Getting ready to wire a 220v outlet for my toys that need it, but I'm having a hard time understanding the relationship between breaker/circuit sizing and the appliance/cord sizing. Nothing is longer then 15' (basically right next to the panel).
My plan is to wire a 50 amp 220V outlet, which my research shows that it needs a minimum of the following from breaker to receptacle:
Now from the receptacle (outlet) is where I get confused. Do I size the appliance's cord for the machine or the circuit? The only thing going to this new 220v outlet right now is a 22 amp 5hp motor. Thus my thinking is that a 10/2 SOOW wired to a 6-50P plug would be acceptable for this application. Anything pulling more amps would require a new beefier cord. Or does it need to be sized for the 50 amp load, requiring 6/2 SOOW?
My plan is to wire a 50 amp 220V outlet, which my research shows that it needs a minimum of the following from breaker to receptacle:
- 6/2 Romex NM-B
- Double pole (or pull) 50/50 amp breaker
- 6-50 Receptacle
Now from the receptacle (outlet) is where I get confused. Do I size the appliance's cord for the machine or the circuit? The only thing going to this new 220v outlet right now is a 22 amp 5hp motor. Thus my thinking is that a 10/2 SOOW wired to a 6-50P plug would be acceptable for this application. Anything pulling more amps would require a new beefier cord. Or does it need to be sized for the 50 amp load, requiring 6/2 SOOW?