Circuit to a shed (with a twist)

RVA-Jeff

Well-known member
Joined
Feb 29, 2012
Messages
144
Location
Richmond, VA
The twist is that I only need/want 120v to this shed. Couple lights and an outlet for a mower trickle charger. ~100' away from house. I have some 10/2 wG UF. Will this work on a 20a breaker from house? Do I need a breaker box/disconnect, isolated ground and ground rod at the shed? Or just terminate it in a 4" box then run a light and outlet feed from there with wire nuts?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,683
Location
Long Island
OK. Thanks. I thought the larger diameter wire would not fit into the breaker.

Jim

Nah, it'll fit just fine. In fact, for a long enough run, 8 gauge might be recommended for a 20A circuit, and I suspect that even 6 gauge might fit the same breaker.

The shed end is another story, but 10 gauge will be easy enough to wire nut to 12 gauge in that 4" box.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,187
Location
Minneapolis
It may vary by brand and model but the circuit breaker should accommodate #10 wire with no issues (for example, I just looked up a Square D QO 15 amp breaker and it will take up to #8 wire.) At the other end, the screw terminals on some duplex receptacles are able to accommodate #10 wire as well but you'd have to check your specific receptacle to be sure.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
The shed end is another story, but 10 gauge will be easy enough to wire nut to 12 gauge in that 4" box.

Good point. Don't try to run 10awg in your shed and fight with connecting it to receptacles, etc. Convert to 12awg in your first box in the shed. The long run of 10awg underground does it's job of reducing voltage drop, you don't need to run more of it inside the shed.
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,941
Location
Central New Jersey
....Do I need a breaker box/disconnect, isolated ground and ground rod at the shed? Or just terminate it in a 4" box then run a light and outlet feed from there with wire nuts?

Isn't some type of disconnect of the power required at the shed? Like using a simple switch to shut the power off? And doesn't the circuit have to be GFCI protected as well?

If he uses a GFCI breaker before the wire goes into the ground from the house, that should be sufficient to cover the GFCI requirements right?

And thanks for the answers about the 10 gauge wire (or larger) being able to fit into a 20 amp breaker!

Jim
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,683
Location
Long Island
Isn't some type of disconnect of the power required at the shed? Like using a simple switch to shut the power off? And doesn't the circuit have to be GFCI protected as well?

If he uses a GFCI breaker before the wire goes into the ground from the house, that should be sufficient to cover the GFCI requirements right?

And thanks for the answers about the 10 gauge wire (or larger) being able to fit into a 20 amp breaker!

Jim

Disconnect: Not required. He's allowed a single circuit to the outbuilding. If he wants more power, he could do a MWBC.

GFCI: Yes, required. Cheapest would be to put the GFCI in the 4" box where the wire enters the shed and wire everything past that from the load side.

#10 might be difficult to get into the back of a GFCI outlet though. Might want to pigtail it, or if he's got stranded, crimp on fork terminals.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
you sposed to have a disconnet, simple switch. But I got to wonder, why the absolute panic I. a post about v drop for a couple lights and a trickle charger? No reason not to use the 10 though. You can bury only 12 inches if you gfci first.
 

53Sparky

Well-known member
Joined
Feb 22, 2015
Messages
175
Location
Northglenn, CO
you sposed to have a disconnet, simple switch. But I got to wonder, why the absolute panic I. a post about v drop for a couple lights and a trickle charger? No reason not to use the 10 though. You can bury only 12 inches if you gfci first.

If you used a GFCI breaker, you could save some of the hassle of the deep trench as sberry suggests, but that might be a nuisance if the GFCI trips 100' away from your shed.

Disconnect: Not required. He's allowed a single circuit to the outbuilding. If he wants more power, he could do a MWBC.

GFCI: Yes, required. Cheapest would be to put the GFCI in the 4" box where the wire enters the shed and wire everything past that from the load side.

#10 might be difficult to get into the back of a GFCI outlet though. Might want to pigtail it, or if he's got stranded, crimp on fork terminals.

Everything rlitman said (x2)
 
To avoid these ads, REGISTER NOW!

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Nope.

Remember the 6 breaker handle rule?

