When Insulation Contact (IC) cans get drywalled into the ceiling - how do the no longer accessible junction boxes qualify?

I understand concealed junction boxes are disallowed.

11119.JPEG
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
Because they are "accessible" when the can is removed from the housing, there are 3 screws that hold the can in place & are visible from the floor when installed in a normal height ceiling. Access to the J-box is not easy but it is accessible.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
They are considered accessible when you don't have to remove part of the building or structure to gain access.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Because they are "accessible" when the can is removed from the housing, there are 3 screws that hold the can in place & are visible from the floor when installed in a normal height ceiling. Access to the J-box is not easy but it is accessible.[/Q

Yep,the code say accessible-not easy,comfortable or convenient,especially when it comes time to replace a 4" MR16 potlight transformer...:willy_nil
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
I like the 4" cans I installed recently....you pull out the whole can...box and all when you want to work on it.
 