
I had an AFCI circuit breaker go bad in my previous house. It would just randomly trip every now and then, then after a few months, it would do the same as yours, just trip shortly after turning back on.
I checked all the wiring I could find on that circuit and didn't find anything wrong. I then replaced it with a new AFCI breaker and it stopped tripping.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
I had a similar problem after changing out some receptacles, and it turned out that I had a broken wire in one of the white leads.

My white wires were twisted together in a wire nut and one probably broke partially when first installed, but then stayed in enough contact to keep working. When I installed the new receptacle I disturbed the wiring and it created more of a break in the bad wire. Everything showed normal with a standard plug in receptacle tester, but the GFCI tripped as soon as I plugged in any actual load.

Bruce

A GFCI will not trip because of a broken wire. A GFCI only cares about load in and load out.

However an AFCI would trip because that broken wire can cause an arc.
 
OP
V

vette-kid

Well-known member
Joined
Jul 21, 2008
Messages
3,636
Location
Navarre, FL
After a dry day, the circuit holds fine. Convince me not to start in the wet locations.

Sent from my Moto Z (2) using Tapatalk
 
OP
V

vette-kid

Well-known member
Joined
Jul 21, 2008
Messages
3,636
Location
Navarre, FL
Well the circuit didn't reset itself......
Not sure what you getting at. My point was 24hrs after a hard rain the circuit holds after I reset it. I'm less concerned for faulty wiring and more concerned that something outside is getting wet.

Sent from my Moto Z (2) using Tapatalk
 

b-boy

Well-known member
Joined
Oct 2, 2013
Messages
2,158
Location
Buffalo NY
Outdoor outlets are always a pain. If there's one on the circuit, that's probably the cuplrit.

I replace mine every 5-6 years. Water always manages to work it's way into the 'waterproof' casing.
 