Class A Chimney Pipe for NG?

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
3,969
Location
Upstate NY
I've been using a wood stove in my garage, 6" single wall pipe up to the ceiling, then 6" Class A chimney pipe up to a few feet over the roof peak. I'm looking at taking out the wood stove this summer and installing a hanging natural gas heater that requires a B-vent system.

Is it possible to connect the type B vent (3 or 4" I assume) from the heater to the 6" class A pipe through the roof? I know the Class A pipe is rated for natural gas, but not sure if the increased diameter is an issue. Or could I run the type B vent pipe up inside the chimney pipe and leave it and the existing cap in place? I've installed several HE natural gas furnaces with PVC vents, never with metal B vent.

If these aren't possible, I can always install the heater across the garage against an outside wall and cut a new hole in the wall for the vent system. I don't plan on taking out the wood stove pipe, so I wanted to utilize this existing hole if possible.


Sorry for any stupid questions. Any help is appreciated!
 
To avoid these ads, REGISTER NOW!

zak77

Well-known member
Joined
Sep 18, 2014
Messages
1,354
Location
Monson, MA
I'd say there probably shouldnt be an issue running the b-vent through the class a. You'll need to make a collar of some sorts to take up the space between the exterior of the class b and interior of class a near the cap. That's what i'd do if i were in your shoes.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
Your chimney provides draft - i wouldn't want to increase from 3" to 6" for a small appliance. There shouldn't be an issue capping the 6" on both sides and passing through it with the appropriate venting.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,986
Location
Northern Central Ohio
Your chimney provides draft - i wouldn't want to increase from 3" to 6" for a small appliance. There shouldn't be an issue capping the 6" on both sides and passing through it with the appropriate venting.

My thoughts as well.

I think the 6" may be too big for your appliance and may not get a proper draft.

Honestly, I'd send an email to the manufacturer and inquire about the larger pipe before you buy anything.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Honestly, I'd send an email to the manufacturer and inquire about the larger pipe before you buy anything.

Good idea.......:headscratqpredict two answers:

We don’t talk to end users on install and troubleshooting questions only certified installers or service techs.

We only recommended venting is clearly printed in the install manual........alternations or combinations of A, B, class III is not approved.

B through the A works........or just take the A down and install a complete B system or classs III and side venting leaving the A inplace for the future.
 
To avoid these ads, REGISTER NOW!
OP
C

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
3,969
Location
Upstate NY
Thanks for the input, guys! I think I'll run the B-vent up through the chimney pipe and bend a sheet metal collar for the top and bottom of the Class A pipe to cover the gap.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,411
Location
N CA
I prefer to use either Selkirk or Duravent B-vent. The locking system is better than the competition. They make an assortment of flashings that you could use, at least part of, to flash the Class A pipe. It will take a bit of fabrication and do not screw the flashing to the Class A. I do agree that using the B-vent as a line and the A as a pipe chase is the way to go.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,986
Location
Northern Central Ohio
Good idea.......:headscratqpredict two answers:

We don’t talk to end users on install and troubleshooting questions only certified installers or service techs.

We only recommended venting is clearly printed in the install manual........alternations or combinations of A, B, class III is not approved.

B through the A works........or just take the A down and install a complete B system or classs III and side venting leaving the A inplace for the future.

Very possible to get that type of response. Although people don't mind spending an hour poking around on the 'net but they don't have time to spend 3 minutes shooting an email out with a few questions.

Not saying the OP wouldn't but just typical behavior of people in general.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
True...........I was being a little sarcastic because the garage heater manufacturers seem to be very tight with technical information.........a few have noted here when troubleshooting is requested.
 