Cleaning up spaghetti

e462001

Member
Joined
Feb 15, 2013
Messages
22
Location
East TN
The PO left the panel for the house/garage in a bit of a mess.

DSC_1955small.JPG

DSC_1956small.JPG


This is the only panel for the house with the mains coming in from the right of the box.

I started by putting in a plywood panel above the mess and started anchoring the wires down however I'm worried that I may not be thinking far enough ahead to be doing that yet. The wiring currently runs (drapes) below the rafters, so if I was going to bore holes to run the cables through I'd need to disconnect them either at the box or the other end to run them through the joists back to the box from where they go up through the floor which would mean having to undo the fasteners I started putting in.

The other option I can think of is to box in the wiring along with the ducting that runs across the top of the picture. I plan on framing in and finishing the wall at some point in the future.

Thoughts on those two options or other alternatives. Also the box itself looks pretty crappy to me but I've never wired in a box before so maybe thats as good as it gets? :dunno:

Any advice/thoughts are welcome. I have very little experience with electricity prior to this on AC (mostly just car wiring) but always looking to learn new things.
 
To avoid these ads, REGISTER NOW!

pmilin

Well-known member
Joined
Oct 5, 2012
Messages
193
Location
Colorado
Wow. What a mess. This is unbelievable to me. This wiring is for the house as well as the garage? How did this ever pass code when the house was built?

If you try to re-route the wire through the joints they will likely become too short to reach the box won't they? Is the complete wire path exposed to where you could run a new wire if necessary? Maybe moving the box up is an option as long as the power feed wire is long enough. In any case you have to get those wires secured. Draping around like that is not good.

Also looks like there is a mismatched breaker in the box.
 
Last edited:

RECox286

Well-known member
Joined
Apr 11, 2012
Messages
1,399
Location
South Joisey (yeah, that is part of the USA)
No joking around here:

Neatness only counts in surveying. I've seen

plenty of what electricians leave on a job, calling

it "done" and let me tell you that your panel is almost

pristine to some I've looked at. If it bothers you that

much, then straighten it up to your liking. It won't

make it work any better than it does in its' present

condition, but, at least you will feel better.

Uncle Bob
 
OP
E

e462001

Member
Joined
Feb 15, 2013
Messages
22
Location
East TN
Wow. What a mess. This is unbelievable to me. This wiring is for the house as well as the garage? How did this ever pass code when the house was built?

If you try to re-route the wire through the joints they will likely become too short to reach the box won't they? Is the complete wire path exposed to where you could run a new wire if necessary? Maybe moving the box up is an option as long as the power feed wire is long enough. In any case you have to get those wires secured. Draping around like that is not good.

Also looks like there is a mismatched breaker in the box.

Mismatched breaker? You mean the top one on the left side? I just noticed that now. Another gift from the PO I guess.

A lot of the wire is draping up to 2 feet from the ceiling. The wire path is exposed until it goes up into the ceiling and enters the main house.

Wire length is one reason I considered boxing in the duct with the wires, then I can staple the wires to the bottom of the joists since nothing will be attached to them at that point.

This is the box for house and garage as the garage is the basement of the house.

You, sir, are a master of understatement.
:eyecrazy:

Hah well I'm not a master electrician so I choose to show my other skills in this case.
 
OP
E

e462001

Member
Joined
Feb 15, 2013
Messages
22
Location
East TN
No joking around here:

Neatness only counts in surveying. I've seen

plenty of what electricians leave on a job, calling

it "done" and let me tell you that your panel is almost

pristine to some I've looked at. If it bothers you that

much, then straighten it up to your liking. It won't

make it work any better than it does in its' present

condition, but, at least you will feel better.

Uncle Bob

Good point, the draping wires will be cleaned up no matter what. I was more concerned if there was any potential for bad things to happen with the interior of the box that way.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,111
Location
Modesto, CA
The Sq D breaker needs to be changed to the correct model of pressumably GE brand(if indeed the panel is GE jusgin by the rest of the breakers

I see the incoming feed is 4-wire but the neutral and ground bars are tied together. Before this panel, is there a disconnect or just a meter? If just a meter the feed should be 3-wire and if there is a disconnect, then it should be 4-wire as it is and the tie between the 2 bars NEEDS to be removed!

