Hi all

Beginning of the heating season I asked here about sealing a leaky boiler. Ended up installing a slightly used Weil Mclean Gold Series Boiler and it installed easily and has worked perfectly all winter.

I have a 4 zone system controlled by zone valves and all the controls are wired as they were in the old boiler. I installed a separate electric water heater and no longer heat domestic hot water with the boiler.

I have a Honeywell Aquastat L8148A and it calls for the circulator pump (Taco 007) to be wired to the C1 and L2 terminals on the circuit board. In those positions the pump runs 24-7 and never shuts off .. is that normal operation or is there a way to wire the circulator to turn on only when the thermostat in a zone is calling for heat ? I tried using C1 and C2 and it has constant current also. Do I need another separate relay for the circulator to be controlled by the thermostats ?
Thanks... Mike B
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
You have the end switches on the zone valves connected to the thermostat terminals correct? Does the boiler maintain temp all the time even with no calls for heat?

Was the old method of heating water a tankless coil in the boiler? If so it would have been set up to maintain temp all the time.

What brand of zone valves?
 
OP
O

oldcpecdr

Well-known member
Joined
Jun 16, 2009
Messages
340
Location
Cape Cod
Yes Brewchief

End switches are wires to t-stats, never disconnected them just slid the new boiler in place. Boiler maintains temperature all the time.

Old method of DHW was a Boilermate (don't ever buy one) with its own built in coil and used a separate zone and circulator.

Taco 571 Bronze Zone Valves
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
What wires are connected to the zone valves where?
If you disconnect the wires at the t-stat terminals on the aquastat does the pump shut off?
 
To avoid these ads, REGISTER NOW!
OP
O

oldcpecdr

Well-known member
Joined
Jun 16, 2009
Messages
340
Location
Cape Cod
Removing a thermostat wire at the Aquastat shuts off the relay and the pump goes off.

The Zone valves (4) each have two thermostat wires connected to the bottom two terminals, and then appear to be powered in parallel from the transformer.

The valves work and open when thermostat is raised calling for heat and close when heat is not being called for.

Mike B
 