circulation pump set to Push or pull

slackdaddy1

Well-known member
Joined
Mar 15, 2014
Messages
476
Location
Southern MD
Heated slab, Electric mini boiler, 2- 300' 1/2 pex loops.
is it best to set up the mechanicals to have the pump "pull" the water out of the floor and push into the boiler?
Or to "pull" out of the boiler and "push" into the floor loops?

Thanks,
Slack
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,410
Location
N CA
"Pump Away" By Dan Holohan. Pump away from the boiler and put your expansion tank on the suction side.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Pump away ... after the fill/expansion/air eliminator .. and any 3/4 way valve.
 
To avoid these ads, REGISTER NOW!

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
They dont **** for a darn. Cant really even make suction. Not that your closed system would need that. There usualy on the hot side
 

Bondo

Well-known member
Joined
Dec 22, 2007
Messages
2,549
Location
Greenfield, Maine
Ayuh,.... Ole school was pump Into the boiler,....

New school is to pump Away from the boiler, with the air strainer/ pressure tank, 'tween the pump, 'n boiler,...