The wire needs to be secured within 12" of the box(Romex connector/clamp are already there) and at 4 1/2' intervals.

Nothin bad will happen with the panel that messy. However, its a pain to work on and troubleshoot when its that way. When i get hired to clean a mess up like that, its easier to label everything and then take all wires out and start from scratch. I tell the customer i need half a day to cut in a panel and clean it up so they would be without power for that long. Some are ok with it and others dont want to be burdened and cant stand being with no TV or xBox for that short amount of time so they pass. If it were my panel i would clean it up!

U think that panels bad? Try cleaning up a commercial panel in say an old McDonalds. WHAT A FRICKING MESS.
 
Last edited:
OP
E

e462001

Member
Joined
Feb 15, 2013
Messages
22
Location
East TN
The Sq D breaker needs to be changed to the correct model of pressumably GE brand(if indeed the panel is GE jusgin by the rest of the breakers

I see the incoming feed is 4-wire but the neutral and ground bars are tied together. Before this panel, is there a disconnect or just a meter? If just a meter the feed should be 3-wire and if there is a disconnect, then it should be 4-wire as it is and the tie between the 2 bars NEEDS to be removed!

The wire needs to be secured within 12" of the box(Romex connector/clamp are already there) and at 4 1/2' intervals.

Nothin bad will happen with the panel that messy. However, its a pain to work on and troubleshoot when its that way. When i get hired to clean a mess up like that, its easier to label everything and then take all wires out and start from scratch. I tell the customer i need half a day to cut in a panel and clean it up so they would be without power for that long. Some are ok with it and others dont want to be burdened and cant stand being with no TV or xBox for that short amount of time so they pass. If it were my panel i would clean it up!

U think that panels bad? Try cleaning up a commercial panel in say an old McDonalds. WHAT A FRICKING MESS.
I think I have a spare breaker that will fit the bill but if not I'll pick one up tomorrow. The only thing I see upstream of the box is the meter but I could be missing something as I don't know what I'm looking for.

I see three shielded wires and one bare wire coming in from outside. Does that count as four? My question is based off wiring being labeled as 12-3 and such. What is the difference between three wire and four wire anyways?

What do you mean by cut in a new box?
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
The Sq D breaker needs to be changed to the correct model of pressumably GE brand(if indeed the panel is GE jusgin by the rest of the breakers

I see the incoming feed is 4-wire but the neutral and ground bars are tied together. Before this panel, is there a disconnect or just a meter? If just a meter the feed should be 3-wire and if there is a disconnect, then it should be 4-wire as it is and the tie between the 2 bars NEEDS to be removed!

The wire needs to be secured within 12" of the box(Romex connector/clamp are already there) and at 4 1/2' intervals.

Nothin bad will happen with the panel that messy. However, its a pain to work on and troubleshoot when its that way. When i get hired to clean a mess up like that, its easier to label everything and then take all wires out and start from scratch. I tell the customer i need half a day to cut in a panel and clean it up so they would be without power for that long. Some are ok with it and others dont want to be burdened and cant stand being with no TV or xBox for that short amount of time so they pass. If it were my panel i would clean it up!

U think that panels bad? Try cleaning up a commercial panel in say an old McDonalds. WHAT A FRICKING MESS.
:thumbup::thumbup::thumbup::thumbup::thumbup:
Or any commercial building in Omaha after 5 south of the border remodel jobs!:lol:
That mess could definitely use some cleaning up though.;)
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
No joking around here:

Neatness only counts in surveying. I've seen

plenty of what electricians leave on a job, calling

it "done" and let me tell you that your panel is almost

pristine to some I've looked at. If it bothers you that

much, then straighten it up to your liking. It won't

make it work any better than it does in its' present

condition, but, at least you will feel better.

Uncle Bob
They should be beaten with their own tools.:lol:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,111
Location
Modesto, CA
I believe its orange romex, so ten gauge.

What do you all use up in Chicago?

