clearance question

wirt

Well-known member
Joined
Mar 22, 2013
Messages
88
Location
Illinois
I'm in the process of adding a ceiling with insulation to my garage, I have a 45k Lennox hanging furnace and am wondering what the clearance for the the exhaust pipe should be? It's a double walled vent that goes up through the roof, is 1" enough or should there be more? Also how do you fill the gap around the pipe then?

Btw the ceiling is plywood and the insulation is typical fiberglass Matt.

Thanks
 
To avoid these ads, REGISTER NOW!

metlmunchr

Well-known member
Joined
Sep 10, 2011
Messages
1,278
Assuming this is type B vent on a gas fired furnace......

1" minimum clearance to combustibles.

Use either a firestop support or a firestop spacer at the ceiling penetration to seal it off and to maintain the pipe centered in the opening.
 