That's for the service entrance and also, there's NO handles in this case, never mind less than six. For some reason I thought there needed to be a disconnect on a separate structure as well. At least around here I know there's a requirement, it must be a local code (City of Denver at least).
 

53Sparky

Well-known member
Joined
Feb 22, 2015
Messages
175
Location
Northglenn, CO
That's for the service entrance and also, there's NO handles in this case, never mind less than six. For some reason I thought there needed to be a disconnect on a separate structure as well. At least around here I know there's a requirement, it must be a local code (City of Denver at least).

We went through this in Denver, where a customer wanted lighting to be controlled by a 3 way switch from the house to the shed plus convenience receptacles for use in the shed. That meant that using switches to disconnect the shed would be impractical. It came down to the discussion that if there was only 1 circuit being fed to the shed, up to 20A 120V, we were not required to use ground rods or any separate service, and didn't need a disconnect on the outbuilding.

I do not remember the code references that we cited, but we were able to convince the inspector (in Denver) that it would not be required under those circumstances.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Where is the exception for a single circuit? Says if it is a multiwire it has to do both poles, says a 15A switch is acceptable on a single circuit.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,342
Location
SE MI
If the OP use 10-2 (or 10-3 in a MWBC) won't he have problems terminating it under the screw on a switch/outlet ? Any rules about using a #12 or even a #14 pig tail in the junction box, assuming the circuit is protected by a 20A breaker ?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Where is the exception for a single circuit? Says if it is a multiwire it has to do both poles, says a 15A switch is acceptable on a single circuit.

There is none. A single branch circuit serving an outbuilding needs a means of disconnect at the outbuilding. NEC 225.31 and 32.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,187
Location
Minneapolis
If the OP use 10-2 (or 10-3 in a MWBC) won't he have problems terminating it under the screw on a switch/outlet ?

It depends. Some regular receptacles and switches will accept up to #10 wire on their screw terminals, but you have to check the specs for the particular make and model to make sure.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
There is none. A single branch circuit serving an outbuilding needs a means of disconnect at the outbuilding. NEC 225.31 and 32.

That's what I thought! Thanks P.

When I wired a detached garage in Denver about 10 years ago, with a single circuit (not MWBC), they required a disconnect switch in the building at the first box. A standard toggle switch was sufficient. NEC also counts MWBC as a single circuit for the purposes of feeding a separate structure.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
Since the most difficult part of this job is to trench the new line between the two buildings, it seems like you would want to go with a large gauge wire just in case you decided to make changes later. However, I wonder how far you could go without the inspector thinking you were gaming the system.

For example, to cover possible future upgrades the OP could run MHF from the house to the garage. However, he could use junction boxes at each end so that he could break it out into a single MWBC circuit in the garage and at the panel, would there be any code violation?

Bruce
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,683
Location
Long Island
That's what I thought! Thanks P.

When I wired a detached garage in Denver about 10 years ago, with a single circuit (not MWBC), they required a disconnect switch in the building at the first box. A standard toggle switch was sufficient. NEC also counts MWBC as a single circuit for the purposes of feeding a separate structure.

A switch is a disconnect. So is an outlet.
As far as I can tell (and please correct me if I'm wrong), either one of those would be sufficient.

What you cannot do, is run a wire to the outbuilding, and use it to hardwire something without a disconnect. Say lights, or a compressor, etc.
 

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
Since the most difficult part of this job is to trench the new line between the two buildings, it seems like you would want to go with a large gauge wire just in case you decided to make changes later. However, I wonder how far you could go without the inspector thinking you were gaming the system.

For example, to cover possible future upgrades the OP could run MHF from the house to the garage. However, he could use junction boxes at each end so that he could break it out into a single MWBC circuit in the garage and at the panel, would there be any code violation?
At that point, why not just mount a small subpanel with a main breaker in it? At that point, you have to drive two ground rods ($30 and 20 minutes), but you don't have to figure out how to connect MHF to a disconnect and then a smaller gauge wire to the load, only to have to redo a bunch of that if/when you decide to upgrade later.

I agree that the trench and conduit is the bulk of the work (and 2" isn't much more money or effort than 1"), but then it seems like you might as well just put the panel in now.
 