Lame *** city of Chicago banned NM-b long ago...so they have to use conuit for everything- EMT, FMC, MC, BX/AC(oh wait BX is probably not allowed because code no longer allows the conduit to be used as EGC)...
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
I also see several of my pet peeves all in one box. A handy box used for a GFI, feed thru on a handy box, and side feeding a handy box. Basically I hate handy boxes, but when you do any or in this case all of these things, that box is crammed and the wires likely are cut way too short to make it fit, and are jammed in there with high potential for insulation damage. I bet that EMT connector coming in the side is within fractions of an inch of touching the hot terminal on the GFI. First thing I would do is replace that with a 4 square deep box.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Just a note: a SQ D HOM is not classified to be used in any panel, they are UL listed to be used in SQ D loadcenters only. Breakers are listed to be used in the manufacturers panels, some are UL classified to be used in other manufacturers panels but you have to have the paperwork to prove it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,111
Location
Modesto, CA
I think I have a spare breaker that will fit the bill but if not I'll pick one up tomorrow. The only thing I see upstream of the box is the meter but I could be missing something as I don't know what I'm looking for.

I see three shielded wires and one bare wire coming in from outside. Does that count as four? My question is based off wiring being labeled as 12-3 and such. What is the difference between three wire and four wire anyways?

What do you mean by cut in a new box?

Sorry didnt see this earlier.

If u have a breaker with your meter, then 4-wire is fine but the tie bar needs to be removed.

If u have no breaker at the meter then 3-wire is fine and nothing needs to be changed.

3-wire is for before the first disconnect. After that u need 4-wire. The difference being an isolated neutral in the 4-wire.

If u take some pics and post em we can tell u what u have at the meter.

Cutting in a new box means cutting the wires and terminating them in the panel.
 

pmilin

Well-known member
Joined
Oct 5, 2012
Messages
193
Location
Colorado
I see the incoming feed is 4-wire but the neutral and ground bars are tied together. Before this panel, is there a disconnect or just a meter? If just a meter the feed should be 3-wire and if there is a disconnect, then it should be 4-wire as it is and the tie between the 2 bars NEEDS to be removed!

Looks like the neutrals and grounds are using the ground bus and neutral bus interchangeably. Shouldn't the all the grounds be on the ground bar and all of the neutrals be on the neutral bar?
 

RivennHewn

Well-known member
Joined
Jun 4, 2011
Messages
10,393
Location
PNW
When we were buying our house, the bank refused to lend on it due to the condition of the "Panel". It was a 1948 fuse box that had been "Johnny Home Owner'd" to the point that I was scared to get into it.

I hired a contractor, and paid $2600. That was 13 years ago.

Probably the worst I'd ever seen.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,111
Location
Modesto, CA
Looks like the neutrals and grounds are using the ground bus and neutral bus interchangeably. Shouldn't the all the grounds be on the ground bar and all of the neutrals be on the neutral bar?

It all depends on the answer to my previous questions. If this is the main service panel with no discpnnect ahead of it, then EGC and neutrals should land on the same bar...
 

Kracin

Well-known member
Joined
Mar 25, 2013
Messages
1,666
Location
Omaha, NE
:thumbup::thumbup::thumbup::thumbup::thumbup:
Or any commercial building in Omaha after 5 south of the border remodel jobs!:lol:
That mess could definitely use some cleaning up though.;)

hah, or any in the plant i work in here in omaha as well. seems like people know only a select few are going to see their neatness in the panel, so why bother right lol
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
hah, or any in the plant i work in here in omaha as well. seems like people know only a select few are going to see their neatness in the panel, so why bother right lol

Heres some of my past commercial work,I don't do nearly as much pipe bending anymore.
 

Attachments

  • user70324_pic5012_1328010365.jpg
    user70324_pic5012_1328010365.jpg
    102.5 KB · Views: 70
  • user70324_pic5013_1328010365.jpg
    user70324_pic5013_1328010365.jpg
    63.6 KB · Views: 52
  • user70324_pic5034_1328593671.jpg
    user70324_pic5034_1328593671.jpg
    130.5 KB · Views: 50
  • user70324_pic5035_1328593671.jpg
    user70324_pic5035_1328593671.jpg
    129.5 KB · Views: 46
  • user70324_pic5036_1328593729.jpg
    user70324_pic5036_1328593729.jpg
    74.6 KB · Views: 45
  • user70324_pic5037_1328593729.jpg
    user70324_pic5037_1328593729.jpg
    109.1 KB · Views: 43
  • user70324_pic5038_1328593729.jpg
    user70324_pic5038_1328593729.jpg
    95 KB · Views: 39

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
It all depends on the answer to my previous questions. If this is the main service panel with no discpnnect ahead of it, then EGC and neutrals should land on the same bar...


I believe he said this is the main panel to the house. Do not remove the bond bar between the ground and neutral if this is true...


Sent from my iPad using Tapatalk
 

Rickster55

Well-known member
Joined
Jun 22, 2009
Messages
1,132
Location
Syracuse, NY
I would (and have) straighten out the spaghetti. As others have said, it won't work any better but it'll look nicer. But only if you are confident with your level of skill to do it.
 

Kracin

Well-known member
Joined
Mar 25, 2013
Messages
1,666
Location
Omaha, NE
Heres some of my past commercial work,I don't do nearly as much pipe bending anymore.

nice, looks like too much work from lazy people.

we have engineers who don't give a F. hooking motors up with emt runs on floating bases, going around our crew and paying commonwealth to do some BS while we aren't in the building like doing 480 power drops with SO cord for permanent install of machines. using cabinets that are completely overloaded with wires, undersizing everything. it's damn annoying. but you can't blame them too much, they don't hire a single EE, or anyone that specializes in electrical (hell we don't, we just have to know it all), they take fresh out of college mech and a few other engineer types and throw them all in the mix and have them start doing stuff they never thought they'd be doing.
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
nice, looks like too much work from lazy people.

we have engineers who don't give a F. hooking motors up with emt runs on floating bases, going around our crew and paying commonwealth to do some BS while we aren't in the building like doing 480 power drops with SO cord for permanent install of machines. using cabinets that are completely overloaded with wires, undersizing everything. it's damn annoying. but you can't blame them too much, they don't hire a single EE, or anyone that specializes in electrical (hell we don't, we just have to know it all), they take fresh out of college mech and a few other engineer types and throw them all in the mix and have them start doing stuff they never thought they'd be doing.


Engineers.... :spit:


Sent from my iPad using Tapatalk
 

frankush

Well-known member
Joined
Oct 23, 2011
Messages
1,156
Location
IL
Lame *** city of Chicago banned NM-b long ago...so they have to use conuit for everything- EMT, FMC, MC, BX/AC(oh wait BX is probably not allowed because code no longer allows the conduit to be used as EGC)...

Say what you want, but I'd rather run pipe and pull my own wire, than play with romex all day long. I've seen crappy pipe runs, but they can't compare with most of the romex jobs I've seen all over the US.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,111
Location
Modesto, CA
Say what you want, but I'd rather run pipe and pull my own wire, than play with romex all day long. I've seen crappy pipe runs, but they can't compare with most of the romex jobs I've seen all over the US.

Ive seen good NM-b jobs and Ive seen bad ones.

Pipe can be done just as crappy- undersized/overfilled, bad bends, wrong connectors, etc!

Plus pipe adds cost to the job vs. NM-b
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,111
Location
Modesto, CA
According to someone whose opinion I respect, EMT over NM adds 20% to the cost of the job of wiring a house, but they have crews who sh*t & git.


But if you want to see a NM job done well enter "NM run with a iron" at your favorite search engine (hopefully not google) and you will see a work of art.


I did it for you.

http://www.electrical-contractor.net/forums/ubbthreads.php/topics/122256/NM_Run_With_An_Iron.html

Gotta say thats some of the best NM-b wiring work ive ever seen! :eyecrazy:

Ive only been in a few of those multimillion dollar homes...

Doing NM that way has got to add to the job cost. But it sure does look amazing!

The time alone needed to plan the runs like that must be insane!

I would love to work and learn with that outfit!

Craftsmenship is still out there!
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Gotta say thats some of the best NM-b wiring work ive ever seen! :eyecrazy:

Ive only been in a few of those multimillion dollar homes...

Doing NM that way has got to add to the job cost. But it sure does look amazing!

The time alone needed to plan the runs like that must be insane!

I would love to work and learn with that outfit!

Craftsmenship is still out there!

Somebody has to be willing to pay for it, not many are.
 